That's all good news @eliuccio
... and extra thanks for posting here the photo of the trips with blue levers on the side of the Growatt ARK Battery Control Unit.
I'm pleased to note that the Cahill engineer has taken the trouble to actually explain a number of points,
rather than just switching the battery back on. 😀
His observation that the battery system is "isolated" matches what I had expected.
The word isolated can mean two different things in this situation.
What he (and I) mean here is that the battery 52v cabling is 'floating' and not tied to earth or anything else.
That's how it should be...
... and that's why my own batteries don't have the connections covered.
I can't get an electric shock by touching them, and nor can you.
I can think of two possible reasons why the battery trips went off.
The one which is most relevant is that there might've been a lightning strike nearby (within a couple of miles).
Sometimes trips pick up the passing spike and switch off.
No harm done.
Good news with having the RCBO changed for a bi-directional one.
That provides confidence that the safety protection will actually work if it needs to!
Whatever UKPN say about the Service Fuse upgrade from 60A, please let us know.
If they insist on a move to 3-phase, please don't be daunted.
We can help to explain what's involved both during and after that upgrade.
It would mean you'd have your Smart Meter changed too.
That's fine.
I'm a Smart Meter specialist and I can answer whatever you'd like to know.
An upgrade to 3-phase under these circumstances shouldn't require you to pay anything.
You will, however, be asked to divide the household circuits across more than one phase.
We have photos of your consumer units here, and I already have an idea how to achieve what's required at minimal cost for the electrician's time.
Let's wait and see what UKPN say first.
Save energy... recycle electrons!
@transparent there is big difference in LV vs HV for DC circuits compared AC.
A 9v PP3 battery will kill you if you are daft enough to put your tongue on it.
There are cases where children have swallowed button cells and not survived, they are 3.3V
Posted by: @agentgeorge...
There are cases where children have swallowed button cells and not survived
...
The same has been claimed of my sister-in-law's cooking, although in fairness that's more a case of salt and buttery.
OK, taxi's ordered.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok Straight to the cells with you!
Toodles, heats his home with cold draughts and cooks food with magnets.
@agentgeorge if you'd like to start a new topic on the dangers of AC/DC electricity, please do so.
Tag me there and I'll contribute.
It is an important issue, and relevant for this forum.
But I don't think other readers will find it here on p.4 of a topic which is about a particular Home Battery Storage problem.
PS... and I do test PP3 batteries by touching them to my tongue! 😲
Save energy... recycle electrons!
@transparent Who needs a test meter?!😉
Toodles, heats his home with cold draughts and cooks food with magnets.
Need to put a warming on this thread incase anyone is following it… If it’s a discharged pp3 you'll get a tizzy tongue, don't try it with a fresh one.
It is all getting ticklish...
And phased with all of this. Anyone seeding for a any solar farm anywhere? 😀
@agentgeorge That’s a ittle too inscrotumable for me… Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles As we have had the topic issue resolved, we can edge off track a bit, and do a bit of testiculating; that’s wandering around a solar farm, waving ones hands in the air and talking bollox
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 483 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My DIY Heat Pump installation
@polar-bear So from your diagram I see that you are usi...
By bontwoody , 1 minute ago
-
Great idea. TOU includes Agile (mirroring wholesale)...
By Batpred , 4 minutes ago
-
RE: Electricity price predictions
So he must have a good team helping him in this.. ...
By Batpred , 1 hour ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Gone with Fernox Alphi-11, relieves the installers conc...
By Crimson , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
I can't do it for a Shelley device, but I can for Eastr...
By cathodeRay , 3 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
There is no such thing as a silly question! @toodles ...
By JamesPa , 4 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
Isn't this a great example of KISS!
By JamesPa , 5 hours ago
-
RE: Who has a V2G EV installation
Would that be a Chint RCD perhaps? Have a look at thi...
By Transparent , 5 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
11.2kW Ecodan Manufacturer: Misubishi Model: PUZ-WM...
By DRB01 , 18 hours ago
-
RE: Homely asking about Solar Panels.
@majordennisbloodnok I will report back with any develo...
By Toodles , 21 hours ago
-
RE: Mediation with RECC, what's your experience?
@editor Thank you, I really appreciate it! I've made ...
By TreeWizard , 22 hours ago
-
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Are you able to post a photo of that 180-litre cylinder...
By Transparent , 1 day ago
-
Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 1 day ago
-
RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 2 days ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 2 days ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 2 days ago