Vaillant water pressure gauge vs Analogue gauge

21 Posts
4 Users
2 Reactions
1,725 Views
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 92
Topic starter  

@adamk - Yes they get very close when HP is off within 0.1 or 0.2 once the HP goes on there a difference of 0.4-0.6


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote
(@adamk)
Honorable Member Member
Joined: 10 months ago
Posts: 192
 

yeah sounds like its pumping against something. is the whole circuit UFH?



   
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 92
Topic starter  

@adamk - Its a huge system, ground floor is predominantly UFH around 100sqm, rest is rads I think 13 of them


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote



(@adamk)
Honorable Member Member
Joined: 10 months ago
Posts: 192
 

Posted by: @jeegnesh

@adamk - Its a huge system, ground floor is predominantly UFH around 100sqm, rest is rads I think 13 of them

just wondering if the UFH is creating some back pressure and the rad locksheilds are closed down too much so when the pump kicks in its pumping against too much resistance.

 



   
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 92
Topic starter  

@adamk not sure I want to mess with the lockshields I assume that would mess with the balancing. 

have someone coming next Wednesday to take a look at all the issues. 


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
👍
1
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 92
Topic starter  

@adamk yes they equalise once off


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 92
Topic starter  

As winter is coming back, I can give an update -- so the new installer came months ago and flushed the system and removed the small strainer and instead a regular Y strainer 28mm has been added -- after this the weather was good and so no real testing.  My heating has been running lightly for a month or so and guessing this week it is ramping up.

The good news is after the clean and new bigger strainer my flow rate was touching 2,000 and many months after I just took a look and it still exactly the same figure which suggests the blockage issues are no more.

The pressure gauge still has the same behaviour 1.7bar when off and 1.3 when running this is consistent behaviour, which I still don't know is right or wrong.

Winter 2 - let the games begin again (oh my annual service is due too 🙂 (first one)


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3659
 

Posted by: @jeegnesh

The pressure gauge still has the same behaviour 1.7bar when off and 1.3 when running this is constistent behaviour, which I still don't know is right or wrong.

Mine does something similar, I'm not worried about it, I assume it's just dynamic pressure difference due to resistance in system.  Without pressure differences, generated by the water pump, there would be no flow.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@jeegnesh)
Reputable Member Member
Joined: 1 year ago
Posts: 92
Topic starter  

@jamespa Agreed I don't feel concerned about this, especially as it reverts back, so it can't be leaking out.


13.6kw Solar, 27kw Battery, 10kw Heat Pump and EV Car


   
ReplyQuote