Replacing knackered oil boiler with Samsung ASHP - Perthshire
Interested in red flags, guidance on replacing 26Kw oil-boiler with in-boiler 127l HW tank, with ASHP, 300l tank.
Timber frame with block exterior, 275sq.m, bilt 1999, UFH both floors with room stats in all but 3 bathrooms which are always open. Original heat loss as designed was ca. 18kW. two log burners, one in front hall one in large living room upstairs. Oil aga for cooking always on.
Two suppliers quoted: one calculated heat loss at 13.3kW, the other at 18.94kW so ASHP at 16kw and 2x19kW.
Both quote for buffer tank.
I think I would be tempted to do my own heat loss assessment. Using heatpunk
or you could try this simple one https://openenergymonitor.org/tools/SimpleHeatLoss.html
There is a substantial difference between the two you have. Also i would look at possible easy insulation upgrades to reduce it.
Also I would ask the installers to justify why they think a buffer is necessary. Much better not to have one if possible as it will lower your efficiency.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @dowallydrifter@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
You will not need a buffer if the system is correctly installed. I will connect you with two excellent installers shortly that cover your area so you can get comparative pricing.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @bontwoody@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
Totally agree and I would be suspicious of the high loss estimates. Even if you did use the wood burners and know how much wood you burned you could add that in. I am sceptical about even 13kW unless it's poorly insulated. Any sanity check you could do would be a good idea
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@bontwoody Thanks. Oil figures available but can't isolate aga from the dead boiler usage unfortunately.
@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Posted by: @dowallydrifterNot trivial to add wall insulation to timber frame
It is pointless adding EWI to a timber framed house with external block rainscreen. The movement of air around the timber frame inside of the block outer makes adding EWI irrelevant.
Also in Perthshire with leaky timber frame in an exposed site.
results from the simple calculator point toward 16.5kW heat pump plugging in U values from original docs. walls 0.45, roof 0.24, windows 3.5 - the simple calc will be ignoring the large lounge with vaulted ceiling i guess.
Posted by: @dowallydrifter@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Ive done some rough calculations on those figures after trying to add in the wood and Ive come up with a demand of about 19.5kW at -3C to achieve 21C internal temperature (using the 4000 liter figure), so if James concurs then the original estimate isn't far out. (Although this drops to 13kW using the 2500 liter figure)
We like our living room warm (22.5C) so the way I have approached insulation is to concentrate on that room. Insulated plasterboard has worked very well on both the walls and inaccessible loft areas.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,271 Topics
- 50.8 K Posts
- 141 Online
- 5,933 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: My DIY Heat Pump installation
@temperature_gradient Building regs I had my initial...
By Polar bear , 3 hours ago
-
This is a plot from a Shelly EM monitoring the supply t...
By Ubert767 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Hi again all, Just to update on this... I've now ad...
By benson , 6 hours ago
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
thanks, heatpunk looks great, being able to do the calc...
By giryan , 6 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Why arent you expecting them to make much difference. ...
By JamesPa , 7 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating I wonder if you are being a bit pessimi...
By GrahamF , 7 hours ago
-
@toodles sounds good. I started with cosy but then plug...
By Eliuccio , 7 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 9 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
He showed me a photo of 5-10l/min. However a...
By Crimson , 10 hours ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 11 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 11 hours ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 16 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 18 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 19 hours ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 1 day ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I have just looked at my heat pump 'long interval' (27 ...
By cathodeRay , 2 days ago