Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Since the UK outdoor temperature has dropped below 3 degrees our heat pump is unable to go over 40 degrees flow temp. It reaches 40 degrees for shortish period before starting a defrost drops back to 33ish and starts again in a loop.
The installer has enabled the back up heater which resolves the issue but why is this happening? Is it standard practise to use the backup heater for this during cold spells?
It is unlike to be an issue with the size of the heat pump as this has already been upgraded to a 16KW from an 11KW to resolve the a similar issue where the flow temps where only reaching 32 degrees before getting into a defrost cycle.
Can you tell us what the weather compensation settings are please and also is there a buffer tank/LLH or (separate question) a volumiser. Have you got any kind of low noise/night mode/noise reduction set? Also whats the system volume
Backup heater isn't 'standard practice' but is a known way to deal with a heat pump that is either undersized or operating beyond the system, design envelope (eg my system is designed for -2, its -5 today).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@johnd, I'd hesitate before saying that's definitely wrong, but I'm certainly sceptical. Defrost cycles are certainly a big hit on performance but they're far more affected by damp weather than cold weather - that's why heat pumps work perfectly well in Scandiwegia.
Just to start the ball rolling before better brains than mine come along here, are you able to tell us what heat pump you have, what size of house it's supposed to be heating (with any heat loss info if you have it, but don't worry if you haven't) and whereabouts in the UK your house is?
**edited to add that said better brains than mine definitely includes @jamespa with whom I cross-posted**
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@jamespa There isn't a volumizer or buffer tank. Weather compensation is enabled although it doesn't seem to alter the flow temp automatically based outdoor temps. Low is 0 degrees and high is 15 degrees. I do not know what the system volume is, there are 19 radiator with a mix of 10mm and 15mm plastic pipework. No noise reduction enabled. Octopus did the heat loss calcs at -3 @ 50 degrees = 11KW heat loss. The 11KW heatpump which was installed has been upgraded to a 16kw as the manufacturer deemed it too small when we initially had issues with getting the flow temp above 32 when the outside temp dropped below 3 degrees.
@majordennisbloodnok Its a Peak Energy Products V therm 16KW unit. The house is detached, 3 storey and 5 bedrooms based in Lancashire. Heat loss according to Octopus onsite survey is 11KW.
Posted by: @johndWeather compensation is enabled although it doesn't seem to alter the flow temp automatically based outdoor temps. Low is 0 degrees and high is 15 degrees
That doesn't make much sense as it should alter the flow temp, that's what WC is.
0 and 15 are presumably the outside temps, what are the corresponding flow temps set on the curve? Also with 0 being the low OAT point the ft will flatline at this temp so as soon as oat drops below it won't be warm enough. This needs to be changed.
Can you do some screenshots of the WC config screen? Also how often is defrost occurring and is there anything about where it is sited that would restrict airflow or make the air particularly humid? According to their website/manual "Our unique defrost process means we get better performance in the critical temperature range of between -2°C & +2°C because
our units go into defrost mode less often."!
The online manual is pretty short on detail (I think they have edited out all the useful bits), hopefully the UI is reasonably self explanatory! Is this an Octopus install or someone else?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@johnd, what you’re experiencing is common with air source heat pumps in colder weather in the UK where it’s humid during cold snaps. When the outdoor temperature drops below around 3/4C, frost tends to build up on the outdoor coil, which reduces the heat pump’s ability to extract heat efficiently. To clear this frost, the heat pump initiates a defrost cycle, during which the flow temperature can drop temporarily, often from +40C down to the low 30s. This cycling between heating and defrost is normal and necessary to maintain system performance.
The backup heater is designed to support the system during these cold spells when the heat pump alone can’t maintain the desired flow temperature continuously, especially during defrost cycles. So yes, it is standard practice for some units for the backup heater to come on during cold weather to ensure your home stays warm. Even upgrading the heat pump size doesn’t eliminate the need for defrost cycles or backup heating because the physics of frost formation and heat extraction limits remain.
Having said that, one thing to consider is whether your system has sufficient water volume and proper flow rates. Insufficient system volume can make defrost cycles more noticeable inside the home due to rapid temperature drops, and get stuck in the cycle of flow temperatures not getting above 40C because you’re persistently battling defrosts. Devices like volumisers can help by maintaining stable flow temperatures during defrost, preventing sudden cold blips in your radiators.
I therefore wonder if you have sufficient volume from what you’re describing.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @johndSince the UK outdoor temperature has dropped below 3 degrees our heat pump is unable to go over 40 degrees flow temp. It reaches 40 degrees for shortish period before starting a defrost drops back to 33ish and starts again in a loop.
The installer has enabled the back up heater which resolves the issue but why is this happening? Is it standard practise to use the backup heater for this during cold spells?
It is unlike to be an issue with the size of the heat pump as this has already been upgraded to a 16KW from an 11KW to resolve the a similar issue where the flow temps where only reaching 32 degrees before getting into a defrost cycle.
is the house warm enough?
I have spoken to the installer, apparently the defrost cycles is on a fixed 45 minute cycle, it does not use a sensor to manage it. He has adjusted the cycle and I have seen a huge improvement. Has anyone has this issue with fixed timed defrost cycles?
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 493 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 2 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 2 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 3 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 4 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 4 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 5 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 7 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 8 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 10 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 12 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 16 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 2 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago