[Solved] Low shower pressure after ASHP retrofit
I have recently had a Daikin ASHP system installed replacing our combi gas boiler. Everything has been OK except the shower pressure is now greatly reduced compared to before install. The install engineers suggested the issue was with the cartridge so I replaced it but the problem remains. I have also check the shower head and hose, all fine.
Note -the hot water flow to the taps is fine but if the HW tap is open and the shower on the flow almost stops.
The hot water tank is located in the loft space.
Can anyone suggest what it could be causing this?
First this will be unrelated to the heat pump itself. It is just a heat source.
Two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
What is your stored water temperature?
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
@johnmo
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
Posted by: @jacscold will have 6 bar and the hot will be at 3 bar
If that's the case it's a winder you get a hot shower at all.
Posted by: @jacsthere is a combination valve on it as the engineers considered this may be causing the issue??
They are mandatory, the balanced flow port for cold water is on the combination valve. Extremely unlikely to the an issue with the combination valve.
So other things come up
If the balanced flow has not been used
You need a check valve on the hot water outlet of the cylinder to stop reverse flow, you will also need a prv on the cold water main sett to a max of 3 bar.
@johnmo please can you explain why I'd struggle to get a hot water shower with those water pressures?
if I turn in the stop clock to reduce flow, could this help?
Posted by: @jacsplease can you explain why I'd struggle to get a hot water shower with those water pressures?
Your mixer is designed to see almost equal pressures on cold and hot sides. Most shower mixers will self adjust to maintain set flow temperature.
If one side is 6 bar and the other 3 bar, the 3 bar will not break in to the 3 bar. So I suspect the mixer will wind back cold water flow as far as it can, to achieve the target flow temperature. As a consequence you have rubbish flow.
Try
Switch shower on, open one or more cold taps, see what happens. If you are getting big pressure differences that should help identify.
-
Bosch CS5800i 5kW - Experience So Far
1 week ago
-
Yes, the "zoning with ASHP" topic again...
5 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
9 months ago
-
Has anyone seen this problem before? Huge anticycling times
11 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
1 year ago
- 26 Forums
- 2,221 Topics
- 49.3 K Posts
- 98 Online
- 5,881 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: New Fogstar 15.5kWh upright solution
Thank you. The way that framework splits between 1 an...
By Batpred , 2 hours ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@jamespa thank your for your input.We used the heating ...
By bonobo , 4 hours ago
-
The Mars and Richard Kitchen Show
Just stopping by to say: 1) Mars I'm so sorry that yo...
By Lucia , 4 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks both. I’ll push gor thr glycol, 5% is 5% i cant ...
By Crimson , 4 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
My circulation pump cycles, when the compressor is off,...
By KenBone , 5 hours ago
-
RE: Odd noise in our Ideal Logic ASHP
Should have all you radiators and con...
By KenBone , 5 hours ago
-
RE: Automation options to maximuse efficiency & ToU tariffs
If you are asking what is available to the non geek hou...
By JamesPa , 6 hours ago
-
Yes, you make a good point and beyond servers, engineer...
By Batpred , 7 hours ago
-
RE: Isolating the system for a planned power cut
Insurance helps and when adding high powered devices li...
By Batpred , 8 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
Is there a lookup facility to see your limit, or is it ...
By DREI , 14 hours ago
-
RE: Electricity price predictions
Without getting too much into politics, given that the ...
By Batpred , 14 hours ago
-
UK Consumer Law Reality Check (for anyone dealing with ...
By DREI , 14 hours ago
-
@dgclimatecontrol Thanks... this was resolved back in M...
By Sandman1600 , 15 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
That's the problem with the UK, in comparison with Amer...
By DREI , 16 hours ago
-
Electrical is the only way forward.. But until we get...
By Batpred , 16 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: Panasonic Model: WH-WXG12ME8 Type: AS...
By Andy-e , 16 hours ago
-
In our installation, we actually have an LLH but any di...
By Toodles , 16 hours ago
-
RE: Large heat pump options for church building
This church project has more in common with a commercia...
By GrahamF , 16 hours ago
-
RE: How good is the app support for your heat pump?
It looks quite interesting and, like you, I'd only want...
By Sheriff Fatman , 16 hours ago
-
RE: External wall insulation - your experience
So our house is in SE England. We mainly had mixed w...
By Batpred , 1 day ago