Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
12kW Samsung gen 6 short cycling
Posted by: @craig1980A quick update on my system.Â
I'm running at a COP of around 3.3-3.4 at around 3 degrees outside temp including water heating for an hour at midnight. I'm still messing with settings so hopefully this will increase. Once the cold weather arrives the COP definitely drops.Â
LWT at around 28-29 degrees and WC is on.Â
Derek got to the bottom of the issue. I was running the WC settings incorrectly. There are 3 options which run the pump in different ways whilst WC is on and one of those tells the pumps to turn off after 7 mins then back on. That's why it was short cycling.Â
I still need to contact Samsung and I'll let them know about this thread. My Teva out sensor is showing -50 so I may need a new sensor there. I've checked the outside heat pump and it is all plugged in properly. I'll reply on here with any updates.Â
Craig (@craig1980) would you be kind enough to provide @iantelescope with details of the changes that you made to the controller settings to stop the short cycling.Â
Â
Hi Derek,
Many thanks for the data.
I have tried the Samsung Field bits 2091 Options 1 to 4Â on several occasions.
I too found the field bit 2091 option 4 was suspiciously near to my original 8 minute Cycle time.
Samsung field bit 2091, Water Pump 3 subroutine :
1) Delay for 3 minutes
2) OFF for 7 minutes .
3) ON for 3 minutes.
4) OFF for 7 minutes.
However, I, and the French Samsung Engineer tried all of these settings , multiple times, without any great effect.
The pulsing briefly increases the water temperature, and cycle time during the water cycle .
I Do currently use Water Pump 3 given the 2 C thermostat Hysteresis and the slight resultingincrease in cycle time caused by the extra, mid cycle, Motor pulse.
I have , however tried setting Field bit 2091 , Water Pump 2 subroutine again. given that many other parameters, and settings have changed in the interim.
Samsung field bit 2091, Water Pump 2 subroutine has however a 1 C Hysteresis.
Many thanks to you and Craig.
- 27 Forums
- 2,775 Topics
- 65.4 K Posts
- 2,674 Online
- 7,180 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 6 hours ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 6 hours ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 6 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Hi all, I'm new to this game having spent the last 25...
By gz00 , 8 hours ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 12 hours ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 17 hours ago
-
@mrkfm, I'd also suggest that whenever you're ready, st...
By Mars , 1 day ago
-
RE: Are you planning to use a wood burner to supplement your central heating this winter?
I use my stove daily for backup and comfort. Definitely...
By Margarethomas , 1 day ago
-
@rob-of-york Thanks. I wish I'd started on this site as...
By mrkfm , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@downfield I just checked this morning and OE just r...
By Papahuhu , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Thanks Will. I'll probably be a week or so before get...
By Singlespeed , 2 days ago
-
RE: Cooling using an air to water heat pump
From experience this summer, a single-split A2A unit on...
By Rob of York , 2 days ago
-
Analysis of the economics of switching to an A2W ASHP compared to other heat sources
This post aims to analyse the economics of installing, ...
By Rob of York , 4 days ago
-
RE: Cooling with air to water heat pumps
@editor does that mean you have to have two separate ex...
By mrkfm , 4 days ago
Members Online
No online members at the moment