Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Single vs. three phase for heat pump, EV and appliances
We're considering the electrical needs for our house which currently has a 100A fuse on the consumer board. We have an 18kW heat pump and various other appliances (fridges, TVs, routers, distribution pumps, etc.). We're also thinking about adding an electric vehicle (EV) charger in the future. Could you advise on whether a single-phase or three-phase electricity supply would be best suited for our situation?
Additionally, what are the key differences between single-phase and three-phase electricity in the context of residential use, especially considering the high electrical demand from the heat pump and the potential addition of an EV charger?
In terms of "upgrading" to three phase, it is a matter of splintering off from the power lines to our house or it is more complex than that?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
The 18 kW/h heat pump is presumably the rated output rather than consumption? Being a little pessimistic so perhaps a COP of 3.0 meaning 6 kW/h required for the heating? I have a rather smaller drain with just over 2.5 kW/h if running flat out (rarely seen it draw more than 1.5 - 2 kW/h though). Beyond that, being all electric, we have an induction hob, immersion heater (max. 3kW/h) and one of the two microwave combination cookers runs up to about 3.5 kW/h though now that is rare as we use the air fryer for most roasting etc. We don’t have an EV, the 100 amp fuse has taken everything so far. I note that the Tesla system pulls 10 kW/h when charging plus perhaps up to 3 kW/h more for domestic draw at this time occasionally. I suppose I may have loaded the system to approx. 15kW/h at times - we are on single phase. I imagine to go three phase will be teeth suckingly expensive? Regards, Toodles. (I will be interested on the developments on this topic!)
Toodles, heats his home with cold draughts and cooks food with magnets.
A 100A supply will provide up to approximately 24kW, which should be more than adequate for virtually all domestic needs.
I believe that for improved battery life EV's should be charged slowly if possible.
@derek-m that should give us ample breathing room then. With the heat pump running flat out (and the house maxed out too), we're never drawing more than 5-6kW - spikes to 8kW if doing a legionnaires run. Interesting. Thank you.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor I did look at 3 phase, it was painful, got quoted 10k just for the DNO piece. and that was for tapping into the phases that's only 5 metres away on the street , already going to neighbours houses. Plus whatever for electrician works on my side, which I never tried to get quoted for.
I have a 100A fuse, I have a HP that pulls 6kw in worst case , only at the peak of the HW cycle. Plus 2 EV's (7kw each to charge) plus fully electric kitchen (10kw ish all maxed) plus 3 powerwalls (15kw). that does all work fine with single phase 100A. because not all are on all the time, and the batteries are bidirectional.
With 100A I can and do pull 23kw from grid during offpeak in winter for several hours if everything is charging overnight on cheap rate and the HP is running all night also. If I had less than 100A I would struggle to "download" enough cheap rate charge if both cars needed a large chunk.
Getting batteries helps as it can protect the main fuse / grid. You can tell a powerwall what the max allowed grid is, it will slow down its rate of charge (or discharge if needed, providing there is some charge in it of course) in order to protect the grid fuse.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank When I had the first 13.5 kW/h of Powerwall, the system was configured with ‘permissions’ from Tesla in as much that when the system was ready to go, the installers had to contact Tesla for final settings to be configured I think. At that time, I could charge the battery at 5 kW/h. When the second 13.5 kW’h of capacity was added, the installer (different company) had to finalise some settings with Tesla and the battery can now draw or discharge at a rate of 10kW/h to / from the grid. Recharges, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
I did have a 100A fuse but noticed a couple of weeks ago that it was replaced with an 80A one when the service head was replaced last year as a result of a rotting backing board. The ASHP is still at the 'future development' stage at the moment but I do expect to have solar PV and a 6kW battery as soon as my DNO can spare the time to address my G99 application (first submitted in November, but that's another story). I already have an EV and charger. There is potentially a large power demand in the kitchen, with 2 ovens, a microwave, washing machine, dryer, dishwasher and hot tap, as the main loads. It's most unlikely that everything will be on at the same time, but I will monitor the trends and will ask for my 100A fuse to be returned if I think there is an issue. As a safety measure, both the EV charger and battery charger will automatically reduce demand if necessary, in any case.
I have single phase with a 100A fuse (we are a 100% electric house). The wiring is only 7 years old and we have a smart meter. The DNO is SSEN in this part of Oxfordshire. A neighbour, with two large electric SUV's, and wants to charge them quickly, has recently had their supply upgraded to three phase.
