Good morning all,
After months of problems and complaints, I finally have a formal report from LG categorically stating that our 9kw heat pump is undersized for our 2700 sqft home - which is why we cannot heat the rooms in weather with temperatures below 4° and why the pump is so horribly noisy in those conditions as it is under significant strain and working at full capacity 24/7 to try to do so.
This is fantastic progress, but what now? I'm about to approach the developer who built my new build property, but does anyone have any advice or knowledge of laws concerning sufficient heating systems? I need to make sure the builder and Omnie, who designed the underpowered system and have always maintained there's nothing wrong with it (although could never explain why my home wouldn't heat above 16.5° all winter) have no wriggle room and recognise their legal obligations.
Do I need to engage a solicitor? What should I do in the first instance?
Help!
Sam.
Sam,
do you know if RHI is being claimed by the developer (I assume it isn't by you)? If so they would have to have filled in an MCI calculation and submitted it to OFGEM. That should ensure the sizing is correct. It'd be worth asking them for this or anything else they used to size the system.
Kev
Have LG confirmed what size ASHP is suitable?
Do you have access to the system data showing flow rates/temps etc? It would be interesting to see the flow temp when the ambient temp is sub 4 degrees to see when every zone is calling for heat what it is actually flowing at.
If I switch on every single zone/radiator on our system it will only flow at 37-40 max. Is your property all radiators or a mix of UFH and radiators?
Mitsubishi Ecodan 14kw ASHP + 500l Cylinder
@kev-m, do you know if there's a way of searching the MCS database?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Sam,
As suggested previously, have you been in touch with trading standards or consumer protection? They would probably be able to point you in the correct direction.
You should also get in touch with MCS, their helpline number is 0333 103 8130.
Personally I would not go down the route of getting a solicitor just yet, keep that as a last resort.
Your local MP may also be of assistance, since the government want us all go 'green'.
Hope this helps.
Regards,
Derek.
@derek-m, I completely agree with you. The first point of attack would be MCS, but the only thing I'm unsure of (which I think Sam informed me of) is that the installers weren't MCS accredited. If they're not, there's not much recourse there. Sam can correct me if I've remembered this incorrectly. A phone call should clarify this. Also, if they were MCS accredited, there'll be insurance in play which Sam can use to get the matter resolved. Our MCS certificate states that we're insured by HEIS, and they'll put right any problems.
Trading standards and consumer protection is also a good course of action to pursue as a next step.
The solicitors play is a last resort in most cases, because of the money involved, but negligence and incompetence shouldn't be that difficult to prove, given that LG have now issued a formal report stating the incorrect size heat pump was installed.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
A quick looks suggests the MCS data is available but you need to ask for a login
Hi,
Mars, unfortunately you are correct. We do not have an MCS certificate. I've been advised to contact the builder with the report quoting the 2015 consumer rights act.
I suppose my main concern is that Omnie will simply write a report stating it is big enough.
Sam
I don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
@sam, I would demand the heat loss and emitter calculation from Omnie. If they say that the heat pump is the correct size, they must provide the evidence to back that up, and the only way to do that is to share the aforementioned calculations.
I can't remember if you told me this, but have you called MCS and verified from them that there isn't a MCS certificate for your property?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @samI don't know about the flow data, although the technician has attached a data report that will hopefully mean something to the right people.
It's all underfloor heating and he's recommended a UN3 CHASSIS 12-16KW 1Ph.
He has calculated a heat loss of 8.61kw based on 0.035kw/m2 , leaving only a heating capacity of .39kw
I missed this earlier comment. Is the calculation from the LG technician, not Omnie?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Installing your own ASHP - DIY
3 weeks ago
-
ASHP install contract and BUS grant money
2 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
3 months ago
-
Heat Pump starting current
3 months ago
- 22 Forums
- 2,058 Topics
- 45 K Posts
- 59 Online
- 3,315 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Grant Aerona3 - Home Assistant control via Modbus
@majordennisbloodnok I deffo don’t disagree I would lov...
By Grantmethestrength , 59 minutes ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
That's a very perceptive point, @jeff. We're all very g...
By Majordennisbloodnok , 1 hour ago
-
RE: Renewables & Heat Pumps in the News
The update above was posted here a few days ago along w...
By Jeff , 2 hours ago
-
RE: Commencing on an ASHP Installation Process
That is really down to system volume. Plus the ability ...
By Johnmo , 14 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Mine has been doing a CoP of -3.18, yes negative, combi...
By Johnmo , 21 hours ago
-
RE: Battery sizing - How low can you go!
The second 6.5 kWh Growatt battery was installed today....
By ChandyKris , 23 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
Thanks for that thoughtful reply. Unfortunately we g...
By JamesPa , 24 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
So… I called them this morning and I’m up and running o...
By Westkent , 24 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Your system seems to be more modern than mine, mine was...
By abbote , 1 day ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 2 days ago
-
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 2 days ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 2 days ago
-
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 4 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 5 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 5 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 6 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 6 days ago