Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My "installation" was fitted with a 50 l Volumising tank some six months after it was "installed".
I was given at least four opinions from Five different "experts" as to Why I needed a Volumising tank......
Why I need a volumising tank................
1 To protect the HEAT PUMP.
A Volumising tank would provide "Hydraulic Isolation" between the Radiators and the Heat Pump .
Any changes in water pressure or Flow rate on the radiators would be isolated from the HEAT PUMP. ( from SAMSUNG Service)
Â
2 . To protect the Heat PUMP during de-Icing.
During sharp frosts the Heat Pump should be protected from the ICE accumulation.
A Volumising tank should store enough Energy to "allow the De-ICing to Complete during severe frosts." ( from SAMSUNG DALLIUM , )
Â
3. To prevent Rapid Cycling , or Hyper Cycling.
A increased volume of water in a volumising tank will reduce rate of temperature fall ...................... and increase the Cycle time.
 See Buffer Sizing .....from MCS
After a dispute between my "installer" and SAMSUNG, my "installer" was fired , and a 50 L Volumising tank was ordered..
Two engineers appeared to install the Volumising tank but explained "that they did not know why I needed a tank nor where to fit it!.
Â
Â
ian
Â
Â
Posted by: @cathoderayThis is important information! Context means a lot when interpreting COPs.
I thought I did put enough context in place with my chart - re posted below. I was showing clearly the COP as labelled for short periods of time. I think with an average of 5.3 over a longer period of time (7 hours) the very high efficiency periods are not far from reality.Â
Based on observations by others regarding Samsung Gen6 [specifically the poor insulation on the temperature probes], I may actually have an even higher COP than I do.
In short, I think that there are times in the year, when a well designed system coupled with good emitter characteristics (mine has some way to go on both) you can get and should be getting a high COP.
Hi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
@iantelescope what you've described is what is usually referred to as a buffer tank , due to the fact that its providing hydraulic isolation. A cylinder (which may well be exactly the same part) when installed as in the way that is commonly described as a "volumiser", doesn't provide hydraulic isolation, but does provide the other points you mentioned.
see diagrams on pages 1 and 2 in here(yep, midsummer wholesale again)
Are you able to draw up a detailed system schematic so we can understand your system better with the goal of improving it?
if they didn't know where to fit it, there's at least a possibility that its not doing the right thing.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066Â Â
I tried to find Samsung's equivalent to Midea's Engineering data book which has detained outputs (and COPs) at different ambients and LWTs but didn't have any luck - maybe you have the data? It would provide another benchmark to compare your figures to.
Â
Â
first result, page 29 of the pdf
Â
Â
@transparent on the "what sort of meter to use" point:Â there's no reason for me to need larger screen of the 220, as I'll be reading it purely over modbus.Â
I currently have this:
and intend to modify it to thisÂ
does that make sense?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iantelescopeHi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
Are you using Weather Compensation (WC) mode?
What is the present Leaving Water Temperature (LWT) on your system?
Â
Posted by: @iantelescopeHi Derek,
No , I am still hyper-Cycling!
YES, I am still loosing lots of energy across the Heat Exchanger , pipes et al.!
After nearly of year of problems caused by my "installers" incompetence followed by the endless denials of responsibility from the NIC,MCS and the RECC ..........
I have been advised by the "charitable " MCS and NIC to get a lawyer...............impossible for a 75 year old OAP.
Which is worse ....my "installer" or the Toothless Tigers of the "Charities" supposedly operating as regulators?
I should have installed this myself!
ian
Â
Â
Â
Â
This link was posted on the forum yesterday which you may find of use.
https://www.theheatinghub.co.uk/articles/raise-complaint-about-heat-pump-installation
Â
Posted by: @iantelescopeTwo engineers appeared to install the Volumising tank but explained "that they did not know why I needed a tank nor where to fit it!.
Pretty much par for the course, though my installer was better, he not only suggested the volumiser in the first place when I mentioned the short cycling and showed him the charts with the short cycling clearly visible, he also knew what it did and where it could be fitted (in practice, wherever there is space in the heated areas in the house so its losses contribute to space heating).
Posted by: @william1066In short, I think that there are times in the year, when a well designed system coupled with good emitter characteristics (mine has some way to go on both) you can get and should be getting a high COP.
