(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3383
 

Posted by: @crimson

Other half informed me exact changes by engineer:

  • flow temp max up to 45
  • UFH manifold - speed 3 (no idea why!!)
  • connected loose wire

So now of course installer will have a get out of jail free stating manufacturer made changes.

They cant get away with this argument, all three changes are easily reversible if the installer thinks the wrong thing was done!

Putting the flow temp up should make a difference (at the expense of efficiency) and is a good 'test' move IMHO. If it works it proves that there is no fundamental problem, and leads directly to a discussion about efficiency and how removing the LLH would maintain both house temperature and efficiency.

Is there any possibility that the reason its not currently heating is just air in the system/no system pressure?  Bleeding/topping up are things that householders are going to do/have to do and, unless they are reckless, its not reasonable to void warranty if householders carry out this basic piece or ongoing maintenance, particularly just after a system has been filled and is thus quite possibly full of dissolved air  (you know it is, you can hear gurgling).


This post was modified 1 hour ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@crimson)
Honorable Member Member
Joined: 2 years ago
Posts: 290
Topic starter  

Posted by: @grantmethestrength

@crimson mate you have proper been through the wars, I really hope you get some resolution, and soon.

 

thanks. Just heard a big clunk.

secondary pump is now off.

P1 error on the Grant panel

 



   
ReplyQuote
(@grantmethestrength)
Reputable Member Member
Joined: 10 months ago
Posts: 147
 

Yup that will be your lack of pressure


Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery


   
ReplyQuote



(@crimson)
Honorable Member Member
Joined: 2 years ago
Posts: 290
Topic starter  

But why did pressure plummet?

on Monday gauge didn't read 0. But flow setter did.

so much for the hydraulic separation of the LLH…



   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3383
 

Pressure will be same either side of llh.  Llh gives some separation of flows but it's the same body of water at same pressure.  

Assuming you mean static pressure, ie measured when water pumps are off, it could plummet because of

  • Dissolved air coming out of solution (air is more compressible than water)
  • Dissolved air coming out of solution and then being vented through the auto bleed.
  • A leak
  • A faulty expansion vessel

The last is the least likely, but not impossible.   There may be other reasons but these are the ones that come to mind.

The first recourse sofaik is simply to top it up via the filling loop and manually bleed any points where air is obviously collecting. That's certainly what I have been doing with my central heating for the past 30 years!

Flow setter could possibly read zero without pressure being zero if the air in the llh goes below the port which feeds the flow setter.  Again there may be other reasons eg pump has run dry because of air in system or airlock.  

 


This post was modified 44 minutes ago by JamesPa
This post was modified 43 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote