Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
12kW Samsung gen 6 short cycling
Posted by: @craig1980A quick update on my system.Â
I'm running at a COP of around 3.3-3.4 at around 3 degrees outside temp including water heating for an hour at midnight. I'm still messing with settings so hopefully this will increase. Once the cold weather arrives the COP definitely drops.Â
LWT at around 28-29 degrees and WC is on.Â
Derek got to the bottom of the issue. I was running the WC settings incorrectly. There are 3 options which run the pump in different ways whilst WC is on and one of those tells the pumps to turn off after 7 mins then back on. That's why it was short cycling.Â
I still need to contact Samsung and I'll let them know about this thread. My Teva out sensor is showing -50 so I may need a new sensor there. I've checked the outside heat pump and it is all plugged in properly. I'll reply on here with any updates.Â
Craig (@craig1980) would you be kind enough to provide @iantelescope with details of the changes that you made to the controller settings to stop the short cycling.Â
Â
Hi Derek,
Many thanks for the data.
I have tried the Samsung Field bits 2091 Options 1 to 4Â on several occasions.
I too found the field bit 2091 option 4 was suspiciously near to my original 8 minute Cycle time.
Samsung field bit 2091, Water Pump 3 subroutine :
1) Delay for 3 minutes
2) OFF for 7 minutes .
3) ON for 3 minutes.
4) OFF for 7 minutes.
However, I, and the French Samsung Engineer tried all of these settings , multiple times, without any great effect.
The pulsing briefly increases the water temperature, and cycle time during the water cycle .
I Do currently use Water Pump 3 given the 2 C thermostat Hysteresis and the slight resultingincrease in cycle time caused by the extra, mid cycle, Motor pulse.
I have , however tried setting Field bit 2091 , Water Pump 2 subroutine again. given that many other parameters, and settings have changed in the interim.
Samsung field bit 2091, Water Pump 2 subroutine has however a 1 C Hysteresis.
Many thanks to you and Craig.
- 26 Forums
- 2,700 Topics
- 63.3 K Posts
- 993 Online
- 7,107 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Can DNO change a G99 export allowance once approved?
I have a Solar/battery system with an approved G99 expo...
By AndrewJ , 18 minutes ago
-
RE: Electricity price predictions
Chinese manufacturing has the ability to be very good q...
By Majordennisbloodnok , 4 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: GotGordon Manufacturer: Samsun...
By Gotgordon , 15 hours ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
@ian33a I am not easy with sleep either unfortunately…....
By MK4 , 17 hours ago
-
RE: Renewables uptake near you
In a village of under 40 houses...Conservation Area. I'...
By Tim441 , 1 day ago
-
RE: Home Alone with Home Assistant (previously A Beginner's Guide to ASHP Monitoring)
Great news, @bontwoody.
By Majordennisbloodnok , 1 day ago
-
Haier R290 Super Aqua Monobloc. Output capacity tables.
As I mentioned in my introduction post, I've been consi...
By Singlespeed , 1 day ago
-
RE: Air to air bus grant installer anywhere
I am consistently told by aircon folks (ie air/air) tha...
By EtchedPixels , 2 days ago
-
RE: What is possible with FIT, SEG, Hate Pumps and Batteries?
Thank you, everyone, for your replies. Our FIT provid...
By ian33a , 2 days ago
-
@mk4 And of course, the panels are less productive due ...
By Toodles , 2 days ago
-
RE: GivEnergy inverter tripping due to over-voltage?
I'm trying to get clarity on exactly when the inverter ...
By Tim441 , 2 days ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
Autocorrupt seems to be working overtime.
By Majordennisbloodnok , 2 days ago
-
RE: Vehicle-to-Home with a Heat Pump: Is the Technology Ready and Which EV Should I Buy?
I looked into that wallbox a bit more off the back of t...
By Majordennisbloodnok , 3 days ago
-
RE: Say hello and introduce yourself
@jandp awesome system I hope it works out well.
By Judith , 3 days ago