Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
I've been using this heatpump for two winters now and am usually happy with it but am annoyed by the low CoP and it seems like whatever setting I use, it does not get better.
In the screenshots it runs on the heat curve setting (-1 because it ran too hot for my liking). The auto-adaptation setting often is around 1.7 CoP and the current ones somewhere between 2 and 2.5.
I was wondering if there is anything obvious in how it runs, that might make it less efficient? I seems like the heatpump turning on and off rather than constantly running at a lower frequency is not ideal. From the few Melpump screenshots I've seen on here, this is not usually the case.
Any ideas?
The detailed report in the lower figure is from the 10th Feb. It seemed like an average enough day for an example.
Welcome to the forums.
I assume that you're getting the MelPump data via the MelCloud integration? Assuming so, then the daily totals are those being reported by the Ecodan unit itself, and Mitsubishi's reporting tends to overstate energy usage to some extent. Is there an electricity smart meter within the installation, as the first thing to check would be how closely the usage figures align to the actual consumption?
Having said that, the MelPump data suggests that the unit is cycling quite frequently at an outside air temperature of around 7°C, which will adversely impact efficiency, so there is definitely scope to look to improve how it is running if this is typical. The COP figures across the 12 month period do also look very low in general, albeit the assumption is that the summer months are showing only performance for Domestic Hot Water, which will naturally be less efficient. Oddly, your MelPump data doesn't look like its giving the option to show DHW COP and Heating COP separately, which is different to how the graphs display on my system.
Those with more technical expertise than me will likely reply requesting more specifics regarding your system. The logical start point for performance issues would typically be an oversized system but a 6kW heat pump would suggest a fairly low heat loss. Do you have any information as to what the assessed heat loss was at installation?
One thing I did spot was that the flat target temp you're showing in the graph is for zone 2, but the actual data is for zone 1. Is your system set up as a zoned one, or is there a single open loop? On the current display the target temp needs to be shown for zone 1 so that we can see what the weather comp setting is trying to achieve, rather than the flat profile for (a presumably non-existent) zone 2.
On the detailed report, do you have a 'share as URL' option? If so, then this would be the most useful way to post the data, as it allows readers to highlight the individual graph points, which may assist their diagnosis.
There are definitely some elements of your post that I can attribute to the inaccuracies of the Mitsubishi reporting, one of which is the fact that the inaccuracies worsen when auto-adaptation is used (see post here regarding this https://renewableheatinghub.co.uk/forums/postid/58460/) which would potentially explain some of the gap between the 1.7 Auto Adaptation figure and the higher one for weather compensation. However, the overall CoP numbers do look very low in general, so any inaccuracies of reporting are only part of the diagnosis and the frequent cycling on the snapshot that you have provided is definitely indicative of inefficient running.
The good news is that there's a helpful community here who can assist in trying to better understand this. I'm a fellow Ecodan user with a particular focus on it's reporting output, but there are others with far better understanding of the technicalities than me.
130m2 4 bed detached house in West Yorkshire
10kW Mitsubishi Ecodan R290 Heat Pump - Installed June 2025
6.3kWp PV, 5kW Sunsynk Inverter, 3 x 5.3kWh Sunsynk Batteries
MyEnergi Zappi Charger for 1 EV (Ioniq5) and 1 PHEV (Outlander)
User of Havenwise (Full control Jun-Dec 2025, DHW only from early Dec)
Subscriber to MelPump App data via CN105 Dongle Kit
Thank you for the kind introduction!
Posted by: @sheriff-fatmanWelcome to the forums.
I assume that you're getting the MelPump data via the MelCloud integration? Assuming so, then the daily totals are those being reported by the Ecodan unit itself, and Mitsubishi's reporting tends to overstate energy usage to some extent. Is there an electricity smart meter within the installation, as the first thing to check would be how closely the usage figures align to the actual consumption?
No, sadly not. It's all coming from the unit itself.
Posted by: @sheriff-fatmanWelcome to the forums.
Having said that, the MelPump data suggests that the unit is cycling quite frequently at an outside air temperature of around 7°C, which will adversely impact efficiency, so there is definitely scope to look to improve how it is running if this is typical. The COP figures across the 12 month period do also look very low in general, albeit the assumption is that the summer months are showing only performance for Domestic Hot Water, which will naturally be less efficient. Oddly, your MelPump data doesn't look like its giving the option to show DHW COP and Heating COP separately, which is different to how the graphs display on my system.
I also don't see any options for seeing the COP separated. I assume that's because of the system itself, rather than the software?
Posted by: @sheriff-fatmanThose with more technical expertise than me will likely reply requesting more specifics regarding your system. The logical start point for performance issues would typically be an oversized system but a 6kW heat pump would suggest a fairly low heat loss. Do you have any information as to what the assessed heat loss was at installation?
I don't recall any info on that but we compared with similar places (semi-detached with 2 adults +2 kids, similar house age+renovations) and 6 kW seemed to be the right choice.
Posted by: @sheriff-fatmanOne thing I did spot was that the flat target temp you're showing in the graph is for zone 2, but the actual data is for zone 1. Is your system set up as a zoned one, or is there a single open loop? On the current display the target temp needs to be shown for zone 1 so that we can see what the weather comp setting is trying to achieve, rather than the flat profile for (a presumably non-existent) zone 2.
Indeed, I should have ticked both. We have 2 zones with zone 1 being the upstairs with radiators and zone 1 downstairs with underfloor-heating. You can see them both using the link below
I have considered that one of the two zones might not be configured properly but I have not noticed any obvious heat loss anywhere. Maybe it is the fact that the system is juggling two zones?
Hi Fellow Ecodan owner here.
Looking at your MelPump data if I read it correctly it looks like your heatpump is heating the two zones to the correct temperature - ie 20 Deg room temp and presumably you are warm enough.??
Your delta T is quite low which suggest a good flow rate. If your main concern is a low reported COP it would be worth trying to find the flow and return temperature probes that the Ecodan will be used to calculate the heat output and hence the COP. These are often just taped onto the pipes and not insulated and don’t necessarily get an accurate reading. The heat output is calculated by multiplying the flowrate x delta T x heat capacity of fluid. With Delta T being only a couple of Deg it doesn’t take much of an error to have a big impact on the COP calculation.
Your heatpump is cycling but the run times seem to be > 30 min so not really classed as short cycling, 7 Deg outside is middling tending towards mild so it’s possible your heatpump might be a bit oversized.
how does it run when it’s colder? Does it run continuously at say 4 Deg C?
I presume your system is using the Mitsubishi 2 zones capability - ie with a motorised blending valve controlled by the heatpump to blend down the water for UFH?.
Do you know if you have glycol ? From memory there is a setting in the installer menu for this - this affects the heat capacity of water so the heatpump needs to know this to calculate COP correctly.
I don’t really have experience of the Mitsubishi COP calculation as I use external monitoring on my system.
Hope that helps.
Posted by: @travellingwaveLooking at your MelPump data if I read it correctly it looks like your heatpump is heating the two zones to the correct temperature - ie 20 Deg room temp and presumably you are warm enough.??
Thank you. Absolutely, it's nice and cozy.
Posted by: @travellingwaveYour delta T is quite low which suggest a good flow rate. If your main concern is a low reported COP it would be worth trying to find the flow and return temperature probes that the Ecodan will be used to calculate the heat output and hence the COP. These are often just taped onto the pipes and not insulated and don’t necessarily get an accurate reading.
Would they be outside on the actual heat pump or closer to the water tank?
Posted by: @travellingwaveYour heatpump is cycling but the run times seem to be > 30 min so not really classed as short cycling, 7 Deg outside is middling tending towards mild so it’s possible your heatpump might be a bit oversized.
how does it run when it’s colder? Does it run continuously at say 4 Deg C?
Here is a record from last week, when it was a bit colder and the COP dropped below 2. No continuous running.
Posted by: @travellingwaveI presume your system is using the Mitsubishi 2 zones capability - ie with a motorised blending valve controlled by the heatpump to blend down the water for UFH?.
Yes, that's the one.
Posted by: @travellingwaveDo you know if you have glycol ? From memory there is a setting in the installer menu for this - this affects the heat capacity of water so the heatpump needs to know this to calculate COP correctly.
We had two radiators uninstalled during re-plastering, which resulted in some water leaking out, but I wouldn't have thought that it would have a massive impact. Maybe it does!
One other thing I noticed, where I just don't get how the heatpump makes decisions, is where it just stops and let's the pipes cool down (often at night), like last night. And about once every two weeks it needs the boosters to get back up, which is not enough and the house cools down until I restart the system.
I'll see that I find the probes and will try to calculate my own COP. Is this where I would place an external monitoring system?
Thanks again!
Well you are warm and your flow temp at 3 Deg outside temp is only 35 degrees so you should be getting pretty decent COP. Hopefully it is just a measurement issue rather than real poor performance.
The flow and return sensors would normally be found near to the cylinder. They connect into the big white box - FTC6 which also normally lives near the cylinder. If you spot any cables seemingly attached to the pipe work that may be them- the sensor itself is a small metal tube about 5mm diameter maybe 20mm or so long, often just taped to the pipe with insulating tape. If you can’t find them send a few pictures of the pipe work around the cylinder.
your heatpump is still cycling. At 3 Deg outside one would expect continuous operation. Do you know if your rads have been balanced? Do some get hotter than others? May not be very easy to tell as 35 Deg is barely warm to the touch.
What I did to balance mine is put the Ecodan into fixed flow temp control mode (I think you are currently in Auto Adapt Mode) Once in fixed mode you can set the flow temperature manually to a much higher value - say 50 degc - this makes it easier to feel which radiators are getting either too much or not enough flow as you will be able to feel it better. You can then balance the system- various videos on how to do this - basic idea is to adjust the lock shield valves on each radiator so that water flow is distributed more or less evenly. In your case it is possible that the rads closer to the pump are too open and leading to water short circuiting back to the heatpump meaning the heat pump can’t get rid of the heat hence cycling.
Might not be the issue but certainly worth checking.
Did you get any handover pack from your installer? This should state if glycol antifreeze has been added and what concentration.
Ref radiator removal- have you checked system pressure - should be about 1.5 bar, might need topping up if you’ve had a rad off.
By the way don’t leave it in fixed temp mode - very inefficient - just use it for balancing.
Ref stopping and needing booster to get back up to temp - that sounds like something not set up right. Personally I would disable any booster heater as it could mask other issues and is costly to run - you should not need it.
It can be normal for the heatpump to stop if either the room temp gets above the target - or flow temp gets above target, it should start back up automatically once things have cooled down.
Where is your heatpump control screen by the way , please don’t tell me it’s in the airing cupboard next to the cylinder😱
when you say you have to restart it what are you having to do? Any error messages?
Some of this stuff is getting quite technical so let me know if not clear.
From memory disabling booster requires changing DIP switch settings inside FTC so may not be something you want to do/ but in any case booster should only come on if heatpump is struggling to reach temp.
-
Interpreting MelPump data / cycling?
3 days ago
-
Ecodan Zone 2 Mitshibishi thermostat Auto Adapt
1 month ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
2 months ago
-
Running my new Nibe ASHP efficiently
2 months ago
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
2 months ago
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 425 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 3 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 4 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 6 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 7 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 8 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 8 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 9 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 10 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 12 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 12 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 14 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 14 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 15 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 16 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago