Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm Plus PCB Failure
Hello all
I have a 5kw Arotherm Plus ASHP which was commissioned around 18 months ago however unused for around 9 months.
On restarting the system the ASHP was showing connected but wouldn't start then heat was requested (DHW or Heating) and after a few hours F.1117 Compressor Failure was shown.
Investigating further its evident that the 240vAC neutral on the PCB has failed - looks like it has overheated/melted.
Has anyone had similar issues and if so do you know the root cause? I've temporarily repaired the board which now means the ASHP is functional so I know this is the problem but before I replace the board I'd like to know why it happened and how to try and prevent it happening again!
I'll try and contact Vaillant directly also.
Thanks in advance for any advice!!
Hi, I have the same problem. Same place, what was the cause of the problem?
thx for the reply,
wim
Your original post must have fallen into the 'black hole' that appears to exist in the website from time to time.
Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.
@derek-m , @wimdeboysere - I've no idea what caused it - could see how potentially was condensation, didn't open the unit up prior to restarting it.
A new board is in and all has been fine since!
Posted by: @derek-mYour original post must have fallen into the 'black hole' that appears to exist in the website from time to time.
Looking at the photos I suspect that the cause may have been condensation, possibly due to the heat pump not being used for 9 months.
It is difficult to tell from the photo's, but PCB's for outdoor use should be coated with a waterproof lacquer.
I think the main board on the unistor is also Broken, screen shows connection failure and i cant measure power on the bus connection, Room thermostat is also dead.So the best thing tot do is put in a new main also of does it get power from the (dead)heatpump outside?
@pdfreeman did you have to pay for the replacement and did Vaillant offer any information on what may have caused this?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
@wimdeboysere did you have your system installed after pdfreeman’s and how long has yours been installed?
Have you raised it with Vaillant?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
Did the fried slug on the left have anything to do with the failure or was it collateral damage!
-
Heat pump done right first time? Installation in Kent.
2 months ago
-
Vaillant arotherm plus heat pump frost protection
3 months ago
-
ECO4, ECO3, ECO2, ECO1, HUS, BUS, GBIS Dedicated Support and Advice
4 months ago
-
Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
2 years ago
-
Vaillant Arotherm monobloc error f.788 - ASHP is not working!
2 years ago
- 27 Forums
- 2,745 Topics
- 64.5 K Posts
- 201 Online
- 7,149 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@toodles I invested on Miele a pair of frodge frozor wh...
By AgentGeorge , 5 minutes ago
-
RE: Flushing system, cleaning and inhibitor
Flush and fill all complete. Octopus kindly gave us a...
By Old_Scientist , 15 minutes ago
-
RE: Wood burner with ASHP - direct air?
For what it's worth I installed a wood burner in this o...
By BlizzardGreen , 1 hour ago
-
@editor Thanks for your response and recommendations. ...
By DavidB , 8 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
I think I saw a diagram for an exhaust air dhw tank wit...
By JamesPa , 22 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks, however that's an answer to a subtly different ...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Such elegant symmetry. look at my lumpy bag of...
By Papahuhu , 4 days ago
-
RE: PV and battery long payback - sense check query
Quite probably not, but you can get a 32A relay and a S...
By JamesPa , 4 days ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s Look forward to making contact soon! Regards, To...
By Toodles , 4 days ago
-
I don't notice mine defrosting, and most of the time Im...
By JamesPa , 5 days ago
-
RE: Do I need to change the control unit when replacing my Ecodan Air Source Heat Pump
Kind of you, @calumm, but it was @f1p who did the heavy...
By Majordennisbloodnok , 5 days ago
-
RE: Electricity price predictions
2. As EV ownershp increases it'll certainly increase de...
By EtchedPixels , 6 days ago