Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
Hello all,
I have received the heat pump design from eon after 6 weeks of waiting
here's key points:
-
The estimated heat loss is approximately 3.92 kW. with proposed a 5 kW Vaillant aroTHERM Plus heat pump. This sizing is based on continuous heating (24/7 operation) and does not include spare capacity for intermittent heating or temperature setbacks.
-
A 250-litre Vaillant hot water cylinder is included in the proposal and is to be installed in the loft space, subject to a suitable base being constructed by a third-party joiner and approved by a structural engineer.
-
Two radiators are proposed for replacement
The proposed system flow temperature is 50°C for -1.7°C(London suburbs)
scop 3.41
TRVs are proposed to be removed from all radiators to ensure sufficient water flow through the heat pump system. This helps support defrost cycles and improves overall efficiency in line with an open-loop system design.
-
Upgrading the existing 15 mm mains cold water supply is not included within the scope of the heat pump installation.
is the temperature flow 50°C quite high?
Can I insist on lower design temp?
primary pipes 28mm branching to 22mm then 15mm to the rads
no UFH, propery is fairly insulated.
is it a haggling process with eon since they can swap up to 60% of rads
also, the existing water tank and the header in the loft seating just above a bearing wall.
my concern is getting a structural engineer to calculate the load, only to tell me that it has to go where the existing tank is seating.
what the solution here, do they need to swap and putting the cylinder, however platform is needed beforehand.
have i missed anything
I have attached the design proposal
Many Thanks
I wasn’t sure reading your quote if I had correctly understood that they predicted you would be paying more in bills than at present. Then on p36 is is in no doubt that is what they predict. You don’t comment on that which I find surprising.
They don’t say how big your existing cylinder is (which might be my oversight in a quick skim read)., therefore it’s difficult to understand why they want to move it to the loft, where it will loose more heat, being outside your heated envelope. The DHW is the big disruptive aspect.
You've got nice big primary piping so no need for replumbing there. I don’t understand your comment on cold water feed dimensions, since you need less supply capacity with a cylinder than with a combi-boiler. What have I missed?
Taking the TRVs off seems unnecessary, because the old analogue ones close down gradually and don’t impact the volume suddenly (and hence induce fast cycling). You might want to keep them especially in the bedrooms for comfort and preference.
Yes 50c is on the high end but using 45C might mean changes to radiators which mean the room is less easy to use afterwards. You’ll only know if they do you a 45C quote too. But the radiators are easily changed later
In general it’s a sensible proposal to me but I’m sure other eyes will see what I didn’t.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
- 26 Forums
- 2,673 Topics
- 62.5 K Posts
- 237 Online
- 7,084 Members
Join Us!
Directory
Degrees of Separation
Latest Posts
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
I wasn’t sure reading your quote if I had correctly und...
By Judith , 1 hour ago
-
RE: Several AC coupled batteries
I think with any size of heat pump you are likely to br...
By AndrewJ , 1 hour ago
-
RE: Help with quotes/proposals
If you tell us a bit more about the quotes and your hou...
By JamesPa , 3 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Vaillant arotherm plus 12kW. Installed March 2025. Ex...
By Harebell , 11 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
What exactly is it proposed to fit?
By JamesPa , 11 hours ago
-
RE: Load Shift and Lifestyle Shift Complete - our journey has ended, for now
Last year we managed a net nil cost. Exceeding all my h...
By Tim441 , 15 hours ago
-
This is exactly our ethos, we have restricted our servi...
By ASHP-BOBBA , 23 hours ago
-
-
RE: MCS 2.0 - Changes in January 2025
It strike's me that there's various improvements which ...
By Temperature_Gradient , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@majordennisbloodnok The M5StickC turned up...
By Bash , 1 day ago
-
-
Many messages back and forth later… GOV UK One Login ...
By Toodles , 1 day ago
-
RE: Say hello and introduce yourself
@will-h, this isn't a dig but we would prefer if anyone...
By Majordennisbloodnok , 1 day ago