Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm Plus PCB Failure
Hello all
I have a 5kw Arotherm Plus ASHP which was commissioned around 18 months ago however unused for around 9 months.
On restarting the system the ASHP was showing connected but wouldn't start then heat was requested (DHW or Heating) and after a few hours F.1117 Compressor Failure was shown.
Investigating further its evident that the 240vAC neutral on the PCB has failed - looks like it has overheated/melted.
Has anyone had similar issues and if so do you know the root cause? I've temporarily repaired the board which now means the ASHP is functional so I know this is the problem but before I replace the board I'd like to know why it happened and how to try and prevent it happening again!
I'll try and contact Vaillant directly also.
Thanks in advance for any advice!!
Hi, I have the same problem. Same place, what was the cause of the problem?
thx for the reply,
wim
Your original post must have fallen into the 'black hole' that appears to exist in the website from time to time.
Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.
@derek-m , @wimdeboysere - I've no idea what caused it - could see how potentially was condensation, didn't open the unit up prior to restarting it.
A new board is in and all has been fine since!
Posted by: @derek-mYour original post must have fallen into the 'black hole' that appears to exist in the website from time to time.
Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.
It is difficult to tell from the photo's, but PCB's for outdoor use should be coated with a waterproof lacquer.
I think the main board on the unistor is also Broken, screen shows connection failure and i cant measure power on the bus connection, Room thermostat is also dead.So the best thing tot do is put in a new main also of does it get power from the (dead)heatpump outside?
@pdfreeman did you have to pay for the replacement and did Vaillant offer any information on what may have caused this?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
@wimdeboysere did you have your system installed after pdfreeman’s and how long has yours been installed?
Have you raised it with Vaillant?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
Did the fried slug on the left have anything to do with the failure or was it collateral damage!
-
Heat pump done right first time? Installation in Kent.
1 month ago
-
Vaillant arotherm plus heat pump frost protection
3 months ago
-
ECO4, ECO3, ECO2, ECO1, HUS, BUS, GBIS Dedicated Support and Advice
3 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
2 years ago
-
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
2 years ago
- 26 Forums
- 2,724 Topics
- 63.8 K Posts
- 579 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Microgeneration Certification Scheme (MCS)
I’ve just spotted that Ian Rippin is leaving MCS as CEO...
By Mars , 30 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
Hi. I have 16 panel solar panels producing about 20k...
By peterackstraw , 5 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 6 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 20 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago