Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Heat Pump SCOPs – The Truth Might Not Be What You Think

16 Posts
12 Users
6 Reactions
4,252 Views
(@david-stanford)
Active Member Contributor
Joined: 2 years ago
Posts: 2
Your energy: 0 kWh
Topic starter   [#1909]
wpf-cross-image

When it comes to ASHP efficiency, there’s often a lot of discussion and misunderstanding. SCOP (Seasonal Coefficient of Performance) is a key measure of efficiency, but what does it really tell us, and how can we interpret it? After analysing data from the top 20 heat pumps on heatpumpmonitor.org – all with SCOPs above 4.0 over the past 365 days – I’ve uncovered some insights that might surprise you.

What the Data Reveals (At Time of Writing)

  1. Air Source Dominates: Of the top 20 heat pumps, 19 are air source, and only one is ground source.
  2. System Volume is Often Overlooked: Surprisingly, 75% of users don’t calculate or record their system volume. For those that do, systems with 15 litres per kW of peak capacity or more perform best. The top-performing system has 16 l/kW. However, going far beyond 15 l/kW offers diminishing returns, and there isn’t enough data to confirm its benefits.
  3. Manufacturer Diversity: The top-performing models come from a range of manufacturers, including Viessmann, Nibe, Vaillant, Grant, Samsung, Mitsubishi and Acond. This highlights that system design is often more critical than the brand.
  4. Refrigerants Don’t Make a Big Difference: Among the top six ASHPs, there is an even split between those using R290 and R32 refrigerants, suggesting no significant efficiency advantage to either.
  5. Single-Zone Systems Rule: Every system achieving a SCOP above 4.0 is a single-zone setup. Multi-zone systems seem to struggle to match this level of efficiency.
  6. Flow Temperatures are Key: Systems with a maximum flow temperature of 45°C or lower dominate the top-performing list. Higher flow temperatures tend to drag down efficiency.
  7. Modest DHW Settings Win: The top six ASHPs have domestic hot water (DHW) set to an average temperature of 45°C, reinforcing the importance of keeping DHW temperatures modest for better efficiency.
  8. Building Efficiency is Less Relevant: Interestingly, building efficiency (measured in W/m2) varies wildly among the top systems, from 19 to 76 W/m2. This suggests that SCOP is influenced more by system design than the property’s insulation or efficiency level.
  9. Supplementary Technologies Enhance Results: Over half of the top 20 systems either don’t heat DHW or use supplementary technologies such as hybrid boilers, photovoltaic (PV) panels or solar thermal systems to improve performance.

Notable Features in Top Systems

  • Buffer Vessels: These are present in many high-performing systems.
  • 10mm Microbore Pipework: Often considered suboptimal, this pipework appears in some top-performing setups, proving that careful system design can overcome perceived limitations.
  • Thermostatic Radiator Valves (TRVs): Despite some reservations, TRVs are used in many systems, likely in specific zones like bedrooms.

Key Takeaways

From this analysis, a few clear lessons emerge:

  • Aim for 15+ l/kW System Volume: This seems to be a reasonable rule of thumb for optimising efficiency.
  • Focus on System Design: The manufacturer matters less than a well-designed, balanced and commissioned system.
  • Refrigerant Choice Isn’t Critical: Both R290 and R32 perform equally well in top systems.
  • Stick to Single-Zone Systems: Multi-zone setups don’t achieve the same efficiency levels.
  • TRVs Are Acceptable: While they may reduce efficiency slightly, TRVs can work well if carefully implemented, likely in specific areas like bedrooms.
  • Keep Flow Temperatures Below 45°C: Lower flow temperatures are crucial for high SCOPs.
  • Lower DHW Temperatures: Reducing DHW temperatures has a substantial positive impact on system efficiency.
  • Don’t Stress About Building Age or Efficiency: A correctly sized heat pump can deliver excellent results in properties with varying levels of efficiency.
  • Supplementary Technologies Help: PV, solar thermal, and hybrid systems can boost overall system performance.



   
Like
3
Quote
Mars
 Mars
(@editor)
Replacing my heat pump
Illustrious Member Admin
Joined: 6 years ago
Posts: 5047
Your energy: 80 kWh
 

Some super interesting findings. Not surprised about heating DW to 45C being the most efficient way to go. That's what we set ours to.


Dad’s Outside with the Heat Pump Again
He wanted to save the planet. His family just wanted him to come inside.
Get the book → · Free UK shipping
The Ultimate Guide to Heat Pumps · Britain’s Heat Pump Shitshow
Heat Pumps Explained · From Zero to Heat Pump Hero · Bodge Buster
From Zero to Heat Pump Hero and Bodge Buster are rewritten and updated for 2027.
New to heat pumps? Heat Pump Fundamentals course — 50% off with INTRO50.


