Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Is it normal to use power from the grid when running off the battery?

44 Posts
8 Users
5 Reactions
1,880 Views
(@johnnyb)
Estimable Member Member
Joined: 1 year ago
Posts: 114
Topic starter   [#2747]

I've recently had a Solis hybrid inverter fitted, with a battery, and I am surprised to see that my energy use in the Octopus app shows between 130 and 300W used every half hour of the day while running off the battery/solar. This is average out at around 400Wh use all the time, plus the amount I have used overnight to charge the battery.

This doesn't seem normal, it seems a lot of energy to use.

The electrician who fitted it is coming out on Friday so I wanted to ask what other people are seeing on their bills before he comes.


This topic was modified 3 months ago 3 times by JohnnyB

   
Quote
TechnoGeek
(@technogeek)
Estimable Member Member
Joined: 3 years ago
Posts: 174
 

@johnnyb I would say that is normal. Inverters I believe, control current flow by adjusting voltage levels so the power from various sources is directed into your home. Unfortunately the voltage on the grid also fluctuates which causes momentary imports from the grid into your home instead of from your batteries, however the inverter should react to this and adjust itself to get the battery back supplying your house.

This happens on my solar / battery system and is normal I would say. I also see on occasions power actually being exported to the grid for brief moments ( 2 to 8 seconds ) again due to voltage fluctuations on the grid etc. Up until today however I was not getting paid for the exports! 😀

 

Regards


5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System


   
ReplyQuote
 Bash
(@bash)
Estimable Member Member
Joined: 6 months ago
Posts: 163
 

Posted by: @johnnyb

I've recently had a Solis hybrid inverter fitted, with a battery, and I am surprised to see that my energy use in the Octopus app shows between 130 and 300W used every half hour of the day while running off the battery/solar. This is average out at around 400Wh use all the time, plus the amount I have used overnight to charge the battery.

This doesn't seem normal, it seems a lot of energy to use.

The electrician who fitted it is coming out on Friday so I wanted to ask what other people are seeing on their bills before he comes.

Yes, you will have some import unfortunately.

The inverter as mentioned above will sometimes overshoot as it tries to balance the demand.

You may also exceed your inverter rating if the demand is greater.

300w is very high though every half hour (unless your inverter rating is maxed out and additional import is needed).

My inverter tends to overshoot on average by about 20w an hour (and undershoot also, but I don't have an export licence and can't claim that back).

 



   
ReplyQuote



Toodles
(@toodles)
Famed Member Contributor
Joined: 4 years ago
Posts: 2694
 

@bash If I am to believe the Tesla app, the Gateway will ‘phone home’ and sniff the grid every so often during the hours set to use battery power (higher rates of tariff). Perhaps @transparent may know, if this is some form of ‘housekeeping’ routine to keep the system in sync with the grid perhaps. The connections shows a draw of 0.1 kW for perhaps 5 seconds or so then ‘hangs up’ again. Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
ReplyQuote
 Bash
(@bash)
Estimable Member Member
Joined: 6 months ago
Posts: 163
 

Posted by: @toodles

@bash If I am to believe the Tesla app, the Gateway will ‘phone home’ and sniff the grid every so often during the hours set to use battery power (higher rates of tariff). Perhaps @transparent may know, if this is some form of ‘housekeeping’ routine to keep the system in sync with the grid perhaps. The connections shows a draw of 0.1 kW for perhaps 5 seconds or so then ‘hangs up’ again. Regards, Toodles.

I don't know Toodles. We have a Solis inverter, very similar to @JohnnyB and I was referring to this more specifically. I am not familiar with the Tesla Powerwall.

 



   
ReplyQuote
Toodles
(@toodles)
Famed Member Contributor
Joined: 4 years ago
Posts: 2694
 

@bash I was thinking that maybe this might be a generic practice for systems attached to the grid, hence my asking if @transparent might know. Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
👍
1
ReplyQuote



Transparent
(@transparent)
Famed Member Moderator
Joined: 4 years ago
Posts: 3134
 

Yes @toodles - I believe that the majority of grid tied equipment with the potential to export do indeed draw small quantities of power from the grid.

In the Sunsynk inverters, which are relatively new to me, I notice that there is a parameter which can be configured to say how much this Trickle Current can be.

image

 

I'm not wholly convinced that the reason stated by Sunsynk is the entire story.

However, I can imagine that all inverter manufacturers would err on the side of drawing enough electricity to prevent pre-paid meters cutting power to the home.

 


This post was modified 3 months ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 767
 

Posted by: @johnnyb

I've recently had a Solis hybrid inverter fitted, with a battery, and I am surprised to see that my energy use in the Octopus app shows between 130 and 300W used every half hour of the day while running off the battery/solar. This is average out at around 400Wh use all the time, plus the amount I have used overnight to charge the battery.

This doesn't seem normal, it seems a lot of energy to use.

The Solis S6 has various modes of use. I currently have it self to prioritise self use. I created a soliscloud account and use the app to change the config (a bit more is available via the buttons on the inverter). There is also browser based access to soliscloud.

This is set under "Storage mode". In that same user menu, you also find various settings like export controls, calibration (I left at the default -30), whether the battery can or not be charged from grid, etc.

I find the app useful to check what is happening (in the attached screenshot, the power being used by the various circuits is shown). By default, it only updates info every 5 minutes, but you can ask Solis to change this. 

 

image

 

 


8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@johnnyb)
Estimable Member Member
Joined: 1 year ago
Posts: 114
Topic starter  

This isn't working out as a small amount.  I've downloaded the half hourly import readings from Octopus this evening and it is averaging 370W per hour when the battery is discharging, or 6.6kWh or nearly £2 worth in the 18 hours the battery isn't charging. I think there is something wrong as that is rather a lot of electricity.

If anyone else has half hourly bills or can download their use in a spread sheet it would be interesting to here what is normal.



   
ReplyQuote



Batpred
(@batpred)
Prominent Member Member
Joined: 1 year ago
Posts: 767
 

@johnnyb I added that to the Solis inverter thread

I get 0w import during the day


This post was modified 3 months ago by Batpred

8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC


   
ReplyQuote
(@johnnyb)
Estimable Member Member
Joined: 1 year ago
Posts: 114
Topic starter  

@batpred I may be asking you for more info in how you have your inverter set up as it seems a similar model to mine.  I have just seen your post with the screenshot of your Octpus account and no import during the day.  That is reasurring as mine looks quite different to yours at the moment.

image

The electrician so coming out tomorrow to run through a few things with me and I will ask him if there is anything he is aware of that needs changing.

 

Edited to add:

I see we posted at similar times. I am going to read through your posts about your inverter and see what info I can glean.  Thanks.


This post was modified 3 months ago by JohnnyB

   
ReplyQuote
(@chandykris)
Estimable Member Member
Joined: 2 years ago
Posts: 152
 

@johnnyb I have a Growatt, and I download my half hourly data from Octopus and analyse it every month. Other than peak winter when heat pump is running, we don't import from the grid outside the off-peak hours. Maybe, occasionally like 20 Wh. and that too only briefly. But, not to the tune of 6.6 kWh in a day.


16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Bosch Induction Hob
Pod Point Solo 3 charger


   
ReplyQuote



Page 1 / 4



Share:

Join Us!

Latest Posts

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security PRO
This Site Is Protected By
Shield Security PRO