Although single phase is fine for our needs at present (any EVs clearly limited to 7kW charging though), it prompted me to consider the issue. I think electrical supply capacity will be like Internet speeds. We will mostly be happy with 1 phase for now but more and more people will want 3 phase as we pile on more demanding applications. But there won't be grid capacity to meet this demand. So get in early while it is still available?
In our village all power is brought in on overhead cables which share telegraph poles with the old BT phone service (we have fibre to the door internet via buried cables now). The nearest to me is in my neighbour's garden. SSEN quoted £6k + VAT to bring 3 phase to my meter. All new works have to go underground and this price excluded the cost of digging a suitable trench from the pole to my property.
I don't have an EV at present and itseems quite expensive for some forward planning that I presently have no urgency to implement.
The nerd in me would love to have 3 phase just because but, for now, I'll take my chances that single phase will serve us well for several years to go. I hope I am not proved wrong.
Mike
Grant Aerona HPID10 10kWh ASHP
We’re all elec too, and on a 100A single phase fuse. I haven’t considered changing it to 3phase - it would be simple though to fit even more PV 😎 Instead we got a home battery, which effectively allows more PV than we can export, and also removes pesky day time electricity use.
As is at night when plugged in the car draws 32A, the home battery 16A, heatpump 3A. During the day we’re either zero or exporting up to our permitted 32A.
Our elec voltage varies a lot, from 225V(at night if the Tesla is charging) up to 252V(day, full export).
I had a survey from UKPN as I was considering moving my supply (inside to outside) and we touched in three phase.
The costs were not small for a 3m distance to the cable - bout £5k. That was purely the UKPN costs - I'd need to organise the trench on my property and any other work.
His view was for most domestic cases 100A single phase was adequate and that included induction hob, PV, battery, EV charger & heat pump.
@gunboatdiplomat I should be OK then as I don’t have the EV but do have the rest! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,603 Topics
- 60.6 K Posts
- 268 Online
- 6,958 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Anyone concerned about GivEnergy?
Oh for a Crystal Ball and a polishing cloth… Toodles.
By Toodles , 9 minutes ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 27 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@sonosppp, the Powerflex 2000 is a really interesting p...
By Mars , 54 minutes ago
-
RE: Ecoflow UK Support & Info Thread
@sonosppp I've just recorded my review of the Delta 3 M...
By Mars , 56 minutes ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Sorry, I don't know what a UFH is. That valve ...
By bazcurtis , 2 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
True. But a minor earth leakage will make no significa...
By JamesPa , 4 hours ago
-
RE: Renewables & Heat Pumps in the News
A bit meh! TBH. No strong opinion and not really bothe...
By JamesPa , 4 hours ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
That's true. Some heat pumps quote capacity including ...
By JamesPa , 7 hours ago
-
RE: Microbore heat pump installs
It's possible you don't need to replace the microbore b...
By JamesPa , 8 hours ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 10 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 21 hours ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 21 hours ago
-
@transparentransparent I guess there is nothing you don...
By David999 , 22 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Alan(alan22) Manufacturer: Valiant Mo...
By Alan , 22 hours ago
-
Having seen that screenshot, I think I know what "Gener...
By Transparent , 22 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
I had an initial estimate for a Grant HP, as we are loo...
By Batpred , 23 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
So we are starting to see the options land where they m...
By Batpred , 24 hours ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
After running a search in the god ol' watson, this is w...
By Batpred , 1 day ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
@drei I wrote an email to Greg Jackson at the end of la...
By Toodles , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
Sorry to resurrect, but did you have any luck tweaking ...
By marcexec , 1 day ago
-
RE: Choosing a time for DHW heating?
@grahamf On the initial question of when to heat the DH...
By DavidAlgarve , 1 day ago
-
RE: ECO4, ECO3, ECO2, ECO1, HUS, BUS, GBIS Dedicated Support and Advice
It has come to my attention that Consumer Energy Soluti...
By Mars , 1 day ago
-
Hello I’ve sent an email to @editor asking if there...
By Little Lights , 2 days ago
-
RE: Replacement parts Samsung Gen5 control panel
Thanks so much for your detailed reply. I will see if I...
By Ian L , 2 days ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Your ‘hand waving’ above isn’t too far off mostly. Our ...
By Judith , 2 days ago