   
ReplyQuote
(@A E Deans)
Joined: 2 years ago
Posts: 4
 

Thanks Mars I am getting 3.7 Scop with an oversized Mitsubishi 8.5 kw heat pump . Still
Trying different settings to try and improve it. Have installed open energy monitoring and
It’s under Dalkieth. Set hot water 47c . Does anyone know if switching down pump speed helps presently 25.61 l/m
Cheers Andrew Scotland



   
ReplyQuote
JamesPa
(@jamespa)
Vaillant
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5756
Your energy: 114 kWh
 

↑

Does anyone know if switching down pump speed helps presently 25.61 l/m

Pump speed needs to be sufficient to carry away the energy, any less wont do, any more is wasting energy.

The energy carried away is flow rate (l/s) * specific heat capacity of the transfer medium (water or glycol as appropriate) * deltaT at the heat pump (normally designed for 5). 

Assuming water and 5C DT thats 25.61/60*4200*5 =8.9kW, so just abut right for an 8.5kW pump!

If the heat pump is oversized then there may be the potential to reduce the water pump speed.  Some heat pumps modulate pump speed according to energy demand.  If yours does or can then thats an option.  Otherwise you could try turning it down on the water pump itself but the heat pump may complain.  The energy saving from turning down the water pump is small however so this isnt likely to make a massive difference.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

 Gary
(@gary)
Reputable Member Member
Joined: 4 years ago
Posts: 350
Your energy: 0 kWh
 

I have tried my 8.5kw Ecodan at various pump speeds its currently at pump speed 2 that gives 14L/min, the recommended flow rate for 8.5 Ecodan is 15.4L/min, to achieve the optimum dT of 8, not 5 that you see quoted.

Using the mass flow calc James quoted you get to 8.6kw at dT8 so that makes sense as well.

The advantage of using a lower flow rate is that the Ecodan doesn't have its own internal pump so ours is in the airing cupboard so the slower the pump the less noise it makes too



   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 5 years ago
Posts: 1069
Your energy: 2 kWh
 

Two other things that greatly effect SCOP but havent been mentioned are the climate where you are living and what you deem to be a comfortable internal temperature.
Someone living in London who is happy with a 19C indoor tempearture will have a much better SCOP than someone with exactly the same system living in the North of Scotland who likes a 22C room.


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
Like
Bang on
2
ReplyQuote
(@mike-h)
Reputable Member Member
Joined: 5 years ago
Posts: 200
Your energy: 0 kWh
 

Posted by: @david-stanford
↑

Aim for 15+ l/kW System Volume: This seems to be a reasonable rule of thumb for optimising efficiency.

Can you explain the mechanism for this effect? Could it just be coincidental rather than causal? System volume may prevent short cycling, but there are other ways of achieving that. 



   
ReplyQuote
(@A E Deans)
Joined: 2 years ago
Posts: 4
 

Yes I have room temperature 20.5 and live in central belt . Perhaps I was overthinking scop it’s gone back to daily cop of 4.5 . Will try lower pump speed as heat pump comes off and on 2 or 3 times an hour
thanks for commenting



   
ReplyQuote

(@A E Deans)
Joined: 2 years ago
Posts: 4
 

Thanks I will try that and look at results



   
ReplyQuote
DREI
 DREI
(@drei)
Estimable Member Contributor
Joined: 1 year ago
Posts: 99
Your energy: 0 kWh
 

A heat pump is only as good as the desired room temperature. Bearing in mind that optimal room temperature for cognitive function sits between 21 and 24 degrees, with average around 22/23 degrees. 45 flow temperature relates to around 42.5 mean water temperature (MWT). Make sure to use that with your heat loss calculation, desired room temp and radiator sizes for best outcome.



   
ReplyQuote
DREI
 DREI
(@drei)
Estimable Member Contributor
Joined: 1 year ago
Posts: 99
Your energy: 0 kWh
 

You can even go as low as 40c flow temp, if you want a high SCOP, as long as your radiators are sized correctly and you use the correct desired room temp, nothing is impossible. I don't think you will find any radiators that can do 40c flow rate and room temp higher than 21c, unless going to silly 3 meters K3 rads or very very expensive multi chamber rads (£10k per radiator).



   
ReplyQuote
(@old_scientist)
Samsung
Prominent Member Member
Joined: 2 years ago
Posts: 581
Your energy: 24 kWh
 

Posted by: @drei
↑

You can even go as low as 40c flow temp, if you want a high SCOP, as long as your radiators are sized correctly and you use the correct desired room temp, nothing is impossible. I don't think you will find any radiators that can do 40c flow rate and room temp higher than 21c, unless going to silly 3 meters K3 rads or very very expensive multi chamber rads (£10k per radiator).

We run a standard flow temp of around 32C all year round (certainly between 30-35C) and achieve a comfortable (for us) 20C room temp. Our radiators are all of standard K2 types. Other than on the very coldest of nights, even running a flow temp of 30C overnight puts out more heat than required as we like a setback of 18C for sleeping.

As long as your emitters are large enough to dissipate the required amount of heat at reduced flow temps, very low flow temps are possible. The limiting factor for us is actually dissipating the ~3.5kW of heat produced by the heat pump when running at minimum during milder weather, hence the required 32C flow temps. Any lower and the radiators cannot dissipate that 3.5kW output flowing from the heat pump.

 


Samsung 12kW gen6 ASHP with 50L volumiser and large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW). Net Zero


   
ReplyQuote