Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat Pump, DHW, UFH and Radiator Install
Ive just been over to help a friend with her ASHP which was tripping the consumer unit. Im pretty sure the problem is a leak which has shorted the pump. However the real issue is what she said to me was happening with the heating.
She informed me that the cylinder was heated every day to 50+C but that the same temperature water was being pumped around her UFH. When the room thermostat hit 20C the heat pump turned off. The upstairs radiators do not get hot.
I was gobsmacked but Im not a plumber so took her at her word and also took a picture of her setup.
Im not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
Thanks in advance
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Could it be that the valve has stuck open so that the higher temperature water intended for the DHW circuit is also flowing through the UFH manifold? Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles I suppose anything is possible. I wish I had took a better photo of the cylinder so I could perhaps look it up and see its connections. Perhaps its a thermal store? The UFH and Rad circuits each seem to have one two-way valve
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody My eyesight is not good enough to follow the pipework to those two valves so I cannot tell which from what however… another thing I cannot see is any insulation - I think most of those pipes need lagging! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected. I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.
Posted by: @bontwoodyIm not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
yes, exactly that.
But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH. What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespa@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected. I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.
Posted by: @bontwoodyIm not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
yes, exactly that.
But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH. What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.
Looking again I think the slightly hidden motorized valve has 3 ports, one directing water to the middle of the cylinder the other to the bottom. The flow to the CH and UFH (which does appear to be common without mixing) appears to come from the bottom. So perhaps this is a combined cylinder/butter tank, with the buffer tank below and the cylinder above. The bottom bit has an immersion, which may just be a backup.
Does that help?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@toodles LOL, I did point that out to her 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa Its a lot more than I had managed to work out James, so thanks yes. Ive offered to switch the pump for her as a belated wedding present, so when I go back I will take some more extensive pictures and trace some pipes. She said she was spending £180 per month on electricity bills so Im hoping that can be reduced substantially.
The heat pump looks on the big size for the house, but was also tipped forwards about 15 degrees so Ive done my best to level it as a temporary measure. Long term its position will be changed.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa I think you are spot on about the integrated buffer vessel, she has sent me her documentation. It was designed for a 50C flow temperature with UFH! There is no thermostatic mixer valve on it.
Im going to try and find out how to access the control unit and see whats going on once I change the pump. It a modern one similar to the Samsung unit from the outside.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So I have changed the pump (all working again) and had a better look around. There appear to be 2 x two way valves one on the upstairs rads and the other on the downstairs UFH.
There is a 3 way valve switching between heating and DHW as normal. Ive been into the installer settings to have a look but need some advice on the LG way of doing things so I will start a new thread.
Thanks for all your help.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody You are most welcome - not that I contributed much, but if it helped, I’m happy! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
That doesn't look like a thermal store to me.
I think it's a combined DHW cylinder (top) and 50-litre buffer tank (below).
Have a look at this diagram from the manufacturer's product literature.
At least that graphic has the ports labelled, which gives you a fighting chance of working out what each pipe is meant to do.
Save energy... recycle electrons!
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 days ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 month ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
3 months ago
-
Running my new Nibe ASHP efficiently
3 months ago
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 136 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 7 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 7 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 7 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 7 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 8 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 9 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 10 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 12 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 12 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 14 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 17 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 20 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago