Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung HTQuiet configuration for the 6th generation controller
hi all,
I have been playing with the configurations over the past weeks. Using this material:
2. https://midsummerwholesale.co.uk/pdfs/samsung-sunamp-quick-start-rev-2.pdf
The installer indicates that he set the Samsung LCD controller as the thermostat. I managed to organize all the water law stuff, etc. It is getting warm in the house now. Not many problems there. The cold days I had a COP of 3 on average, now approaching 4. So that seems to be more or less "in control".
Without an additional external thermostat, #2091 and #2092 should be zero = not used (according to the manual), and #2093 should be put to any of these values (default = 4):
0 Not use
1 Use signal only on/off
2 Use (signal on/off) or WL interlink off (water pump 1)
3 Use (signal on/off) or WL interlink off (water pump 2)
4 Use (signal on/off) or WL interlink off (water pump 3)
These values seem to behave similarly to the ones described in the manual on page 28. The standard temperature is set to "indoor". The Samsung LCD controller gives the right indoor temperature in the room (double-checked with some other devices in the same room).
The issue: the controller triggers based on the ambient temperature: if the room is getting below 20C, it starts the heat pump to heat the radiators following the water law (WC). However, it keeps on doing this and does not seem to "stop" the heat pump once it reaches the required temperature... The above values try to reduce hysteresis, but, also, option 1 does not trigger an "off". I first thought it had something to do with the difference that needs to be larger than a threshold value (Indoor Zone option -> Temperature unit -> 0.1/0.5/1, but that seems incorrect, more for setting the temperature).
The inside temperature sometimes goes up to 21C. It does, however, stop sometimes for whatever reason, I can not get my hands on it.
My reasoning now is that the "Use (signal on/off) or WL interlink off" does not trigger the signal off. But it stops because of the "WL interlink off"... I have no idea what the WL interlink is. My best guess now is that it has to do with #4052, the target deltaT, as usually, in the course of the afternoon, with warmer temperatures, the heat pump is triggered to stop. My eye also fell to #4061 for "zone control", no idea what this is...
Does anybody know what the WL interlink logic is doing and how I control this? Anybody any clue why the "signal on/off" only triggers on and no 'off"?
thanks for any help or pointer...
tom
- 26 Forums
- 2,646 Topics
- 61.8 K Posts
- 1,037 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Solar Produced vs Home Consumed
It's worth adding that if you have a hot water tank and...
By JamesPa , 2 minutes ago
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
@editor Sorry Mars, I didn’t see a notification about ...
By Toodles , 21 minutes ago
-
RE: Hitachi Heat Pump being replaced with Vaillant
Yes to be configured as a volumiser. The pump is to be...
By trebor12345 , 39 minutes ago
-
RE: Anyone concerned about GivEnergy?
So it seems subscription day has finally arrived for Gi...
By TechnoGeek , 2 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 5 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 5 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 18 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 1 day ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago