Replacing knackered oil boiler with ASHP - Perthshire
Interested in red flags, guidance on replacing 26Kw oil-boiler with in-boiler 127l HW tank, with ASHP, 300l tank.
Timber frame with block exterior, 275sq.m, bilt 1999, UFH both floors with room stats in all but 3 bathrooms which are always open. Original heat loss as designed was ca. 18kW. two log burners, one in front hall one in large living room upstairs. Oil aga for cooking always on.
Two suppliers quoted: one calculated heat loss at 13.3kW, the other at 18.94kW so ASHP at 16kw and 2x19kW.
Both quote for buffer tank.
I think I would be tempted to do my own heat loss assessment. Using heatpunk
or you could try this simple one https://openenergymonitor.org/tools/SimpleHeatLoss.html
There is a substantial difference between the two you have. Also i would look at possible easy insulation upgrades to reduce it.
Also I would ask the installers to justify why they think a buffer is necessary. Much better not to have one if possible as it will lower your efficiency.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @dowallydrifter@bontwoody Thanks - will have a go at the calcs as I've the data that they used. I've asked about buffer today and waiting on a reply.
You will not need a buffer if the system is correctly installed. I will connect you with two excellent installers shortly that cover your area so you can get comparative pricing.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @bontwoody@dowallydrifter if you had oil usage figures and didn’t use the wood burners much you could use that as well to get a sanity check.
Totally agree and I would be suspicious of the high loss estimates. Even if you did use the wood burners and know how much wood you burned you could add that in. I am sceptical about even 13kW unless it's poorly insulated. Any sanity check you could do would be a good idea
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@bontwoody Thanks. Oil figures available but can't isolate aga from the dead boiler usage unfortunately.
@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Posted by: @dowallydrifterNot trivial to add wall insulation to timber frame
It is pointless adding EWI to a timber framed house with external block rainscreen. The movement of air around the timber frame inside of the block outer makes adding EWI irrelevant.
Also in Perthshire with leaky timber frame in an exposed site.
results from the simple calculator point toward 16.5kW heat pump plugging in U values from original docs. walls 0.45, roof 0.24, windows 3.5 - the simple calc will be ignoring the large lounge with vaulted ceiling i guess.
Posted by: @dowallydrifter@jamespa oil varies 2500-4000 litres a year for boiler and aga, ca. 4 cu.m wood p.a. Original design for UFH showed outside walls with K=0.45 W/sq.m/K roof K=0.24 W/sq.m/K, and windows at 3.5 W/sq.m/K . Independent engineer in 1999 when built reckoned 18Kw at -5degC. Not trivial to add wall insulation to timber frame. Loft insulation doable to some (bats permitting!) more constrained access in rest of roof.
Ive done some rough calculations on those figures after trying to add in the wood and Ive come up with a demand of about 19.5kW at -3C to achieve 21C internal temperature (using the 4000 liter figure), so if James concurs then the original estimate isn't far out. (Although this drops to 13kW using the 2500 liter figure)
We like our living room warm (22.5C) so the way I have approached insulation is to concentrate on that room. Insulated plasterboard has worked very well on both the walls and inaccessible loft areas.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 22 Forums
- 2,070 Topics
- 45.3 K Posts
- 17 Online
- 3,343 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
Fair enough. With R290 heat pumps, which seems to be...
By JamesPa , 1 hour ago
-
RE: Heat pump installation and BUS Grant timings
EPC no longer necessary Here is the link to the part...
By JamesPa , 4 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@benson Ours is ‘resting’ for the summer now (unless we...
By Toodles , 5 hours ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 7 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent ‘Protein’s extra Luv’.
By Toodles , 14 hours ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 1 day ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@johnmo You are correct, standard Ethylene glycol used ...
By Brendon Uys , 1 day ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 2 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 2 days ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 2 days ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 2 days ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist @profzarkov thanks to you both for the v...
By Grahamh-uk , 2 days ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 3 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 4 days ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 4 days ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 4 days ago