Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My "installation" was fitted with a 50 l Volumising tank some six months after it was "installed".
I was given at least four opinions from Five different "experts" as to Why I needed a Volumising tank......
Why I need a volumising tank................
1 To protect the HEAT PUMP.
A Volumising tank would provide "Hydraulic Isolation" between the Radiators and the Heat Pump .
Any changes in water pressure or Flow rate on the radiators would be isolated from the HEAT PUMP. ( from SAMSUNG Service)
Â
2 . To protect the Heat PUMP during de-Icing.
During sharp frosts the Heat Pump should be protected from the ICE accumulation.
A Volumising tank should store enough Energy to "allow the De-ICing to Complete during severe frosts." ( from SAMSUNG DALLIUM , )
Â
3. To prevent Rapid Cycling , or Hyper Cycling.
A increased volume of water in a volumising tank will reduce rate of temperature fall ...................... and increase the Cycle time.
 See Buffer Sizing .....from MCS
After a dispute between my "installer" and SAMSUNG, my "installer" was fired , and a 50 L Volumising tank was ordered..
Two engineers appeared to install the Volumising tank but explained "that they did not know why I needed a tank nor where to fit it!.
Â
Â
ian
Â
Â
Posted by: @cathoderayThis is important information! Context means a lot when interpreting COPs.
I thought I did put enough context in place with my chart - re posted below. I was showing clearly the COP as labelled for short periods of time. I think with an average of 5.3 over a longer period of time (7 hours) the very high efficiency periods are not far from reality.Â
Based on observations by others regarding Samsung Gen6 [specifically the poor insulation on the temperature probes], I may actually have an even higher COP than I do.
In short, I think that there are times in the year, when a well designed system coupled with good emitter characteristics (mine has some way to go on both) you can get and should be getting a high COP.
Hi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
@iantelescope what you've described is what is usually referred to as a buffer tank , due to the fact that its providing hydraulic isolation. A cylinder (which may well be exactly the same part) when installed as in the way that is commonly described as a "volumiser", doesn't provide hydraulic isolation, but does provide the other points you mentioned.
see diagrams on pages 1 and 2 in here(yep, midsummer wholesale again)
Are you able to draw up a detailed system schematic so we can understand your system better with the goal of improving it?
if they didn't know where to fit it, there's at least a possibility that its not doing the right thing.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066Â Â
I tried to find Samsung's equivalent to Midea's Engineering data book which has detained outputs (and COPs) at different ambients and LWTs but didn't have any luck - maybe you have the data? It would provide another benchmark to compare your figures to.
Â
Â
first result, page 29 of the pdf
Â
Â
@transparent on the "what sort of meter to use" point:Â there's no reason for me to need larger screen of the 220, as I'll be reading it purely over modbus.Â
I currently have this:
and intend to modify it to thisÂ
does that make sense?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iantelescopeHi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
Are you using Weather Compensation (WC) mode?
What is the present Leaving Water Temperature (LWT) on your system?
Â
Posted by: @iantelescopeHi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
This link was posted on the forum yesterday which you may find of use.
https://www.theheatinghub.co.uk/articles/raise-complaint-about-heat-pump-installation
Â
Posted by: @iantelescopeTwo engineers appeared to install the Volumising tank but explained "that they did not know why I needed a tank nor where to fit it!.
Pretty much par for the course, though my installer was better, he not only suggested the volumiser in the first place when I mentioned the short cycling and showed him the charts with the short cycling clearly visible, he also knew what it did and where it could be fitted (in practice, wherever there is space in the heated areas in the house so its losses contribute to space heating).
Posted by: @william1066In short, I think that there are times in the year, when a well designed system coupled with good emitter characteristics (mine has some way to go on both) you can get and should be getting a high COP.
I am sure that's right, but for my part, I like to reassure myself I am not getting Maoist tractor production is up figures. Thanks to @dandee, I managed to have a look at the Samsung performance data, and it looks as though in favourable conditions COPs in the region of 6 are indeed possible with your unit. I think that means you can have more confidence in your results, but again, if it was me, I would be wary of being too pleased with myself. COPs of around 6 are extremely good, and most heat pumps won't get there most of the time. It will be interesting to hear what your SCOP is once the heating season is over, if you plan to calculate it. I think mine will be between 3.0 and 3.5, and although I now trust the energy in figure a bit more, I am still wary of the energy out. Now that I have found out that I do have an inline flow meter, I do have the option of verifying the modbus flow rates, which as previously noted tend to remain in a small range, meaning the only extra data I need to collect independently is the LWT and RWT. But that is probably something that will have to wait until the start of the next heating season, though I can set up the hardware over the summer.
Â
Midea 14kW (for now...) ASHP heating both building and DHW
I now control of my Primary Water loop as a function of the room Temperature. Yet another Arduino, A new function "yetaarduino".
The Control measures the room temperature and sets the PWM Signal to the primary water loop circuit.
The Multiplying factor setting the change in Flow rate against the Temperature change will have to be found by experiment. with an initial setting of 1 lpm per degree C.
The Secondary water loop , on the other side of the Heat Exchanger remains , for the present under control of an oscillator.
ian
Â
Â
Posted by: @iantelescopeI now control of my Primary Water loop as a function of the room Temperature. Yet another Arduino, A new function "yetaarduino".
The Control measures the room temperature and sets the PWM Signal to the primary water loop circuit.
The Multiplying factor setting the change in Flow rate against the Temperature change will have to be found by experiment. with an initial setting of 1 lpm per degree C.
The Secondary water loop , on the other side of the Heat Exchanger remains , for the present under control of an oscillator.
ian
Â
Â
The normal method of controlling the indoor temperature would be by varying the LWT, in conjunction with changes made by WC. I suppose varying the flow rate may also work.
I seem to remember someone asking whether your heat exchanger is actually a buffer tank. Could you provide a photo?
Did you resolve the cycling issue?
Â
My Volumising tank was originally designed and selected by Samsung Dallium , Samsung's own service depot at Wigan .
My "installer's technical designer " then described the Samsung proposal to install the volumising tank as "ludicrous" and that "their own engineers would complete the job".
My "installer's technical designer "was then fired "for Technical incompetence!".
The Volumising tank was then "discovered under the former Technical designer's desk .....some two months later!
Two "Engineer's" then appeared to install the "Volumising tank " but "did not know where the tank was to be installed within the pipework.
The "Volumising tank " was designed by Samsung-Dallium to "allow the Heat pump to complete DE-icing on Cold Scottish nights".
The MCS also provided information about controlling short Cycling.........with a different size of volumising tank in a different pipework location!
The "Volumising tank was fitted across the Primary ports of my Heat Exchanger .......total confusion!
The DE-icing works very well during winter.
The Short-Cycling on the primary water loop has also stopped.
However, the Secondary water loop, the radiator loop , is now hyper-cycling ..........
Presumably another volumising tank should be fitted to my secondary , radiator water loop?
ian
Â
Â
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 527 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
I put some washing up liquid in when I clean mine, then...
By JamesPa , 7 minutes ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
@seoras OK Im not sure if this relates to your commen...
By JamesPa , 8 minutes ago
-
RE: Our 10 year old Grant heat pump failed
Since my last post on this topic we've reached a conclu...
By Mike Patrick , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 12 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 13 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 16 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 17 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 18 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 19 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 21 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 21 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago