Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @jaketPosted by: @sunandairA loss
Posted by: @jaketHow do I check the emitter value & that the flushing value is fully closed (what does this look like / where is it positioned?)
I had wondered if you have a list of your radiator sizes and how large your underfloor heating area is since a small emitter capacity can cause cycling. The flushing valve refers to your schematic diagram.... I noticed on the drawing there was a flushing bypass valve which isn’t always fitted. And mentioned it as an aside issue. Just to check that the valve is fully closed since this could cause hot water to bypass the heating system.
Having said all that, your latest hourly graph looks better for all the changes you have made so things appear to have improved.
-- Attachment is not available --
Unfortunately I think the issue has not been resolved. See below hourly temps from 13h00.
I’m going to run it for a few days in the current setting to see what the overall consumption / COP figures are like - if these are still terrible I may try out auto adaptive.
-- Attachment is not available --
Hi @jake. I’ve started getting a bit of cycling since we have had 12c OAT. we get about 2 or 3 cycles an hour. Auto adapt does help a little by reducing the cycle size but usually adds a few degrees to the flow temp to reduce the cycling but then stops and pauses to reduce the output.
Regarding your charts... I find it easier to read the charts when I screenshot my phone to landscape. It produces a longer time line for the hourly graph. Also by adding the tank set temperature line and one of the 25c lines I get a Better proportioned graph with 5c horizontal lines. I think this helps in reading the deltaT of the Flow and Return. Here are 2 screen shots of the same chart. Does the different setup help to see the performance of the output when it’s viewed in landscape? I hope you can see how the top and bottom lines help to change the proportions of the vertical temperature scale.
Here is your chart from yesterday
This second one below, I’ve tried to copy your scale and orientation- but it’s the same chart as mine above in landscape format.
I think the flat bottom to the return temp shows how the slab temperature is preventing anymore heat being dropped from the circulation in to the UFH - so without being able to deliver heat at the rate it is being generated the flow temp rises until it reaches the set point, hence cycles. So I would read from this that the radiator circuit was not active, as otherwise the return temp would vary more.
In an ideal system the compensation curve would match the heat loss of the house at the different OATs – but if zoning is removing chunks of the house-side heat load then that equation becomes unbalanced. If you have two stats high so they are always calling, then the call from the third stat would effectively switch the entire house demand on and off. This should give you more balance, which should be more efficient.
Having UFH and radiators makes it tricky as the speed of heat transfer into the house is different, auto adapt can be too eager to put more heat in if it doesn’t register a change of temperature within a certain time, which is more likely when the heat transfer to the room is moderated and extended by the slab. But if you try auto adapt then it will refer to the temperature of the room the FTC controller is in – which looks like the second floor from the pic (I presuming you don’t have a Mitsubushi remote stat to set as the target location). When the system has the knowledge of current and desired temps it can use those to create longer runs with appropriate pauses to control the total heat delivery.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Ah okay so you also get some cycling when the OAT low double digits. What is your COP?
Interestingly I spoke to the installer briefly today, who said it is normal for the unit to cycle about three times an hour. We didn't have the chance to fully discuss my concerns (he was on site looking at another property) but I will try get him out to take a full look at my set up & stats.
@jaket we have decided a bit of cycling (but not too much) when it’s 10 or 12c is better at achieving a high CoP and minimise KWh consumption.
The question we faced is - what is acceptable cycling? We have decided 2 cycles per hour is stable enough and at 10 or 12c that gives us a CoP of about 4.0 sometimes 3.8. At that kind of cycling we are able to run the system at about 32c with 2 cycles per hour and 37c flow temperature without cycling. However we have about 21kw output capacity from our radiators and its a 8.5 Ecodan.
@sunandair your logic makes sense.
My concern is that my COP is 2.5 at best. So I’m trying to find the best set up to maximise the COP, and then understand how to minimise the kWh demand (while being at a comfortable temp inside).
Hi @jaket
we have similar systems
100% eclectic house, Ecodan 8.5kW - PUZ-WM85VAA, 210l pre plumbed cylinder, full house UFH total floor about 120spm, part is 1920s solid wall however its been fully internally insulated, part is 1950s foam cavity insulated and part is newbuild, with new double and triple glazing and MVHR.
I have recently modified to removing zoning and unnecessary complexity in my system and like you are now looking more at optimising running conditions.
do you have a heat and electric meter or are you taking reading to calculate COP from the unit / app ? this is the way I have to and find the data as only a guide
this is the cycling I am getting today at 11-12 with OAT of 6c as you can see pretty bad but my floors just cant give up the heat pumps minimum output to my understanding
my next steps are to possibly try auto adaption or schedule in shutdowns 3h on 1h off
how are you getting on it seems you are in a similar position?
My settings are 37c @ -5c to 26 @ 15c I would like this lower as the house is 21c feeling a bit to warm sometimes
however I am already getting a lot of cycling.
Posted by: @richMy settings are 37c @ -5c to 26 @ 15c I would like this lower as the house is 21c feeling a bit to warm sometimes
however I am already getting a lot of cycling.
Cycling isn't necessarily a bad thing, since it may mean that you are using less electrical energy to keep your home warm.
What is the heat loss calculation for your home?
@rich I have an 8.5kw ecodan to keep cycling to 1 per hour at any temp below 10C I need to run at 32C, anything less leads to a lot of cycling.
That is with upstairs rads on and UFH downstairs all open, even then the house will heat up and thermostats will cut off the heat pump after a few hours.
You will have to run it more on and off at a higher flow temp if you want to reduce/eliminate the cycling.
Posted by: @gary@rich I have an 8.5kw ecodan to keep cycling to 1 per hour at any temp below 10C I need to run at 32C, anything less leads to a lot of cycling.
That is with upstairs rads on and UFH downstairs all open, even then the house will heat up and thermostats will cut off the heat pump after a few hours.
You will have to run it more on and off at a higher flow temp if you want to reduce/eliminate the cycling.
What range of indoor temperatures do you get when operating your system in that manner?
-
Mitsubishi Ecodan not good enough ?
2 weeks ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
4 weeks ago
-
Mitsubishi Ecodan circulation pump running.
1 month ago
-
Ecodan Auto Adapt Options
1 month ago
-
Ecodan heat pump leak
1 month ago
Currently viewing this topic 2 guests.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 932 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 19 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 19 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago