I have just received a link to this Report on Health and Safety aspects of Commercial BESS (1MW and above).
I've read only the first 10% thus far, but it contains information which would be useful for this discussion.
The report is by Frazer Nash Consultants on behalf of DESNZ, and has a direct email to one of the authors at the start.
That's a refreshing change to the usual unattributed government reports!
Note that many aspects of Health and Safety are not 'material issues' for planning purposes.
For example a threat to people and wildlife from contamination outside of a BESS site would be considered 'material' due to environmental legislation.
However, a potential risk to staff who are tasked with maintenance of BESS equipment is not a planning issue.
Yes, I know it should be... and I would still raise it in a submission opposing a planning application.
But the legal advisor to the Planning Committee would intervene to point out that it can't be a reason for which consent should be withheld.
Planning legislation for energy-based sites is not competent, and needs Parliament to seek amendments.
Save energy... recycle electrons!
Posted by: @transparentI have just received a link to this Report on Health and Safety aspects of Commercial BESS (1MW and above).
This is a pearl! The list of bibliographic references may be very useful as well.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @transparentNote that many aspects of Health and Safety are not 'material issues' for planning purposes.
For example a threat to people and wildlife from contamination outside of a BESS site would be considered 'material' due to environmental legislation.
However, a potential risk to staff who are tasked with maintenance of BESS equipment is not a planning issue.Yes, I know it should be... and I would still raise it in a submission opposing a planning application.
Sorry but I disagree completely.
Planning law is about the effect of a development on the population in general, the environment, or neighbours. It is not about workplace safety or any other matter essentially private to the applicant, and nor should it be.
Laws are compartmentalised for good reason. In the case of planning law there are already many, many complaints that 'nothing happens in this country'. If you conflate it with workplace health and safety and other things, that gives even more ways people can try to stop anything happening for reasons which, lets face it, have nothing to do with the reason they state.
So IMHO its entirely correct that a threat to people and wildlife from contamination outside of a BESS site is 'material' due to environmental legislation but a potential risk to staff who are tasked with maintenance is not.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Indeed! As an ex-H&S co-ordinator, I would agree that the staff tasked with the duties of keeping any such equipment and the site ‘safe’ whilst ensuring that said staff and any ‘outsiders’ were not endangered whilst carrying out such duties or being present in the area is indeed a H&S matter entirely. (Steps down from his soap and in doing, so slips and trips over his own tongue.) 😉 Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
There are some strange attitudes and requirements in H&S; whereas I was responsible for ensuring the safety of all staff working in or at the various premises over which I had jurisdiction, the students were not so ‘covered’ - I just owed them a ‘duty of care’. Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @toodlesThere are some strange attitudes and requirements in H&S; whereas I was responsible for ensuring the safety of all staff working in or at the various premises over which I had jurisdiction, the students were not so ‘covered’ - I just owed them a ‘duty of care’. Toodles.
Interesting indeed!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @cathoderayIt does make one wonder why there is so much hand wringing and bed wetting in the regulatory, emergency service and insurance sectors about all lithium batteries. They need to sharpen up their act and focus on the real risks from particular types of lithium batteries, rather than on imaginary risks across the board.
All players would normally be expected to be transparent about why they are generally considering lithium batteries risky.
But clearly these batteries came into the market without much safety related research being carried out. Alternatives using raw materials that are not as tightly concentrated (in terms of supply chain in a single country) are rightly exploiting this lack of peer reviewed research to carve space in what is still a fast growing market.
From what I saw, sodium batteries are more stable, easier to recycle, etc. They seem to operate in a wider voltage range, so the inverters would need some adjustment. And I think this would make it difficult to mix use of lithium and sodium batteries and allow them to be managed by a single inverter? Anyway, this would be something to discuss in a thread about sodium batteries.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@batpred — your latest post here has more than a bit of a whiff of AI about it, be that as it may, we might hope that regulators might be transparent, even if they often aren't, but the insurance industry? They are gaming us for a profit! Plus the principle of autonomy means that a business is free to do as it pleases within the law, and is not obliged to give a single word of explanation.
Posted by: @batpredBut clearly these batteries came into the market without much safety related research being carried out.
This simply isn't true. Lithium ion batteries in general and LiFePO4 batteries in particular have be subject to very severe stress testing, and for the latter, no one, so far as I know, has ever got one to spontaneously ignite or explode. They have even been seen to survive, albeit badly scorched, at the epicentre of a fire/explosion.
Edited to correct some typos
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @batpredFrom what I saw, sodium batteries are more stable, easier to recycle, etc. They seem to operate in a wider voltage range, so the inverters would need some adjustment.
That's somewhat of an understatement. 🤨
The following table compares a 16-cell battery which must deliver 5kW to a load using the two cell chemistries you've chosen:
The much wider voltage range of the Na-ion chemistry means that it must handle greater current at the lower-end of its capacity.
The additional copper required for the inter-cell busbars and the cable to connect to a load or inverter quickly wipes out any possible cost savings.
Posted by: @batpredI think this would make it difficult to mix use of lithium and sodium batteries and allow them to be managed by a single inverter?
You wouldn't even attempt to mix different Li-ion cell chemistries on the same inverter.
Inverters and BMS units can only operate correctly and safely if they are handling one type of cell.
Have you yet looked into the specifications for a notional 5kW inverter which is designed for Sodium-ion cells?
If so, please post the URL here.
Save energy... recycle electrons!
Posted by: @cathoderay@batpred — your latest post here has more than a bit of a whiff of AI about it, be that as it may, we might hope that regulators might be transparent, even if they often aren't, but the insurance industry?
It is not AI, it was my own thinking! I was just describing a possible explanation.
The fact that there is recent research about safety of lfp batteries (when, as far as I know, there have not been significant changes in them) made me think this was a gap.
Posted by: @cathoderayPosted by: @batpredBut clearly these batteries came into the market without much safety related research being carried out.
This simply isn't true. Lithium ion batteries in general and LiFePO4 batteries in particular have be subject to very severe stress testing, and for the latter, no one, so far as I know, has ever got one to spontaneously ignite or explode.
Ok, I should have said "without sufficient safety related research being published" ...
I assume that the research published before missed key safety tests including the ones covered in the recent paper?
Additionally, very shorty after I wrote my post, I saw what seemed better safety related research on sodium batteries...
The hypothesis is them that china's dominance in lithium processing and batteries would naturally lead to statements creating conditions for sodium alternatives to be pursued...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @transparentPosted by: @batpredFrom what I saw, sodium batteries are more stable, easier to recycle, etc. They seem to operate in a wider voltage range, so the inverters would need some adjustment.
That's somewhat of an understatement. 🤨
..
Have you yet looked into the specifications for a notional 5kW inverter which is designed for Sodium-ion cells?
If so, please post the URL here.
Yes, more than an adjustment...
This is the only combined inverter+ battery that I found (from Eleven) , but the specs look very high level:
https://drive.google.com/file/d/1pG90wpIrX0OzYN4iSgJrZViJMG958heh/view?usp=drivesdk
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
I too had spotted the Na-ion battery and matching inverters from Eleven in Cambridge.
it's good to see a British company designing something for the obvious gap in the market.
Note that their inverters can only be used with their own Na-ion battery.
It's not a generic approach. They need to be transferring data between their own BMS and the inverter across the CAN-bus to make the system work.
You must use their own supplied cables for the battery connection,
And the Emergency Power Supply socket is intended to switched manually to feed the home during an outage:
Their North Sea range is fairly new, and I expect they'll add more features in later models.
Save energy... recycle electrons!
- 26 Forums
- 2,426 Topics
- 55.1 K Posts
- 161 Online
- 6,104 Members
Join Us!
Worth Watching
Latest Posts
-
RE: R290 and Foundation Air Bricks
@editor apart from the question of noise, as the argume...
By SAEnergy , 17 minutes ago
-
RE: Is it normal to use power from the grid when running off the battery?
@batpred I may be asking you for more info in how you h...
By JohnnyB , 7 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
@johnnyb The noise of the Solis is nothing very sign...
By Batpred , 7 hours ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
@papahuhu Yes, good information is often hard to find, ...
By Old_Scientist , 7 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@toodles ahhh no trouble yeah probably won't mess with ...
By Burtis , 8 hours ago
-
RE: Daikin Wireless Thermostat
@bash we have mostly south facing rooms which would ove...
By Judith , 8 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Some more examples of those that really should be benef...
By Jeff , 10 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
I've now had an interesting email from a Complaints Res...
By MairiA , 11 hours ago
-
RE: Reliable, easy to use home battery options
Correct. LiFePO₄ cells mustn't be charged if their te...
By Transparent , 12 hours ago
-
RE: Water outage in the the south-east
Indeed!Any contamination in the well water would be tra...
By Transparent , 14 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I hear some cases of apparent misconfiguration of inver...
By Batpred , 14 hours ago
-
Are split ASHPs with R290 refrigerant coming soon?
Question. Are there any (or likely to be in the near t...
By iotum , 16 hours ago
-
RE: Setback savings - fact or fiction?
Indeed. In many ways, a defrost is a setback, with the ...
By cathodeRay , 16 hours ago
-
RE: Heat pump not reaching flow temperature
The good news is that it leaves no excuse if it doesn't...
By JamesPa , 16 hours ago
-
RE: How to use my Hanchu battery storage for home without it feeding back into the grid?
@countryman-helmsley In that case is there a button ...
By IRMartini , 17 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Great. It’s not bad is it, though I agree it may repres...
By Davesoa , 18 hours ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@f1p apologies, you are absolutely correct
By Patch321 , 19 hours ago
-
RE: Samsung E101 Error Message and my ASHP Efficiency
@johnnyb amazing that the our forum is serving its purp...
By Mars , 1 day ago
-
Best option for controller upgrade? - Grant Aerona
Fairly new heat pump owner - Grant Aerona 3 10kw - and ...
By Topher , 1 day ago
-
Just a brief update to keep things transparent. Secti...
By DREI , 2 days ago