Looking for help with a Mitsubishi FTC2BR controller
Hi everyone. Long story short, my installation did not qualify for a grant and the build project was well over budget, so got a plumber in for hardware install and sparky for wiring etc.
The heat pump is a 5kw Ecodan with FTC2BR bought as package. Stats, manifold, wiring centre are Wunda.
The sparky (who has since done a Mitsubishi installer course) says the FTC, shortly after start up, commands the circulation pump off, which then causes the heat pump to shut down as there is no flow. This happens on both DHW and UFH cycles. System uses a zone valve each rather than a 3 way valve.
Has anyone had a similar experience with the FTC2BR or could offer any insight into why the circulation pump is being commanded off? Mitsubishi technicals response to my sparky was basically 'bin the controller and buy an FTC6' which obv I’m not exactly happy to do…!
Thanks all, biggles.
In addition to my reply on Buildhub. Have you considered dumping all the third party rubbish and then you have no need for the FTC2BR.
I doubt you need any of the third party stuff, just set to weather compensation and leave the heat pump to get on with it. If you have a thermostat that stops things you are flowing to hot and impacting CoP.
Hi, yes, planning to use the stats as safety limits, ditto mixer on manifold as safety limit to avoid floor over heating, and run the ashp on weather compensation. I’ll use manually set zone valves for trimming.
But as I understand it, this is what the FTC2BR does (controlling the heat pump flow temp and therefore weather compensation ) so I don’t understand your suggestion of getting rid of it?
@biggles welcome to the forums, and thanks for sharing your experience with us. It sounds like you’ve had quite a journey with your installation.
I reached out to Mitsubishi on your behalf to get some clarity.
Basically, the FTC2BR is specifically designed to work with a Building Management System (BMS) and isn’t a standalone controller like the FTC6. Essentially, it relays commands from the BMS to the heat pump but can’t control the heat pump on its own without third-party BMS inputs. Mitsubishi mentioned that this should have been clear to whoever sold the system to you, which suggests it may not have been purchased directly through them.
While I understand it’s frustrating to be advised to upgrade to the FTC6, Mitsubishi confirmed there’s a valid reason for it, given the limitations of the FTC2BR in a non-BMS setup.
I know this probably isn’t the news you wanted, but if you have any more questions or need further advice, feel free to ask - there’s a lot of knowledge in this community, and we’re here to help! Hopefully, we can get you pointed in the right direction.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @bigglesHi, yes, planning to use the stats as safety limits, ditto mixer on manifold as safety limit to avoid floor over heating, and run the ashp on weather compensation. I’ll use manually set zone valves for trimming.
But as I understand it, this is what the FTC2BR does (controlling the heat pump flow temp and therefore weather compensation ) so I don’t understand your suggestion of getting rid of it?
Maybe not the most efficient way to run your heat pump. Your trimming is just done by balancing the loops. Instead of off or on commands from the thermostat.
If you want to protect the floor just use a pipe stat, then you are not running the heat pump hotter than is really needed and you can ensure the system has an always open flow path.
Deleting the FTC2BR as explained above by Mars. It is just an interface not a controller. Basically a fancy relay box.
Posted by: @bigglessafety limit to avoid floor over heating
Just to show you what occurs when you switch from DHW heating - max flow temp 60 degs.
Within about 40 secs the flow temperature drops from 60 to 30 degs. Has a slight bounce back up 33 after a few minutes. My piping length to diverter valve is 10 to 12m each way, so quite long.
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 354 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat loss based on gas usage
In a word yes. Measurements based on a sing...
By JamesPa , 4 minutes ago
-
RE: Experience - New Build / Complete New Heating System
Newbuild 200sq m house, 16kW? Somebody is having a lau...
By JamesPa , 10 minutes ago
-
RE: Heat pump not reaching flow temperature
I would describe this as either a fault or a configurat...
By JamesPa , 25 minutes ago
-
RE: I’m glad the cold spell is over!
Thanks for the update, @judith. Cold spells with heat p...
By Mars , 31 minutes ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
@johnbroome As I say I think you probably have a fau...
By JamesPa , 1 hour ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I started reading this thread thinking I would...
By Hook , 2 hours ago
-
RE: Please help with the settings ecodan
@sheriff-fatman when I increase it to number 3, the ...
By nose1972 , 2 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
So far as i can see no because its NOT connected to the...
By JamesPa , 2 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
I forgot to mention: Octopus measured our heat loss at ...
By Toodles , 3 hours ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
Thanks Mars and thank you for reaching out to so many p...
By iotum , 4 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @davec Manufacturer: Peak Energy Mode...
By DaveC , 4 hours ago
-
RE: Rate the quality of your heat pump design and installation
Well, the guy came out, turned the heat pump to max, we...
By razz , 4 hours ago
-
Midea R32 setup and bizarre running with lengthy off periods?
Hi I am new to the world of ASHP and have just had a re...
By Countryman Helmsley , 4 hours ago
-
RE: Setback savings - fact or fiction?
Given the weather has been relatively stable, the empir...
By Batpred , 5 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor That is very kind! Thank you so much.
By johnbroome , 6 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hi I am not sure how large your house is b...
By TechnoGeek , 7 hours ago
-
RE: Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
I've been thinking along similar lines to @tim441 from ...
By Sheriff Fatman , 7 hours ago
-
Thanks, @technogeek. Good to hear about the accuracy. ...
By Majordennisbloodnok , 8 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In my case it was a very specific pattern of behaviour ...
By Sheriff Fatman , 8 hours ago
-
RE: Vaillant aroTherm not heating with many faults
@ashp-bobba Yeah I'll give it a go, will check filter...
By Anon67 , 8 hours ago