[Solved] Low shower pressure after ASHP retrofit
I have recently had a Daikin ASHP system installed replacing our combi gas boiler. Everything has been OK except the shower pressure is now greatly reduced compared to before install. The install engineers suggested the issue was with the cartridge so I replaced it but the problem remains. I have also check the shower head and hose, all fine.
Note -the hot water flow to the taps is fine but if the HW tap is open and the shower on the flow almost stops.
The hot water tank is located in the loft space.
Can anyone suggest what it could be causing this?
First this will be unrelated to the heat pump itself. It is just a heat source.
Two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
What is your stored water temperature?
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
@johnmo
thank you for responding. I have responded in red with more info.
two things affect flow through the DHW cylinder. Assume it is an unvented cylinder?
yes, it's an unvented cylinder.
First the water supply flow rate to the cylinder. Was this checked and static and dynamic pressure recorded? These should be on the commissioning certificate
according to the comms certificate, the calculated flow rate is 14 l/min.
incoming static cold water supply pressure of 3 bar
If your dynamic (flowing pressure) mains water pressure at peak times is not a minimum of 1.5 bar and 20 l/m flow, levels of performance may not be acceptable!
was measured at around 6 bar pressure during survey.
Do you have a reduced flow if you turn on two taps? Try with two hot and two cold.
I turned on 2 taps and the shower and the flow reduced to a trickle. I'll try 2 hot and 2 cold.
What is your stored water temperature?
46°C but even when the water temp is >60°C (disinfection cycle) poor flow at the shower
If you have high main water pressure, this is reduced at the cylinder to 3 bar. To stop issues you either used a balance flow connection the cylinder or add a similar pressure reducer to the mains near the stop cock.
Did they use a balanced flow to the shower? If they didn't there will be two different pressures going into the mixer tap on the shower, this will cause similar flow related issues.
nothing was added at the stop cock I don't believe.
So based on this then, the cold will have 6 bar and the hot will be at 3 bar?
I'll need to check if a balanced flow connection at the cylinder. I'm not sure to be honest, there is a combination valve on it as the engineers considered this may be causing the issue??
Posted by: @jacscold will have 6 bar and the hot will be at 3 bar
If that's the case it's a winder you get a hot shower at all.
Posted by: @jacsthere is a combination valve on it as the engineers considered this may be causing the issue??
They are mandatory, the balanced flow port for cold water is on the combination valve. Extremely unlikely to the an issue with the combination valve.
So other things come up
If the balanced flow has not been used
You need a check valve on the hot water outlet of the cylinder to stop reverse flow, you will also need a prv on the cold water main sett to a max of 3 bar.
@johnmo please can you explain why I'd struggle to get a hot water shower with those water pressures?
if I turn in the stop clock to reduce flow, could this help?
Posted by: @jacsplease can you explain why I'd struggle to get a hot water shower with those water pressures?
Your mixer is designed to see almost equal pressures on cold and hot sides. Most shower mixers will self adjust to maintain set flow temperature.
If one side is 6 bar and the other 3 bar, the 3 bar will not break in to the 3 bar. So I suspect the mixer will wind back cold water flow as far as it can, to achieve the target flow temperature. As a consequence you have rubbish flow.
Try
Switch shower on, open one or more cold taps, see what happens. If you are getting big pressure differences that should help identify.
-
Has anyone seen this problem before? Huge anticycling times
4 weeks ago
-
Bosch CS5800i 5kW - Experience So Far
1 month ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
1 month ago
-
Yes, the "zoning with ASHP" topic again...
7 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
1 year ago
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 264 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
A while back I had a Y strainer fitted on the external ...
By jeegnesh , 10 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge unfortunately mine is a structure borne no...
By swwils , 42 minutes ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
So to clarify (and rephrase the problem into my own ter...
By Majordennisbloodnok , 1 hour ago
-
RE: Free Ecoheat Heat Pump Install
This is an interesting way of looking at it, and I can ...
By Mars , 2 hours ago
-
RE: Configuring third party dongle for Ecodan local control
That's a good spot and a valuable insight, @sheriff-fat...
By Majordennisbloodnok , 2 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@majordennisbloodnok And did ‘Honey’ order it for you? ...
By Toodles , 3 hours ago
-
RE: Setback savings - fact or fiction?
@robs — thanks again for your detailed comments. Some r...
By cathodeRay , 16 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 20 hours ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 21 hours ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 21 hours ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 22 hours ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 24 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 1 day ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 1 day ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 2 days ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 2 days ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 2 days ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 3 days ago