Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
As you say, nothing appears to be changing dramatically. Though I fail to understand how your home is maintaining an indoor temperature of 18C, with an outdoor temperature of 6C.
Now try setting your system in fixed LWT mode with a setting of 35C.
Â
@derek-m I've no idea. 🤣
I turned the system off for the Octopus saving session at 17:30 room stats showing 18. Went out and came back at 20:30. Turned back on and room stats were at 17.5. Not sure if you need that info but just in case it's relevant.Â
I'll have to work out how to set fixed lwt mode. I'll do it tomorrow. Thanks again.Â
@derek-m overnight it was 4 degrees and it has struggled to keep 18. The house is at 17.5 this morning. COP is down to 3.3 and it's using more power and running for longer. 15.6kw yesterday 13.3hours operation time (that's with turning off for 3hours)and a generation of 51.7.
@derek-m overnight it was 4 degrees and it has struggled to keep 18. The house is at 17.5 this morning. COP is down to 3.3 and it's using more power and running for longer. 15.6kw yesterday 13.3hours operation time (that's with turning off for 3hours)and a generation of 51.7.
Posted by: @craig1980Is this what you mean?
Â
Yes, that would appear to be the correct method. Try running with a LWT of 35C and see how the system responds, and if it stops the 20 second off periods.
Â
Okay, that's done. It was already on standard temperature "water outlet". Could that have been an issue?Â
How is the system operating now? Is it still running 8 mins on and 20 secs off?
What is happening with the room and radiator temps?
What are the flow and temperature readings etc?
Changing the way that the system is being operated is to try to find what is causing the 20 seconds shutdown.
So, it appears to run constantly but at quite high power usage of 1.9kw instantaneous power.Â
Rads feel warmer to the touch but room temp stays at around 18 according to room stats and thermometers that I used for radiator temps.Â
Outside temp is 6.0 according to wired remote.
Water outlet 35.4
Indoor 21.5 (remember, this is in the airing cupboard with the UVC).Â
Posted by: @craig1980So, it appears to run constantly but at quite high power usage of 1.9kw instantaneous power.Â
Rads feel warmer to the touch but room temp stays at around 18 according to room stats and thermometers that I used for radiator temps.Â
Outside temp is 6.0 according to wired remote.
Water outlet 35.4
Indoor 21.5 (remember, this is in the airing cupboard with the UVC).Â
Now measure the top and bottom temperatures on two or three relevant radiators, and the flow rate and temperature readings from the information screens.
Â
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 3,139 Online
- 7,197 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
I think Heat Geek have done an amazing job on their bra...
By Tomtheheatingengineer , 7 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
I have just had 3 heat loss surveys, one by heat geek o...
By David , 7 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
I think that's the key question. After all inverter uni...
By Prunus , 9 hours ago
-
RE: battery storage without solar
As of October 1st they need specific qualifications to ...
By EtchedPixels , 10 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
A unit which uses water to transfer the heat/chill from...
By Temperature_Gradient , 10 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 10 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 11 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 16 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 16 hours ago
-
Although regulations may well vary from country to coun...
By Majordennisbloodnok , 17 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 17 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 20 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@energystoragetech The heat capacity of some...
By JamesPa , 22 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
Sorry you are correct, I was remembering figures from t...
By JamesPa , 1 day ago