Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm Plus PCB Failure
Hello all
I have a 5kw Arotherm Plus ASHP which was commissioned around 18 months ago however unused for around 9 months.
On restarting the system the ASHP was showing connected but wouldn't start then heat was requested (DHW or Heating) and after a few hours F.1117 Compressor Failure was shown.
Investigating further its evident that the 240vAC neutral on the PCB has failed - looks like it has overheated/melted.
Has anyone had similar issues and if so do you know the root cause? I've temporarily repaired the board which now means the ASHP is functional so I know this is the problem but before I replace the board I'd like to know why it happened and how to try and prevent it happening again!
I'll try and contact Vaillant directly also.
Thanks in advance for any advice!!
Hi, I have the same problem. Same place, what was the cause of the problem?
thx for the reply,
wim
Your original post must have fallen into the 'black hole' that appears to exist in the website from time to time.
Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.
@derek-m , @wimdeboysere - I've no idea what caused it - could see how potentially was condensation, didn't open the unit up prior to restarting it.
A new board is in and all has been fine since!
Posted by: @derek-mYour original post must have fallen into the 'black hole' that appears to exist in the website from time to time.
Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.
It is difficult to tell from the photo's, but PCB's for outdoor use should be coated with a waterproof lacquer.
I think the main board on the unistor is also Broken, screen shows connection failure and i cant measure power on the bus connection, Room thermostat is also dead.So the best thing tot do is put in a new main also of does it get power from the (dead)heatpump outside?
@pdfreeman did you have to pay for the replacement and did Vaillant offer any information on what may have caused this?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@wimdeboysere did you have your system installed after pdfreeman’s and how long has yours been installed?
Have you raised it with Vaillant?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Did the fried slug on the left have anything to do with the failure or was it collateral damage!
-
Heat pump done right first time? Installation in Kent.
4 months ago
-
Vaillant arotherm plus heat pump frost protection
5 months ago
-
ECO4, ECO3, ECO2, ECO1, HUS, BUS, GBIS Dedicated Support and Advice
6 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
2 years ago
-
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
2 years ago
- 27 Forums
- 2,787 Topics
- 65.8 K Posts
- 1,537 Online
- 7,192 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: PV and battery long payback - sense check query
@energystoragetech it's highly improbable that @davidb ...
By Transparent , 6 hours ago
-
RE: Heat Geek installations: share your experiences
@editor I suspect that the Heat Geek online quote is a ...
By AndrewJ , 6 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
@toodles The tepeo ZEB is a residential heat battery, w...
By wully , 6 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
Ah, yes. Thanks for clarifying.
By Transparent , 6 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
Ah, that explains it. Thanks! Then I agree with ot...
By cathodeRay , 7 hours ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
@trebor12345 I have been meaning to get home assista...
By Batpred , 17 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
SunSynk hybrid inverters also have the capability to as...
By Transparent , 20 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
If you've got a sash window or a door you can remove th...
By EtchedPixels , 21 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Roughly how most air/air is done except that step 3 doe...
By EtchedPixels , 21 hours ago
-
RE: Nook batteries from Octopus
@batpred If your energy use is low enough that just get...
By EtchedPixels , 21 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
I suspect 4 yrs ago, their approach had not got to this...
By Batpred , 22 hours ago
-
RE: battery storage without solar
Also don't forget that in you may not be able to use th...
By JamesPa , 1 day ago
-
RE: Tesla Powerwall (2) Calibration Cycles
One practical safeguard is to separate the calibration ...
By EnergyStorageTech , 1 day ago
-
RE: Getting closer to a finished Haier system
Apart from sealing the external Primary Pro joints and ...
By Singlespeed , 2 days ago