Vaillant water pressure gauge vs Analogue gauge
Posted by: @jeegnesh@adamk - Its a huge system, ground floor is predominantly UFH around 100sqm, rest is rads I think 13 of them
just wondering if the UFH is creating some back pressure and the rad locksheilds are closed down too much so when the pump kicks in its pumping against too much resistance.
@adamk not sure I want to mess with the lockshields I assume that would mess with the balancing.
have someone coming next Wednesday to take a look at all the issues.
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
As winter is coming back, I can give an update -- so the new installer came months ago and flushed the system and removed the small strainer and instead a regular Y strainer 28mm has been added -- after this the weather was good and so no real testing. My heating has been running lightly for a month or so and guessing this week it is ramping up.
The good news is after the clean and new bigger strainer my flow rate was touching 2,000 and many months after I just took a look and it still exactly the same figure which suggests the blockage issues are no more.
The pressure gauge still has the same behaviour 1.7bar when off and 1.3 when running this is consistent behaviour, which I still don't know is right or wrong.
Winter 2 - let the games begin again (oh my annual service is due too 🙂 (first one)
13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car
Posted by: @jeegneshThe pressure gauge still has the same behaviour 1.7bar when off and 1.3 when running this is constistent behaviour, which I still don't know is right or wrong.
Mine does something similar, I'm not worried about it, I assume it's just dynamic pressure difference due to resistance in system. Without pressure differences, generated by the water pump, there would be no flow.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 424 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsubishi Ecodan R290 10kW performance
@jamespa Time for an update. My installer has been to v...
By Ecoste , 12 minutes ago
-
10kw heat pump run in 24*7 data?
Hey so I have a Valliant Arotherm 10kw this is only my ...
By jeegnesh , 16 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
I am not sure who got the wrong end, after the two or t...
By Batpred , 25 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@swwils suggested me to stick to givEnergy. @dcsh, @...
By Batpred , 30 minutes ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
@davidnolan22 Thanks for the graph. That's really us...
By lukewarmbath , 42 minutes ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
@jamespa Agreed I don't feel concerned about this, espe...
By jeegnesh , 47 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
That's good to know, thanks. I'll definitely be using ...
By AndrewJ , 53 minutes ago
-
RE: Electricity price predictions
@jeff Keeping the ‘smash & grab’ installers who get...
By Toodles , 58 minutes ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@toodles Yep, and it is not even a sticking plaster ...
By Jeff , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
I agree, imperfect systems like voting for politicians ...
By Batpred , 7 hours ago
-
RE: Gov wants to alter our FIT contracts from rpi to cpi
The consultation is just part of the normal process for...
By Jeff , 7 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@mairie - Your constituency member, Dr Zubir Ahmed MP, ...
By Transparent , 8 hours ago
-
@transparent @old_scientist Quick update, I submitted...
By Batpred , 23 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Lol. I know they CAN be calibrated, it’s just ...
By Crimson , 23 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
Yes thats true, but that cant happen unless the room te...
By JamesPa , 24 hours ago
-
-
Do Heat Pumps need to start up at Full Power?
When our heat pump starts up, (Daikin EDLA08 8 kW Monob...
By Toodles , 1 day ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@colinc good luck with your project! UFH is the absolut...
By Judith , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Just wondering if/where Ideal might be on your de...
By simonwig , 2 days ago
-
@judith I haven't noticed any noise myself yet, nor my ...
By Eliuccio , 3 days ago