[Solved] Low shower pressure after ASHP retrofit
I have recently had a Daikin ASHP system installed replacing our combi gas boiler. Everything has been OK except the shower pressure is now greatly reduced compared to before install. The install engineers suggested the issue was with the cartridge so I replaced it but the problem remains. I have also check the shower head and hose, all fine.
Note -the hot water flow to the taps is fine but if the HW tap is open and the shower on the flow almost stops.
The hot water tank is located in the loft space.
Can anyone suggest what it could be causing this?
First this will be unrelated to the heat pump itself. It is just a heat source.
Two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
What is your stored water temperature?
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
@johnmo
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
Posted by: @jacscold will have 6 bar and the hot will be at 3 bar
If that's the case it's a winder you get a hot shower at all.
Posted by: @jacsthere is a combination valve on it as the engineers considered this may be causing the issue??
They are mandatory, the balanced flow port for cold water is on the combination valve. Extremely unlikely to the an issue with the combination valve.
So other things come up
If the balanced flow has not been used
You need a check valve on the hot water outlet of the cylinder to stop reverse flow, you will also need a prv on the cold water main sett to a max of 3 bar.
@johnmo please can you explain why I'd struggle to get a hot water shower with those water pressures?
if I turn in the stop clock to reduce flow, could this help?
Posted by: @jacsplease can you explain why I'd struggle to get a hot water shower with those water pressures?
Your mixer is designed to see almost equal pressures on cold and hot sides. Most shower mixers will self adjust to maintain set flow temperature.
If one side is 6 bar and the other 3 bar, the 3 bar will not break in to the 3 bar. So I suspect the mixer will wind back cold water flow as far as it can, to achieve the target flow temperature. As a consequence you have rubbish flow.
Try
Switch shower on, open one or more cold taps, see what happens. If you are getting big pressure differences that should help identify.
-
Yes, the "zoning with ASHP" topic again...
4 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
8 months ago
-
Has anyone seen this problem before? Huge anticycling times
10 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
11 months ago
-
Advice needed on inefficient Samsung ASHP installation
12 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 42 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
@julianc Expressed as a flow diagram, I suspect one wou...
By Toodles , 7 minutes ago
-
RE: Big Changes Coming to Our Heat Pump System
@jamespa The dormitories at my boarding school (in Exet...
By Toodles , 10 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay yes there is the modbus register list at th...
By benson , 21 minutes ago
-
RE: Heat Pump Damage on install - useable or dealbreaker?
@benson I imagine that this may well be a Daikin unit a...
By Toodles , 32 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 15 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 16 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 17 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 19 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 20 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 21 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 22 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago