Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Heat Pump, DHW, UFH and Radiator Install

13 Posts
4 Users
0 Reactions
2,923 Views
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1009
Topic starter   [#1837]

Ive just been over to help a friend with her ASHP which was tripping the consumer unit. Im pretty sure the problem is a leak which has shorted the pump. However the real issue is what she said to me was happening with the heating.

She informed me that the cylinder was heated every day to 50+C but that the same temperature water was being pumped around her UFH. When the room thermostat hit 20C the heat pump turned off. The upstairs radiators do not get hot.

I was gobsmacked but Im not a plumber so took her at her word and also took a picture of her setup.

Im not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?

IMG 0742

 

Thanks in advance

 

 


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
Quote
Toodles
(@toodles)
Famed Member Contributor
Joined: 4 years ago
Posts: 2711
 

Could it be that the valve has stuck open so that the higher temperature water intended for the DHW circuit is also flowing through the UFH manifold? Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1009
Topic starter  

@toodles I suppose anything is possible. I wish I had took a better photo of the cylinder so I could perhaps look it up and see its connections. Perhaps its a thermal store? The UFH and Rad circuits each seem to have one two-way valve


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



Toodles
(@toodles)
Famed Member Contributor
Joined: 4 years ago
Posts: 2711
 

@bontwoody My eyesight is not good enough to follow the pipework to those two valves so I cannot tell which from what however… another thing I cannot see is any insulation - I think most of those pipes need lagging! Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4714
 

@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected.  I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.  

 

Posted by: @bontwoody

Im not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?

yes, exactly that. 

But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH.  What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.  


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 4714
 

Posted by: @jamespa

@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected.  I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.  

 

Posted by: @bontwoody

Im not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?

yes, exactly that. 

But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH.  What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.  

Looking again I think the slightly hidden motorized valve has 3 ports, one directing water to the middle of the cylinder the other to the bottom.  The flow to the CH and UFH (which does appear to be common without mixing) appears to come from the bottom.  So perhaps this is a combined cylinder/butter tank, with the buffer tank below and the cylinder above.  The bottom bit has an immersion, which may just be a backup.

Does that help?

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote



bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1009
Topic starter  

@toodles LOL, I did point that out to her 🙂


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1009
Topic starter  

@jamespa Its a lot more than I had managed to work out James, so thanks yes. Ive offered to switch the pump for her as a belated wedding present, so when I go back I will take some more extensive pictures and trace some pipes. She said she was spending £180 per month on electricity bills so Im hoping that can be reduced substantially.

The heat pump looks on the big size for the house, but was also tipped forwards about 15 degrees so Ive done my best to level it as a temporary measure. Long term its position will be changed.


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1009
Topic starter  

@jamespa I think you are spot on about the integrated buffer vessel, she has sent me her documentation. It was designed for a 50C flow temperature with UFH! There is no thermostatic mixer valve on it.

Im going to try and find out how to access the control unit and see whats going on once I change the pump. It a modern one similar to the Samsung unit from the outside.

image

House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



bontwoody
(@bontwoody)
Noble Member Contributor
Joined: 4 years ago
Posts: 1009
Topic starter  

@jamespa @toodles

So I have changed the pump (all working again) and had a better look around. There appear to be 2 x two way valves one on the upstairs rads and the other on the downstairs UFH.

There is a 3 way valve switching between heating and DHW as normal. Ive been into the installer settings to have a look but need some advice on the LG way of doing things so I will start a new thread.

Thanks for all your help.


House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
Toodles
(@toodles)
Famed Member Contributor
Joined: 4 years ago
Posts: 2711
 

@bontwoody You are most welcome - not that I contributed much, but if it helped, I’m happy! Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
Joined: 4 years ago
Posts: 3157
 

That doesn't look like a thermal store to me.

I think it's a combined DHW cylinder (top) and 50-litre buffer tank (below).
Have a look at this diagram from the manufacturer's product literature.

image

At least that graphic has the ports labelled, which gives you a fighting chance of working out what each pipe is meant to do.


Save energy... recycle electrons!


   
ReplyQuote