(@bontwoody)
@papahuhu I would definitely check the upstairs radiators. If they were locked down too much, that would effect the volume of the system and might account for frequent defrosts and swings by Homely. How long has homely been learning your house?
There are some low cost monitoring options for samsungs which might help you diagnose what is wrong
(@papahuhu)
@bontwoody It’s been converted from 3 zone GCH to single open loop. All TRVs are fully open (on 5). I’ve bled it multiple times, there’s about 36l/min flow rate which although slightly less than nominal, should be fine.
Homely has been running it since Sept, I was running on “smart” mode but it was causing short cycling (4 or 5 starts/hr), homely told me to switch to “standard”. It went from short cycling to not short cycling but to the “on 50% off 50%” cycle I have now.
Installer is offering to remove the homely and move the Samsung control interface into the habitable area from the garage. What’s the reasonable value monitoring solution please, without the homely it’s not Wi-Fi enabled?
bontwoody
(@bontwoody)
@papahuhu OK. what about the lockshield valves, have you tried opening those with the TRVs set to max? Are the upstairs radiators a similar temperature to those on the ground floor? Have you got the Heat loss survey, if so does it flag the radaitors upstairs as being undersize for your flow temperature
Have a read of this:
https://community.openenergymonitor.org/t/monitoring-your-samsung-ashp-controller/27638
(@papahuhu)
@old_scientist
Thanks. How can it possibly detect frost if it’s not touching the coil please? It’s a good 5cm away from the fins.
The only way I can foresee it might work is if it’s measuring both temp and humidity and using the dew point and mass air flow and refrigerant temperature to calculate the theoretical rate of ice deposition.
bontwoody
(@bontwoody)
@papahuhu I think the rear sensor is probably a bit of a wild goose chase, unless its faulty.