I am sure that's right, but for my part, I like to reassure myself I am not getting Maoist tractor production is up figures. Thanks to @dandee, I managed to have a look at the Samsung performance data, and it looks as though in favourable conditions COPs in the region of 6 are indeed possible with your unit. I think that means you can have more confidence in your results, but again, if it was me, I would be wary of being too pleased with myself. COPs of around 6 are extremely good, and most heat pumps won't get there most of the time. It will be interesting to hear what your SCOP is once the heating season is over, if you plan to calculate it. I think mine will be between 3.0 and 3.5, and although I now trust the energy in figure a bit more, I am still wary of the energy out. Now that I have found out that I do have an inline flow meter, I do have the option of verifying the modbus flow rates, which as previously noted tend to remain in a small range, meaning the only extra data I need to collect independently is the LWT and RWT. But that is probably something that will have to wait until the start of the next heating season, though I can set up the hardware over the summer.
Â
Midea 14kW (for now...) ASHP heating both building and DHW
I now control of my Primary Water loop as a function of the room Temperature. Yet another Arduino, A new function "yetaarduino".
The Control measures the room temperature and sets the PWM Signal to the primary water loop circuit.
The Multiplying factor setting the change in Flow rate against the Temperature change will have to be found by experiment. with an initial setting of 1 lpm per degree C.
The Secondary water loop , on the other side of the Heat Exchanger remains , for the present under control of an oscillator.
ian
Â
Â
Posted by: @iantelescopeI now control of my Primary Water loop as a function of the room Temperature. Yet another Arduino, A new function "yetaarduino".
The Control measures the room temperature and sets the PWM Signal to the primary water loop circuit.
The Multiplying factor setting the change in Flow rate against the Temperature change will have to be found by experiment. with an initial setting of 1 lpm per degree C.
The Secondary water loop , on the other side of the Heat Exchanger remains , for the present under control of an oscillator.
ian
Â
Â
The normal method of controlling the indoor temperature would be by varying the LWT, in conjunction with changes made by WC. I suppose varying the flow rate may also work.
I seem to remember someone asking whether your heat exchanger is actually a buffer tank. Could you provide a photo?
Did you resolve the cycling issue?
Â
My Volumising tank was originally designed and selected by Samsung Dallium , Samsung's own service depot at Wigan .
My "installer's technical designer " then described the Samsung proposal to install the volumising tank as "ludicrous" and that "their own engineers would complete the job".
My "installer's technical designer "was then fired "for Technical incompetence!".
The Volumising tank was then "discovered under the former Technical designer's desk .....some two months later!
Two "Engineer's" then appeared to install the "Volumising tank " but "did not know where the tank was to be installed within the pipework.
The "Volumising tank " was designed by Samsung-Dallium to "allow the Heat pump to complete DE-icing on Cold Scottish nights".
The MCS also provided information about controlling short Cycling.........with a different size of volumising tank in a different pipework location!
The "Volumising tank was fitted across the Primary ports of my Heat Exchanger .......total confusion!
The DE-icing works very well during winter.
The Short-Cycling on the primary water loop has also stopped.
However, the Secondary water loop, the radiator loop , is now hyper-cycling ..........
Presumably another volumising tank should be fitted to my secondary , radiator water loop?
ian
Â
Â
- 26 Forums
- 2,591 Topics
- 60.3 K Posts
- 332 Online
- 6,924 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge no idea if they’ve made changes, but I got...
By AndrewJ , 7 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
@wesleyp1874 if you are on Facebook there is a Grant un...
By Grantmethestrength , 8 hours ago
-
RE: Rate the quality of your heat pump design and installation
@josej, this is exactly where the industry keeps trippi...
By Mars , 8 hours ago
-
RE: Say hello and introduce yourself
@alva welcome to the forums and feel free to start a ne...
By Mars , 8 hours ago
-
Ordering up the materials to install another 5 panels o...
By David999 , 8 hours ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
So under part G or the G3 rules you have a responsibili...
By ASHP-BOBBA , 10 hours ago
-
I intend to replace the Plex pipework in the area of my...
By DavidAlgarve , 12 hours ago
-
RE: Electricity price predictions
Mention on the news about Octopus and one or two other ...
By Toodles , 14 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 23 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 1 day ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 2 days ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 2 days ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 2 days ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 2 days ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 3 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 3 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 3 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 4 days ago