Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Rethinking High-Temperature Heat Pumps
The shift towards environmentally-friendly heating technologies is a critical aspect of current sustainable development efforts. Heat pumps have been recognised for their potential to contribute to energy efficiency and environmental sustainability. Nonetheless, new data suggests there may be considerable differences in efficiency and cost between high-temperature heat pumps and those operating at lower temperatures. A thorough review of a slide from an environmental consultant reveals significant findings pertinent to this discussion.

The slide in question, based on data from Sune Nightingale's last year's hourly temperature figures, contrasts the running costs and efficiency of a high-temperature heat pump system — operating without system upgrades on weather compensation from 45 to 70 degrees Celsius — against a well-designed system operating between 25 and 45 degrees Celsius.
A closer examination reveals that the Seasonal Coefficient of Performance (SCOP) for the high-temperature operation stands at a lower 2.47, as opposed to 4.71 for the low-temperature operation. The Coefficient of Performance (COP) directly correlates with the heat pump's efficiency: the higher the COP, the more efficient the system. Thus, the data unequivocally points to the superior efficiency of the low-temperature heat pump.
This efficiency translates into significant cost savings. According to the slide, the annual running cost for the high-temperature heat pump is £3,410, whereas it drops to £1,840 for the low-temperature system, marking a 35% reduction in costs. This is not just a matter of improved efficiency but also reflects on the substantial economic benefits of a system designed for lower operating temperatures.
The slide also hints at the importance of system design. It suggests that incorporating elements like buffer tanks or system separation, which are often part of high-temperature heat pump systems, could further degrade performance.
The revelation presented in the slide is striking. As manufacturers launch high-temperature heat pumps with considerable marketing efforts, the data cautions potential buyers and industry professionals. It implies that, without a meticulous approach to the system design and consideration of operating temperature ranges, high-temperature heat pumps may not be the optimal choice either economically or environmentally.
The evidence, to my mind, is clear: high-temperature heat pumps, despite their popularity and aggressive marketing, may not always be the best path forward. As the industry strives for greener solutions, the focus must shift towards optimising system design and operational parameters to ensure that heat pumps deliver on their promise of efficiency and cost-effectiveness. This slide serves as a stark reminder that, in the realm of sustainable heating, more heat does not necessarily equate to better performance.
What we really need is the levies moving off electricity and onto gas…
I would be interested to know what you feel is high-temperature too, Brendon.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I agree with both of you in different ways.
To me, HT heat pumps are a somewhat quick-n-dirty fix to allow a HP to replace a boiler (ish), with minimal re-working of the house side. They will self-evidently be less efficient than a LT heat pump + good system design, therefore they will cost more units of electricity to run.
If the tariffs stay as they are, the HT "quick fix" approach will cost more than gas to run. with tariffs as they are, only an LT pump + good system design + engineering saves money over gas. (PV + storage batteries can help too but leaving that aside for the moment)
So no-one with more sense than money would be putting in a HT system and planning to run it at HT forever.
But is the argument below also valid?
If the tariffs were reduced so that the run cost of the HT pump is less than gas, then the pure HT approach becomes viable economically for the "typical end customer". Due to not re-engineering the house side, they could perhaps be fitted more quickly with less disruption, and by less expert people , and thus get more done per year. Therefore on the large scale, moving the country faster towards where we want to be. which is what matters.
later on , whenever there's a feasible opportunity in terms of the house's use and users, they can of course refit to run at LT and save some more run cost - if they want to.
questions:
with lots of HT systems, what then happens to the electricity generation and distribution side ? do all these inefficient HT systems blow the grid? do we burn more gas to generate the electricity to run the HT systems than we would have done by just burning the gas in the house?
Do HT systems cope better with low flow rates and high DT that would be expected in a system that's running currently with a boiler? as that'd be a necessary condition for a "minimal remove and replace" approach. or are they the same as LT?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @heacolThe evidence, to my mind, is clear: high-temperature heat pumps, despite their popularity and aggressive marketing, may not always be the best path forward. As the industry strives for greener solutions, the focus must shift towards optimising system design and operational parameters to ensure that heat pumps deliver on their promise of efficiency and cost-effectiveness. This slide serves as a stark reminder that, in the realm of sustainable heating, more heat does not necessarily equate to better performance.
Er is that true, or is it only the case that any heat pumps when run at high temperature results in lower efficiency (which is of course the case)? Two different questions. There are reasons for 'high temperature' heat pumps other than their ability to run at high temperature.
Posted by: @heacolThe slide also hints at the importance of system design. It suggests that incorporating elements like buffer tanks or system separation, which are often part of high-temperature heat pump systems, could further degrade performance.
I think, sadly, you can cross out 'high temperature' in this sentence!
The original text looks like a piece of marketing blurb by a company that doesnt yet have an R290 heat pump, or alternatively by someone paid to rubbish heat pumps (there is plenty of that going on). Several manufacturers seem to be combining a transition to R290 with better sound performance and aesthetics, but then marketing the result as a 'high temperature heat pump'. I guess that, a manufacturer that has chosen not to take this route may wish to confuse matters with imprecise information.
Of course it is true that the focus must shift towards optimising system design and operational parameters to ensure that heat pumps deliver on their promise of efficiency and cost-effectiveness, whilst at the same time being mindful of practicalities particularly in a retrofit situation. So I very much agree with you on that point, but this isn't linked to high temperature.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @iancalderbankTo me, HT heat pumps are a somewhat quick-n-dirty fix to allow a HP to replace a boiler (ish), with minimal re-working of the house side. They will self-evidently be less efficient than a LT heat pump + good system design, therefore they will cost more units of electricity to run.
...
But is the argument below also valid?
If the tariffs were reduced so that the run cost of the HT pump is less than gas, then the pure HT approach becomes viable economically for the "typical end customer". Due to not re-engineering the house side, they could perhaps be fitted more quickly with less disruption, and by less expert people , and thus get more done per year. Therefore on the large scale, moving the country faster towards where we want to be. which is what matters.
later on , whenever there's a feasible opportunity in terms of the house's use and users, they can of course refit to run at LT and save some more run cost - if they want to.
Exactly that. There is clearly an argument, in some, perhaps many retrofit situations with radiators, for running at say 55C ((which I guess is on the cusp). It depends on the specific house and the specific priorities. There is also an argument for running the DHW cycle at (say) 65C, which is exactly what Vaillant do with their R290 pumps - no use of the immersion even for legionella. A rebalancing of the tariffs makes heat pumps more accessible which hastens the change to low carbon heating which is necessary. So I dont think it should be ruled out.
I think its telling that the new building regs specify max design flow temp (even for gas) =55C. Somebody, somewhere, has worked out that this might be a sweet spot balancing capital cost of retrofitting a heat pump with running cost, particularly as the latter rebalances between gas and electricity.
Im certainly not going to advocate running a heat pump at 65C for space heating, but 55C for space heating and 65 for DHW isn't silly. Lower running cost (larger emitters) can then be offered as an optional upgrade.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
You only need a cop of 2.5 to make better use of the gas by burning it in a ccgt and using the electricity to run a heat pump, than piping and burning the gas at point of use.
Something to consider…
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@JamesPa, I wrote the original text and did the original analysis to show that high temperature heat pumps are not the panacea they are portrayed to be by the industry. I have no vested interests other than trying to make sure people are not hoodwinked in to fuel poverty. They are like supercars, they can go way above the speed limit, but there may be serious consequences not mentioned by the industry. The article was warning about the consequences and to show that they are quite competent low temperature machines in the right hands.
I think that you will find the 55C for gas boilers is to ensure condensing takes place, and if the gas boiler is to be replaced at some time in the future with a heat pump, then to avoid further system changes then the system needs to be able to operate at no higher than 55C whatever the heat source.
I have direct experience of this. When a high temp pump was put in to replace a low temp one in my rented accommodation running costs significantly increased no matter what was tweaked on it. It was a nightmare. There was no reason to replace it with the high temp one as the property was designed for a heatpump (except for the microbore).
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 932 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 24 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago