Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
My Grid import for last week:
1 Jan 41.5kwh
2 Jan 25.21kwh
3 Jan 30.1kwh
4 Jan 37.1kwh
5 Jan 39.55kwh
6 Jan 44.2kwh
we wfh so in all day.
Grid import:
2022: 10158 not using weather comp/AI
2023: 8225 using wc/AI
Also note:
we used a hot tub quite a lot in 2022 but used less in 2023. Impacted grid import and solar export.
we have an elec car since June 2023 so actual comparative for 2023 will be under 8000
Its complex making exact comparisons even though i try and keep a spreadsheet. so many variables! e.g. We sometimes import from grid to fill batteries and sell back to Octopus for profit in Saving Sessions and also in 2022 when prices were all over the place.
hot tub usage
e/v
Overall I'm absolutely certain our usage is reduced by WC/AI
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
with regard to tariffs etc.... I do not have any Home Automation and have not looked into it a lot. Can the LG be integrated easily?
My tariffs are:
Import: Octopus Tracker (daily tracker not Agile)
Export: Octopus Fixed (15p)
I use Tracker for a number of reasons:
1. My inverter is only 2.6kw so I can't fill batteries very fast during cheap periods and can't draw from batteries very fast. So i need to use grid at all times.
2. With maximising WC/AI I prefer to keep constant running and not be having to control for tariff reasons
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
On solar...
I have 2 systems:
Original 7 panels 2kw. Pitched roof - south facing
on FIT but now transferred to actual export payment instead of assumed. Produces circa 1500kw pa
New system: 20 panels 6kw. 6deg/flat roof - east facing. Good sun until mid afternoon
Produces circa 5000kw pa
New system includes 3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
newer kit has advantage of ability to import/export at higher rates than mine
recommend looking at utilising emergency power supply - preferably with a gateway such as Tesla, Solaredge or Givenergy All in one so that it auto changes over.
Many installers don't bother to point you at EPS options!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@derek-m If you navigate to the UK LG Therma V heat pump owners group on facebook you will find a complete setup doc for AI I pulled together after my own struggles to get this right. Look in files section V2.
Posted by: @ians@derek-m If you navigate to the UK LG Therma V heat pump owners group on facebook you will find a complete setup doc for AI I pulled together after my own struggles to get this right. Look in files section V2.
Hi Ian,
Thanks for the link but I am not a facebook user, have never been and doubt that I ever will be. Just a friendly old dinosaur. 😋
Excellent document in the Facebook user group. Step by step guide on AI setup
https://www.facebook.com/share/g/HTnrvUAd5v6MwUV7/
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
I would like to reinstate this thread please as Im going to try and sort out a friends LG heat pump. Could you just check what I think I have gleaned so far.
I can get into the SETTINGS menu by using the ver number as the password.
Select Temperature sensor: I can select 'Air+Water' if the thermostat is in a sensible position otherwise just 'Water'
Air Heating Set Temperature: ? Not sure what these do
Water heating Set Temperature ? Not sure what these do
LWT Temperature for Auto Mode: WC curve temperatures
Outdoor Temperature for Auto mode: WC OAT temperatures
After finished in SETTINGS, go back, then into the FUNCTION menu and set
Water Temperature Setting- Heating Temperature Setting to AUTO
Then go back to main screen and set heating to AUTO.
Their house should be idea for a heat pump as its got a big slab and UFH but its costing them a fortune to run at the moment. Just want to be sure I have it all sorted in my head before going over.
Thanks in advance
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Good luck.. take it slowly. Ideally print the doc above and write down all changes so you can revert or seek guidance.
The Facebook group has helpful installers & service engineers - so recommend joining if you can.
After making main changes the tweaks may need to be done if house too hot or too cold.
I now use 5800kWh on AI (weather compensation) vs 8200kWh on fixed flow. Huge savings
Also check tariff. Depends on usage as well as if solar panels, batteries, EV etc. In 2025 i imported 14500kWh at 8p kWh and exported 7500kWh at 15p. Net cost near zero!
Posted by: @bontwoodyI would like to reinstate this thread please as Im going to try and sort out a friends LG heat pump. Could you just check what I think I have gleaned so far.
I can get into the SETTINGS menu by using the ver number as the password. 👍
Select Temperature sensor: I can select 'Air+Water' if the thermostat is in a sensible position otherwise just 'Water. 👍
Air Heating Set Temperature: ? Not sure what these do
16/25
Only works if using controller as your thermostat. Home shouldn’t go below 16 or above 25c.
Water heating Set Temperature ? Not sure what these do
20/55
Water heating will run between 20c and 55c when it needs to resolve it’s curve/heat (e.g. the heat you want)
I use 29/48
LWT Temperature for Auto Mode: WC curve temperatures 👍
Doc suggests 30/50.
Outdoor Temperature for Auto mode: WC OAT temperatures 👍
Doc suggests 3/15 . If possible tweak lower if house warm enough. E.g-2i use -4/15
After finished in SETTINGS, go back, then into the FUNCTION menu and set 👍
Water Temperature Setting- Heating Temperature Setting to AUTO 👍
Then go back to main screen and set heating to AUTO. 👍
Their house should be idea for a heat pump as its got a big slab and UFH but its costing them a fortune to run at the moment. Just want to be sure I have it all sorted in my head before going over.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 Thanks Tim, I think its been set to a constant flow temperature of 54C looking at a photo, so it should make a massive difference to their bills 🙂
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
On the main controller you can easily press
+ or - up to 5 deg
This allows temporary changes to test for a few days
- or if weather colder/hotter than normal
- temp tweak if solar gain or holidays
Etc
- without changing the main settings
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@bontwoody yes, that is shocking!!
Depending where you are hopefully it will run at under 40deg much of the time. Right now its 8deg outside here... LWT is at 38deg.... and house a comfortable 21deg.
Saving elec as well as better efficiency. I would not be surprised if savings 25 to 30%
Fyi I'm now on Octopus Intelligent Go tariff as I also have batteries and EV. import price for 2025 averaged under 10p kWh
I guess they can currently feel the heat in the floor. With AI and lower temps the floor may hardly feel warm! But should keep a very comfortable room temp all the same.
Let us know how it goes!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 495 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 2 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 2 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 3 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 4 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 4 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 5 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 7 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 8 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 10 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 12 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 16 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 2 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago