Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Pipe Work Question?
I'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I think the 22mm plastic pipe might be a bit small for 8kw. 22mm copper is considered ok for 5kW I think. This link gives more detail. https://www.heatgeek.com/does-my-pipework-need-upgrading-for-a-heat-pump-with-cheat-sheet/
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The issue with the 22mm plastic piping in your loft could potentially impact the efficiency of your heat pump system, especially if it differs from the rest of your installation in terms of diameter. We have this issue where the previous owners “narrowed” the pipework when they extended the heating to the north end of the house, creating a bottleneck which I think is the major issue that the rads at the far end of the house struggle.
Did your installers run all the pipework for your system - copper and the 3.5m run in the loft?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor Yes so the pipe work from the HP that runs externally to the loft is copper, then the pipe work runs length of loft to the other end where the DHW tank is, that section inside the loft is plastic. I need to measure accurately to check diameters, but im fairly certain that it’s the same as the copper pipes.
Thinking about it now, all l the pipe work externally from the HP is insulated, I’ve assumed it copper, but don’t know for sure, I might have to check that.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
There is a good video explaining the pipe sizing issue here
https://renewableheatinghub.co.uk/forums/postid/29119
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @ecobakerI'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
That's too tight IMO, we would use 28mm copper, or 32mm MLCP
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 1,862 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
@cathoderay I started to record oil usage per month on ...
By ian33a , 1 hour ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 5 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 10 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 1 day ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago