Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Pipe Work Question?
I'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I think the 22mm plastic pipe might be a bit small for 8kw. 22mm copper is considered ok for 5kW I think. This link gives more detail. https://www.heatgeek.com/does-my-pipework-need-upgrading-for-a-heat-pump-with-cheat-sheet/
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The issue with the 22mm plastic piping in your loft could potentially impact the efficiency of your heat pump system, especially if it differs from the rest of your installation in terms of diameter. We have this issue where the previous owners “narrowed” the pipework when they extended the heating to the north end of the house, creating a bottleneck which I think is the major issue that the rads at the far end of the house struggle.
Did your installers run all the pipework for your system - copper and the 3.5m run in the loft?
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
@editor Yes so the pipe work from the HP that runs externally to the loft is copper, then the pipe work runs length of loft to the other end where the DHW tank is, that section inside the loft is plastic. I need to measure accurately to check diameters, but im fairly certain that it’s the same as the copper pipes.
Thinking about it now, all l the pipe work externally from the HP is insulated, I’ve assumed it copper, but don’t know for sure, I might have to check that.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
There is a good video explaining the pipe sizing issue here
https://renewableheatinghub.co.uk/forums/postid/29119
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
10kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @ecobakerI'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
That's too tight IMO, we would use 28mm copper, or 32mm MLCP
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 612 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 2 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 16 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago