Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
HOT TIP - DHW Cylinder Thermostat
Whilst running some tests on the disinfection cycle of my Daikin Mono 16kw I observed that the temperature of the booster heater was only getting up to 59.9C and not reaching the 60c mark. I had set it to reach 60C for 5 mins to satisfy the legionella cycle but it had been running for 30 mins and could not get pass that magic 60c number.
I had a read through the cylinder book and it said "make sure the thermostat is FULLY insterted", so i unscrewed the thermostat gland and found that i could push in the probe another 2-3 inches. Immediately the reported temperature of the DHW went to 62.9C! So just by pushing in the probe right to the end of the pocket the 60c was satisfied and the disinfection cycle completed for the first time ever!
By my calculations that will save 0.5kw of additional heating every time the DHW is run, so that will be a saving of over 180KW per year just by pushing in the probe where it should be.
This is because the water would be heating an extra 3c above the setpoints for my Eco and Confort settings.
see also
Correction, it should say saving of over 540KW per year just by pushing in the probe - as i have HW heat 3 x per day
-
Homely setup on daikin heat pump
2 months ago
-
Ecodan unable to hit legionella target temp - what's the consensus?
4 months ago
-
Warm weather and heat pumps.
1 year ago
-
Oversized Daikin 9kw
1 year ago
-
Daikin COP / energy used measurement from MMI
2 years ago
- 26 Forums
- 2,623 Topics
- 61.3 K Posts
- 909 Online
- 7,004 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Grant Aerona3 - Home Assistant control via Modbus
I'm trying to control my Grant Areona 3 with modbus, I ...
By Vanq , 2 minutes ago
-
Is Traditional Radiator Balancing Tosh?
So, conventional HP wisdom says to balance the rads by ...
By markspencersmith , 25 minutes ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: appliances direct/superheat Model: 7Kw ...
By Adrian , 33 minutes ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
As a final update on this thread from me; Ribble Valley...
By DaveC , 36 minutes ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
My local council (Highland Council) advised me to ask l...
By seoras , 1 hour ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Fantastic. This is all I needed. Afew planning applic...
By Batpred , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
Commentary on DCs and the grid in the EU. A bit on some...
By Jeff , 8 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
If you put a fan in a pipe you get a much more efficien...
By bobflux , 17 hours ago
-
RE: Mitsubishi ecodan settings
As the owner of a 8kW Ecodan R290 maybe I can help. ...
By RobS , 17 hours ago
-
Wall mounting makes sense. We are now looking for an in...
By Batpred , 21 hours ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you, watson did allow me to find this one! Our ...
By Batpred , 21 hours ago
-
RE: Our 10 year old Grant heat pump failed
Sorry to hear. Grant seem to be selling the R290 pump...
By Batpred , 22 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
.. apparently with american fuel. 🙃
By Batpred , 22 hours ago
-
RE: The Watchdog That Watched and Waited
Spot on. The watchdog that knows how to never take the ...
By Batpred , 22 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Yes, the cost difference may be marginal, if you are lu...
By Batpred , 22 hours ago
-
RE: Don’t Install a Heat Pump Until You Read This
In our latest update, we attempt to show what a poor he...
By Mars , 23 hours ago
-
RE: Heat Pump Pipe Sizing Question
No the retrofit strategy is already published. It's on...
By JamesPa , 23 hours ago
-
RE: Ecodan spells out end of R32 for real environmental alternative
I think I saw the answer to this on another thread but ...
By Batpred , 23 hours ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
This is what we are trying to avoid if we go Ecodan, mu...
By Batpred , 24 hours ago
-
Great points, I agree it is overused. It is also a grea...
By Batpred , 24 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
On old (non inverter) compressors there’s sometimes a ‘...
By robl , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 3 days ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 3 days ago