Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsu Zubadan flow temperature issue
Ive been doing some work with a 12kW Zubadan system that wasnt performing well. Ive established that it is oversized and sorted out some poor insulation problems. It appeared to be running nicely (if rather hot) as shown by the plots below:
The owners have always struggled to heat the house adequately in cold conditions so I was interested to see what happened in this cold snap. The next day at about 8.30pm I had a message to say that they were cold, as I cant adjust the WC curve remotely, I switched to a fixed flow temperature of 55C. The red line shows the target flow temperature.
Unfortunately the flow temperature started to oscillate wildly, with the mean temperature probably reducing. The next day shows the problem clearly with the target flow temperature not being even nearly achieved.
Today, I managed to get to site and upped the WC curve at about 12 noon.
However the average flow temperature stayed well under target, so about about 3pm I switched to a constant flow temperature of 60C, but this still doesnt seem to be raising the average flow temperature.
Does anyone have an idea what is going on? The heat pump does have some fin damage due to being powerwashed. The radiator temperature was at about 38C when I was there, well below the flow temperature, this is after the pipework in the loft was reportedly insulated. Thanks in advance
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Update: The flow temperature has now stabilized at 60C as required, unlike the 55C constant flow temperature yesterday. Im going to leave it a while and if it stays that way switch back to the WC curve.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 2,722 Online
- 7,196 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
The installer visited yesterday and suggested the noise...
By JamesChatz , 46 minutes ago
-
RE: Heat Geek installations: share your experiences
I struggled with this problem as well. An independent t...
By L8Again , 1 hour ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
I am not here to defend Heat geek or anyone else, but I...
By JamesPa , 2 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Your house sounds a lot like mine. 2 surveyors each sp...
By JamesPa , 3 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
Thats true only if you do the wrong experiment. Done c...
By JamesPa , 4 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
@temperature_gradient Isn't that just describing a regu...
By Prunus , 4 hours ago
-
@etchedpixels I thought about that too, and between ...
By RonV. , 7 hours ago
-
RE: battery storage without solar
As of October 1st they need specific qualifications to ...
By EtchedPixels , 17 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 18 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 18 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 23 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 23 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 24 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 1 day ago