[Solved] Low shower pressure after ASHP retrofit
I have recently had a Daikin ASHP system installed replacing our combi gas boiler. Everything has been OK except the shower pressure is now greatly reduced compared to before install. The install engineers suggested the issue was with the cartridge so I replaced it but the problem remains. I have also check the shower head and hose, all fine.
Note -the hot water flow to the taps is fine but if the HW tap is open and the shower on the flow almost stops.
The hot water tank is located in the loft space.
Can anyone suggest what it could be causing this?
First this will be unrelated to the heat pump itself. It is just a heat source.
Two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
What is your stored water temperature?
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
@johnmo
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
Posted by: @jacscold will have 6 bar and the hot will be at 3 bar
If that's the case it's a winder you get a hot shower at all.
Posted by: @jacsthere is a combination valve on it as the engineers considered this may be causing the issue??
They are mandatory, the balanced flow port for cold water is on the combination valve. Extremely unlikely to the an issue with the combination valve.
So other things come up
If the balanced flow has not been used
You need a check valve on the hot water outlet of the cylinder to stop reverse flow, you will also need a prv on the cold water main sett to a max of 3 bar.
@johnmo please can you explain why I'd struggle to get a hot water shower with those water pressures?
if I turn in the stop clock to reduce flow, could this help?
Posted by: @jacsplease can you explain why I'd struggle to get a hot water shower with those water pressures?
Your mixer is designed to see almost equal pressures on cold and hot sides. Most shower mixers will self adjust to maintain set flow temperature.
If one side is 6 bar and the other 3 bar, the 3 bar will not break in to the 3 bar. So I suspect the mixer will wind back cold water flow as far as it can, to achieve the target flow temperature. As a consequence you have rubbish flow.
Try
Switch shower on, open one or more cold taps, see what happens. If you are getting big pressure differences that should help identify.
-
Yes, the "zoning with ASHP" topic again...
3 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
7 months ago
-
Has anyone seen this problem before? Huge anticycling times
9 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
10 months ago
-
Advice needed on inefficient Samsung ASHP installation
11 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 25 Online
- 5,656 Members
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@carlo the 16kw rating refers to output.. afaik? So w...
By Tim441 , 10 hours ago
-
Anyone still weathering it out with Agile?
Being curious, I have continued to monitor the daily ra...
By Toodles , 16 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 21 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 4 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 5 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago