Replacing knackered oil boiler with Samsung ASHP - Perthshire
Interested in red flags, guidance on replacing 26Kw oil-boiler with in-boiler 127l HW tank, with ASHP, 300l tank.
Timber frame with block exterior, 275sq.m, bilt 1999, UFH both floors with room stats in all but 3 bathrooms which are always open. Original heat loss as designed was ca. 18kW. two log burners, one in front hall one in large living room upstairs. Oil aga for cooking always on.
Two suppliers quoted: one calculated heat loss at 13.3kW, the other at 18.94kW so ASHP at 16kw and 2x19kW.
Both quote for buffer tank.
I think I would be tempted to do my own heat loss assessment. Using heatpunk
or you could try this simple one https://openenergymonitor.org/tools/SimpleHeatLoss.html
There is a substantial difference between the two you have. Also i would look at possible easy insulation upgrades to reduce it.
Also I would ask the installers to justify why they think a buffer is necessary. Much better not to have one if possible as it will lower your efficiency.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @dowallydrifter@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
You will not need a buffer if the system is correctly installed. I will connect you with two excellent installers shortly that cover your area so you can get comparative pricing.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @bontwoody@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
Totally agree and I would be suspicious of the high loss estimates. Even if you did use the wood burners and know how much wood you burned you could add that in. I am sceptical about even 13kW unless it's poorly insulated. Any sanity check you could do would be a good idea
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@bontwoody Thanks. Oil figures available but can't isolate aga from the dead boiler usage unfortunately.
@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Posted by: @dowallydrifterNot trivial to add wall insulation to timber frame
It is pointless adding EWI to a timber framed house with external block rainscreen. The movement of air around the timber frame inside of the block outer makes adding EWI irrelevant.
Also in Perthshire with leaky timber frame in an exposed site.
results from the simple calculator point toward 16.5kW heat pump plugging in U values from original docs. walls 0.45, roof 0.24, windows 3.5 - the simple calc will be ignoring the large lounge with vaulted ceiling i guess.
Posted by: @dowallydrifter@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Ive done some rough calculations on those figures after trying to add in the wood and Ive come up with a demand of about 19.5kW at -3C to achieve 21C internal temperature (using the 4000 liter figure), so if James concurs then the original estimate isn't far out. (Although this drops to 13kW using the 2500 liter figure)
We like our living room warm (22.5C) so the way I have approached insulation is to concentrate on that room. Insulated plasterboard has worked very well on both the walls and inaccessible loft areas.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 187 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
JamesPa This yesterdays run. In manual mode, so I tu...
By trebor12345 , 3 minutes ago
-
RE: Electricity price predictions
Well let's start by telling you that since I wrote that...
By Transparent , 4 minutes ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
The initial Aira appointment, certainly in my case when...
By Sheriff Fatman , 51 minutes ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 2 hours ago
-
This is what I answered, I really have no hope: "......
By Batpred , 16 hours ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj oh yes they offer Daikin 8kW, they tried to fo...
By AgentGeorge , 17 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Good point! Just in case anyone re...
By Batpred , 18 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 It would be very useful if you could tell us...
By trebor12345 , 18 hours ago
-
RE: Benefits of an extra horizontal loop for GSHP
A correct sized collector is all you need. Saying this,...
By greenlight , 20 hours ago
-
RE: Grant Aerona Short Cycling
@mikefl, thanks for sharing your operating data, very i...
By Steam Powered , 21 hours ago
-
-
@f1p, sorted, on a android phone Just swaped from ...
By @sand , 1 day ago
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@editor Yes BUT that was 3 years ago installed in Janua...
By rob heatpump bob , 2 days ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 2 days ago
-
RE: Home energy storage & battery register
2 days uninterruptible power supply (at the moment) wit...
By Batpred , 2 days ago
-
We have a Vaillant aerotherm with sensocomfort. We have...
By Newbie , 2 days ago
-
@trebor12345 Yes, expect defrost cycles to initiate at ...
By IaAck , 2 days ago
-
I would probably have them in white as that would match...
By Grantmethestrength , 2 days ago