Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is it normal to use power from the grid when running off the battery?
I've recently had a Solis hybrid inverter fitted, with a battery, and I am surprised to see that my energy use in the Octopus app shows between 130 and 300W used every half hour of the day while running off the battery/solar. This is average out at around 400Wh use all the time, plus the amount I have used overnight to charge the battery.
This doesn't seem normal, it seems a lot of energy to use.
The electrician who fitted it is coming out on Friday so I wanted to ask what other people are seeing on their bills before he comes.
@johnnyb I would say that is normal. Inverters I believe, control current flow by adjusting voltage levels so the power from various sources is directed into your home. Unfortunately the voltage on the grid also fluctuates which causes momentary imports from the grid into your home instead of from your batteries, however the inverter should react to this and adjust itself to get the battery back supplying your house.
This happens on my solar / battery system and is normal I would say. I also see on occasions power actually being exported to the grid for brief moments ( 2 to 8 seconds ) again due to voltage fluctuations on the grid etc. Up until today however I was not getting paid for the exports! 😀
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
Posted by: @johnnybI've recently had a Solis hybrid inverter fitted, with a battery, and I am surprised to see that my energy use in the Octopus app shows between 130 and 300W used every half hour of the day while running off the battery/solar. This is average out at around 400Wh use all the time, plus the amount I have used overnight to charge the battery.
This doesn't seem normal, it seems a lot of energy to use.
The electrician who fitted it is coming out on Friday so I wanted to ask what other people are seeing on their bills before he comes.
Yes, you will have some import unfortunately.
The inverter as mentioned above will sometimes overshoot as it tries to balance the demand.
You may also exceed your inverter rating if the demand is greater.
300w is very high though every half hour (unless your inverter rating is maxed out and additional import is needed).
My inverter tends to overshoot on average by about 20w an hour (and undershoot also, but I don't have an export licence and can't claim that back).
@bash If I am to believe the Tesla app, the Gateway will ‘phone home’ and sniff the grid every so often during the hours set to use battery power (higher rates of tariff). Perhaps @transparent may know, if this is some form of ‘housekeeping’ routine to keep the system in sync with the grid perhaps. The connections shows a draw of 0.1 kW for perhaps 5 seconds or so then ‘hangs up’ again. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodles@bash If I am to believe the Tesla app, the Gateway will ‘phone home’ and sniff the grid every so often during the hours set to use battery power (higher rates of tariff). Perhaps @transparent may know, if this is some form of ‘housekeeping’ routine to keep the system in sync with the grid perhaps. The connections shows a draw of 0.1 kW for perhaps 5 seconds or so then ‘hangs up’ again. Regards, Toodles.
I don't know Toodles. We have a Solis inverter, very similar to @JohnnyB and I was referring to this more specifically. I am not familiar with the Tesla Powerwall.
@bash I was thinking that maybe this might be a generic practice for systems attached to the grid, hence my asking if @transparent might know. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Yes @toodles - I believe that the majority of grid tied equipment with the potential to export do indeed draw small quantities of power from the grid.
In the Sunsynk inverters, which are relatively new to me, I notice that there is a parameter which can be configured to say how much this Trickle Current can be.
I'm not wholly convinced that the reason stated by Sunsynk is the entire story.
However, I can imagine that all inverter manufacturers would err on the side of drawing enough electricity to prevent pre-paid meters cutting power to the home.
Save energy... recycle electrons!
Posted by: @johnnybI've recently had a Solis hybrid inverter fitted, with a battery, and I am surprised to see that my energy use in the Octopus app shows between 130 and 300W used every half hour of the day while running off the battery/solar. This is average out at around 400Wh use all the time, plus the amount I have used overnight to charge the battery.
This doesn't seem normal, it seems a lot of energy to use.
The Solis S6 has various modes of use. I currently have it self to prioritise self use. I created a soliscloud account and use the app to change the config (a bit more is available via the buttons on the inverter). There is also browser based access to soliscloud.
This is set under "Storage mode". In that same user menu, you also find various settings like export controls, calibration (I left at the default -30), whether the battery can or not be charged from grid, etc.
I find the app useful to check what is happening (in the attached screenshot, the power being used by the various circuits is shown). By default, it only updates info every 5 minutes, but you can ask Solis to change this.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
This isn't working out as a small amount. I've downloaded the half hourly import readings from Octopus this evening and it is averaging 370W per hour when the battery is discharging, or 6.6kWh or nearly £2 worth in the 18 hours the battery isn't charging. I think there is something wrong as that is rather a lot of electricity.
If anyone else has half hourly bills or can download their use in a spread sheet it would be interesting to here what is normal.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@batpred I may be asking you for more info in how you have your inverter set up as it seems a similar model to mine. I have just seen your post with the screenshot of your Octpus account and no import during the day. That is reasurring as mine looks quite different to yours at the moment.
The electrician so coming out tomorrow to run through a few things with me and I will ask him if there is anything he is aware of that needs changing.
Edited to add:
I see we posted at similar times. I am going to read through your posts about your inverter and see what info I can glean. Thanks.
@johnnyb I have a Growatt, and I download my half hourly data from Octopus and analyse it every month. Other than peak winter when heat pump is running, we don't import from the grid outside the off-peak hours. Maybe, occasionally like 20 Wh. and that too only briefly. But, not to the tune of 6.6 kWh in a day.
16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Bosch Induction Hob
Pod Point Solo 3 charger
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 292 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago