Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Low shower pressure after ASHP retrofit
I have recently had a Daikin ASHP system installed replacing our combi gas boiler. Everything has been OK except the shower pressure is now greatly reduced compared to before install. The install engineers suggested the issue was with the cartridge so I replaced it but the problem remains. I have also check the shower head and hose, all fine.
Note -the hot water flow to the taps is fine but if the HW tap is open and the shower on the flow almost stops.
The hot water tank is located in the loft space.
Can anyone suggest what it could be causing this?
First this will be unrelated to the heat pump itself. It is just a heat source.
Two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
What is your stored water temperature?
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
@johnmo
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
Posted by: @jacscold will have 6 bar and the hot will be at 3 bar
If that's the case it's a winder you get a hot shower at all.
Posted by: @jacsthere is a combination valve on it as the engineers considered this may be causing the issue??
They are mandatory, the balanced flow port for cold water is on the combination valve. Extremely unlikely to the an issue with the combination valve.
So other things come up
If the balanced flow has not been used
You need a check valve on the hot water outlet of the cylinder to stop reverse flow, you will also need a prv on the cold water main sett to a max of 3 bar.
@johnmo please can you explain why I'd struggle to get a hot water shower with those water pressures?
if I turn in the stop clock to reduce flow, could this help?
Posted by: @jacsplease can you explain why I'd struggle to get a hot water shower with those water pressures?
Your mixer is designed to see almost equal pressures on cold and hot sides. Most shower mixers will self adjust to maintain set flow temperature.
If one side is 6 bar and the other 3 bar, the 3 bar will not break in to the 3 bar. So I suspect the mixer will wind back cold water flow as far as it can, to achieve the target flow temperature. As a consequence you have rubbish flow.
Try
Switch shower on, open one or more cold taps, see what happens. If you are getting big pressure differences that should help identify.
-
7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
2 months ago
-
Bosch CS5800i 5kW - Experience So Far
4 months ago
-
Has anyone seen this problem before? Huge anticycling times
7 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
7 months ago
-
Yes, the "zoning with ASHP" topic again...
1 year ago
- 26 Forums
- 2,675 Topics
- 62.6 K Posts
- 230 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
@majordennisbloodnok @jamespa I stand corrected, A2A...
By Batpred , 20 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I didn't know about those, they look like good pieces o...
By JamesPa , 2 hours ago
-
@mkz, that's very helpful. Even if Urban Plumber are no...
By Majordennisbloodnok , 3 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 3 hours ago
-
My first question is why bother with the auto balancin...
By JamesPa , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 4 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 4 hours ago
-
I share the same experience as @majordennisbloodnok hav...
By Old_Scientist , 5 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 8 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@jamespa many thanks, definitely i will give the pre...
By ragtime27 , 19 hours ago
-
RE: Heat pump installation quotations
@jamespa I noticed that in the Heat Geek design consult...
By Batpred , 21 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@bash, something we haven't touched on already relates ...
By Majordennisbloodnok , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Vaillant arotherm plus 12kW. Installed March 2025. Ex...
By Harebell , 2 days ago