Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Replacing knackered oil boiler with Samsung ASHP - Perthshire
Interested in red flags, guidance on replacing 26Kw oil-boiler with in-boiler 127l HW tank, with ASHP, 300l tank.
Timber frame with block exterior, 275sq.m, bilt 1999, UFH both floors with room stats in all but 3 bathrooms which are always open. Original heat loss as designed was ca. 18kW. two log burners, one in front hall one in large living room upstairs. Oil aga for cooking always on.
Two suppliers quoted: one calculated heat loss at 13.3kW, the other at 18.94kW so ASHP at 16kw and 2x19kW.
Both quote for buffer tank.
I think I would be tempted to do my own heat loss assessment. Using heatpunk
or you could try this simple one https://openenergymonitor.org/tools/SimpleHeatLoss.html
There is a substantial difference between the two you have. Also i would look at possible easy insulation upgrades to reduce it.
Also I would ask the installers to justify why they think a buffer is necessary. Much better not to have one if possible as it will lower your efficiency.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @dowallydrifter@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
You will not need a buffer if the system is correctly installed. I will connect you with two excellent installers shortly that cover your area so you can get comparative pricing.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Posted by: @bontwoody@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
Totally agree and I would be suspicious of the high loss estimates. Even if you did use the wood burners and know how much wood you burned you could add that in. I am sceptical about even 13kW unless it's poorly insulated. Any sanity check you could do would be a good idea
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@bontwoody Thanks. Oil figures available but can't isolate aga from the dead boiler usage unfortunately.
@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Posted by: @dowallydrifterNot trivial to add wall insulation to timber frame
It is pointless adding EWI to a timber framed house with external block rainscreen. The movement of air around the timber frame inside of the block outer makes adding EWI irrelevant.
Also in Perthshire with leaky timber frame in an exposed site.
results from the simple calculator point toward 16.5kW heat pump plugging in U values from original docs. walls 0.45, roof 0.24, windows 3.5 - the simple calc will be ignoring the large lounge with vaulted ceiling i guess.
Posted by: @dowallydrifter@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Ive done some rough calculations on those figures after trying to add in the wood and Ive come up with a demand of about 19.5kW at -3C to achieve 21C internal temperature (using the 4000 liter figure), so if James concurs then the original estimate isn't far out. (Although this drops to 13kW using the 2500 liter figure)
We like our living room warm (22.5C) so the way I have approached insulation is to concentrate on that room. Insulated plasterboard has worked very well on both the walls and inaccessible loft areas.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 27 Forums
- 2,767 Topics
- 65.2 K Posts
- 1,911 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
My first reaction is that these are prima facie much of...
By JamesPa , 23 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist Yes but those predictions were based ...
By Papahuhu , 55 minutes ago
-
RE: Is it the house or the equipment?
Thanks for that @rob-of-york. The two way split I descr...
By springswood , 1 hour ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
If it's a separate contract then it would not be zero r...
By JamesPa , 3 hours ago
-
RE: Siting of the external sensor on a heatpump
Of course had the heat source been a heat pump it would...
By JamesPa , 14 hours ago
-
Never assume, it makes an ass of u and me! OK, tha...
By JamesPa , 14 hours ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
In fairness all heating has cost a lot to run in recent...
By JamesPa , 16 hours ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 2 days ago
-
No, but the heat pump must be capable of delivering a S...
By JamesPa , 2 days ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 3 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 3 days ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 3 days ago
-
RE: Adventures in heat loss calculations
I have seen it stated that the declared calorific value...
By JamesPa , 3 days ago
-
RE: Two heating zones to one zone
@transparent Many thanks. The garage is fairly well ...
By Profzarkov , 4 days ago