Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

12kW Samsung gen 6 short cycling

374 Posts
17 Users
63 Reactions
104.8 K Views
Transparent
(@transparent)
Famed Member Moderator
Joined: 4 years ago
Posts: 3166
 

I think, @craig that you'd better request CES join this topic asap. There's heaps of really useful information which they can use for the advantage of existing customers.

By now they must surely be in debt to both @hughf and @derek-m for a decent bottle of something on their Christmas dinner tables 😉 

Everything I can find online about this installer suggests a reputable company who are busy recruiting to fulfill their growing order book.


Save energy... recycle electrons!


   
ReplyQuote
(@craig1980)
Estimable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

@hughf I doubt I'd manage to get the installer back, let alone get them to change anything. If they even knew how. 

So, I do have the correct pump set up then? 



   
ReplyQuote
(@craig1980)
Estimable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

@transparent I believe they are reputable but just busy fitting pumps the cheapest and fastest way possible. The fitters are on job rate so the more they can do the better they get paid so they are fitting them quickly and shooting off. I've explained that they need to do better with regards to paperwork and set up of the system or education of the end user to set up the system. It's not practical for them to hang around for a few days to let it all settle and tweak WC but if they showed the customer more info than "control it with the room stats" that would help. The system is left on default settings with no WC turned on and no legionella (I do this manually once a month rather than set it up weekly). I'm not unhappy with the system, it's just not good enough to fit it and run. Most customers won't go to the lengths I have and will just run it on room stats then complain it's too expensive. 

COP of 4.14 today but the house is sitting a bit cooler at 17.5. No solar gain whatsoever today though, wet and windy all day. 



   
ReplyQuote



(@hughf)
Honorable Member Member
Joined: 4 years ago
Posts: 489
 

Posted by: @craig1980

@hughf I doubt I'd manage to get the installer back, let alone get them to change anything. If they even knew how. 

So, I do have the correct pump set up then? 

Your system works, I’d leave it at that as it is still under warranty. All anyone needs to do is buy a PWM pump and follow the instructions in the Midsummer Wholesale Samsung installation guide….

 


Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.

My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.


   
ReplyQuote
(@craig1980)
Estimable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

Thanks 👍


 



   
ReplyQuote
(@craig1980)
Estimable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

@derek-m when I got in last night I turned them both up to 25. It was cycling on for 10 mins, off for 7 mins. 

Today it is back to 8 mins on 20 secs off. No changes. 



   
ReplyQuote



(@kev-m)
Noble Member Member
Joined: 5 years ago
Posts: 1276
 

Posted by: @craig1980

@derek-m when I got in last night I turned them both up to 25. It was cycling on for 10 mins, off for 7 mins. 

Today it is back to 8 mins on 20 secs off. No changes. 

I'm watching this from a distance as I can't really contribute.  What puzzles me is what is making it switch on after only 20 seconds off? The 8 minutes on I can understand if the flow is being heated and it reaches its target then switches off. But after 20 seconds off the flow isn't going to have time to cool down let alone the ASHP react via the flow sensors. 

 



   
ReplyQuote
(@craig1980)
Estimable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

My thoughts are that I'm running it too low as I don't want much heat out of it. When it's mild like it is it's stalling. Maybe. I don't really understand how they work. 🙈



   
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

Posted by: @craig1980

@derek-m when I got in last night I turned them both up to 25. It was cycling on for 10 mins, off for 7 mins. 

Today it is back to 8 mins on 20 secs off. No changes. 

Has the indoor air temperature changed, and are both water pumps running continuously?

 



   
ReplyQuote



(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4425
 

Posted by: @kev-m

Posted by: @craig1980

@derek-m when I got in last night I turned them both up to 25. It was cycling on for 10 mins, off for 7 mins. 

Today it is back to 8 mins on 20 secs off. No changes. 

I'm watching this from a distance as I can't really contribute.  What puzzles me is what is making it switch on after only 20 seconds off? The 8 minutes on I can understand if the flow is being heated and it reaches its target then switches off. But after 20 seconds off the flow isn't going to have time to cool down let alone the ASHP react via the flow sensors. 

 

Hi Kev,

The only real way to possibly discover what is causing the problem is to check how each item of equipment is functioning, disregard the ones that are working correctly, until you discover the one that is not working correctly.

Correct me if I am wrong, but does the Ecodan have a setting that specifies how long the compressor has to remain off before it can be restarted?

 



   
ReplyQuote
(@kev-m)
Noble Member Member
Joined: 5 years ago
Posts: 1276
 

Posted by: @derek-m

Posted by: @kev-m

Posted by: @craig1980

@derek-m when I got in last night I turned them both up to 25. It was cycling on for 10 mins, off for 7 mins. 

Today it is back to 8 mins on 20 secs off. No changes. 

I'm watching this from a distance as I can't really contribute.  What puzzles me is what is making it switch on after only 20 seconds off? The 8 minutes on I can understand if the flow is being heated and it reaches its target then switches off. But after 20 seconds off the flow isn't going to have time to cool down let alone the ASHP react via the flow sensors. 

 

Hi Kev,

The only real way to possibly discover what is causing the problem is to check how each item of equipment is functioning, disregard the ones that are working correctly, until you discover the one that is not working correctly.

Correct me if I am wrong, but does the Ecodan have a setting that specifies how long the compressor has to remain off before it can be restarted?

 

Hi Derek,

 

I don't think it does; I think it does a similar thing by looking at flow temp rather than time.  I say 'think' because that table's title suggests it applies to room temp mode? I don't think that's right though.

Screenshot 2022 11 23 17.22.57

 

 There is mention of pump cycles/interval in the smart grid ready section but I'm not sure if that can be set without having smart grid functionality actually running properly. (page 42 in my FTC6 manual) 

 

 



   
ReplyQuote
(@craig1980)
Estimable Member Member
Joined: 3 years ago
Posts: 146
Topic starter  

 

20221127 151813

@derek-m I don't have an Ecodan but you may be talking about something else. 

When you say "indoor temperature" do you mean the measurement on the wired remote on the tank or the one on the room stats? 

Room stats are still the same at around 18 and indoor temp on "heat" screen on wired remote is still the same at around 21-22. 

Both pumps are vibrating so assume they are running. 

20221127 151808

20221127 152032


   
ReplyQuote