Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Thanks Craig, now lower the LWT setting to 30C and see what happens to how the system operates.
Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Posted by: @craig1980Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Hi Craig,
I'm afraid that I have run out of suggestions.
There appears to be something fundamentally wrong with your heat pump, and/or how the system has been installed. The only thing that I can see that appears to be incorrect is the Teva_out temperature reading of -50C, which could possibly be due to a faulty or disconnected temperature sensor.
I would suggest that you e-mail Samsung Technical Help and ask them why your system may be operating as it is doing.
In the meantime set your system back onto WC mode and adjust for the required indoor temperature.
Â
Okay, many thanks for all of your help. I'll update if I find anything from Samsung. Thanks again. Much appreciated.Â
Interestingly, when I put the settings back to WC I get error E121. Upon looking this up in the manual it saysÂ
"Short-or open- circuit error of the room temperature sensor of the zone 1 indoor unit (detected only when the room thermostat is used) Error source - Hydro unit.Â
Posted by: @hughfPosted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
@hughf Please see the topic about Samsung install and buffer tank
https://renewableheatinghub.co.uk/forums/postid/11342
Freedom Heat Pumps claims a buffer tank is required to be within the Samsung warranty, even though the manual implies otherwise and Joule make a pre-plumbed cylinder without a buffer tank.
Â
@mike-h Ah yes, good old freedom. I’d trust the instructions from midsummer wholesale personally. I know that GH was always getting 911 errors (low flow) on his early installs, so they probably mandated a buffer to deal with that issue, allowing the primary pump to run at full speed to charge the buffer.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 27 Forums
- 2,775 Topics
- 65.4 K Posts
- 2,699 Online
- 7,180 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 6 hours ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 6 hours ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 6 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Hi all, I'm new to this game having spent the last 25...
By gz00 , 8 hours ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 12 hours ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 17 hours ago
-
@mrkfm, I'd also suggest that whenever you're ready, st...
By Mars , 1 day ago
-
RE: Are you planning to use a wood burner to supplement your central heating this winter?
I use my stove daily for backup and comfort. Definitely...
By Margarethomas , 1 day ago
-
@rob-of-york Thanks. I wish I'd started on this site as...
By mrkfm , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@downfield I just checked this morning and OE just r...
By Papahuhu , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Thanks Will. I'll probably be a week or so before get...
By Singlespeed , 2 days ago
-
RE: Cooling using an air to water heat pump
From experience this summer, a single-split A2A unit on...
By Rob of York , 2 days ago
-
Analysis of the economics of switching to an A2W ASHP compared to other heat sources
This post aims to analyse the economics of installing, ...
By Rob of York , 4 days ago
-
RE: Cooling with air to water heat pumps
@editor does that mean you have to have two separate ex...
By mrkfm , 4 days ago
Members Online
No online members at the moment