Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Pipe Work Question?
I'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I think the 22mm plastic pipe might be a bit small for 8kw. 22mm copper is considered ok for 5kW I think. This link gives more detail. https://www.heatgeek.com/does-my-pipework-need-upgrading-for-a-heat-pump-with-cheat-sheet/
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The issue with the 22mm plastic piping in your loft could potentially impact the efficiency of your heat pump system, especially if it differs from the rest of your installation in terms of diameter. We have this issue where the previous owners “narrowed” the pipework when they extended the heating to the north end of the house, creating a bottleneck which I think is the major issue that the rads at the far end of the house struggle.
Did your installers run all the pipework for your system - copper and the 3.5m run in the loft?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Yes so the pipe work from the HP that runs externally to the loft is copper, then the pipe work runs length of loft to the other end where the DHW tank is, that section inside the loft is plastic. I need to measure accurately to check diameters, but im fairly certain that it’s the same as the copper pipes.
Thinking about it now, all l the pipe work externally from the HP is insulated, I’ve assumed it copper, but don’t know for sure, I might have to check that.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
There is a good video explaining the pipe sizing issue here
https://renewableheatinghub.co.uk/forums/postid/29119
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @ecobakerI'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
That's too tight IMO, we would use 28mm copper, or 32mm MLCP
- 26 Forums
- 2,610 Topics
- 60.8 K Posts
- 233 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
@jamespa and @colinc to my understanding, the way a plu...
By Mars , 18 minutes ago
-
@cathoderay I turned the room stat down to 12 degrees e...
By Painter26 , 42 minutes ago
-
RE: Electricity price predictions
@jamespa I definitely made full use of the Cosy tariff ...
By ChandyKris , 3 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@judith unfortunately, I completely missed your reply u...
By LeJamaisContent , 4 hours ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
That may well be correct. However we don't have enoug...
By Transparent , 8 hours ago
-
RE: Rate the quality of your heat pump design and installation
@editor Thank you. I joined because I really liked your...
By claireisamazing , 1 day ago
-
I cant, but @editor probably can if you tell him roughl...
By JamesPa , 1 day ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
@madsid I don't quite understand what extra you need...
By Bash , 1 day ago
-
@transparent thank you. Be Thursday before my mate giv...
By David999 , 1 day ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
@johnd our Peak system is no more. The installer cam...
By DaveC , 1 day ago
-
Hah! Well I guess we're all in the realm of conjectu...
By Transparent , 1 day ago
-
These are a bit hard to read but the information is in ...
By bobflux , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Ah, not so useful then For sure, hopefully before ...
By JamesPa , 2 days ago
-
Thanks @editor I appreciate that things go wrong, bu...
By venkman , 2 days ago
-
RE: Home energy storage & battery register
AC coupled Pure Drive 10kW battery Solar PV Solis P...
By Little Lights , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: ispookie666 Manufacturer: Vaillant Mo...
By ispookie666 , 2 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I'm fairly new to the forum and have not voted. Back...
By ispookie666 , 2 days ago
-
I am seeing an increasing number of occasions when my G...
By DavidAlgarve , 2 days ago
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
@editor Thanks Mars. I look forward to the subsequent ...
By DavidB , 3 days ago
-
RE: Anyone concerned about GivEnergy?
Fair enough. Its interesting that opentherm (for boil...
By JamesPa , 3 days ago
-
RE: Brand and installer questions for ASHP
A tank solely in the return (upstream of where the retu...
By JamesPa , 3 days ago
-
RE: Home automation and the cloud; is there a better way?
+1 It's not just cloud though. Many devices have repla...
By bobflux , 3 days ago
-
RE: Summer usage. Why is my Vaillant Aerotherm using so much energy on "heating"?
So the red bars are 'DHW' and the yellow bars 'heating'...
By JamesPa , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 4 days ago