Replacing oil with ...
Replacing oil with a heat pump in a 400-year-old stone farmhouse – sanity check before committing
2 Users
0 Reactions
(@westend)
Considering a heat pump
New Member Member
Your energy: 19 kWh
Topic starter   [#3252]
Hi all,
We're close to committing to replacing oil with an air source heat pump and would really value some independent opinions. It's our forever home, so we want to get it right first time.
The house
  • Detached 17th-century stone farmhouse near Bath
  • 269m² across two floors
  • Solid stone walls averaging approximately 600mm, with no wall insulation
  • Uninsulated solid floors
  • 100mm loft insulation
  • Metal-frame double glazing
  • Fairly exposed rural location
  • Single-phase electricity in the house (three-phase available at the farm, but a faff to bring over)
Current situation
  • Approximately 4,000–4,500 litres of oil annually
  • Very old non-condensing oil boiler on its last legs
  • House is only ever semi-warm despite the amount of oil we consume
  • Typically heating for a couple of hours in the morning and five hours in the evening
  • Existing radiators meet just 17–65% of individual room demand at proposed heat pump temperatures
  • Hot water cylinder needs replacing anyway
  • Oil-fired Stanley range in the kitchen, staying for now
Our main motivation is comfort. We'd love to have a consistently warm house rather than constantly playing catch-up with the heating.
We've had what felt like a thorough survey from Sustain Heating & Renewables.
  • Approximately £19,000 after the £9,000 grant
  • 2 × Clivet Edge EVO 2.0 Mono 8.1 in cascade
  • Quoted combined output of 25.8kW at −7°C / 50°C flow
  • Calculated heat loss of 22.4kW at −7°C
  • 18 replacement radiators (Type 22/33)
  • 300L hot water cylinder
  • 90L buffer
  • Weather compensation
  • Estimated annual electricity consumption of 12,500–15,800kWh
We'd ideally like living spaces at 21–22°C and bedrooms at 18–20°C.
One potentially significant issue is that the heat loss survey assumed 305mm stone walls, whereas subsequent measurements suggest they're closer to 600mm.
A few questions:
  1. Does this seem like a well-designed system for a property of this nature?
  2. How significantly might the incorrect wall thickness affect the heat loss calculation? Could we end up with an oversized system?
  3. Does a cascade make sense, particularly regarding minimum modulation and efficiency in milder weather?
  4. Would it be worth pushing for a 45°C design flow temperature rather than 50°C?
  5. Is the 90L buffer appropriate for this installation?
  6. Does the estimated annual electricity consumption seem realistic?
  7. Does anyone have experience with Clivet heat pumps or Sustain Heating & Renewables?
Most importantly, I'd love to hear from anyone who has made a similar transition from oil in a large, old, relatively uninsulated stone house.
  • Is your house genuinely warmer?
  • How does it cope during prolonged cold spells?
  • What are your annual running costs?
  • Would you make the same decision again?
At current oil prices, the financial case looks fairly compelling, but at more historically normal oil prices, it's less clear-cut. We would probably need to replace the oil boiler and cylinder within the next few years regardless.
I'm not necessarily looking for reassurance. I'd much rather someone pick holes in the proposal now than discover problems after spending £19,000.
Happy to share the heat loss report and radiator schedule.
Thanks in advance!
This topic was modified 2 hours ago by Mars
Your energy: 43 kWh
@westend — welcome to the forum. You are in the right place here!
My initial thoughts:
Calculated heat loss of 22.4kW at −7°C:
(1) this seems very high, even allowing for your property type and size. Don't forget that calculated heat losses are what I call whatiffery - what if this, what if that? The two things to watch out for are exaggerated solid stone wall U values and exaggerated air changes per hour.
(2) at -7° near Bath??? What happened to the famous hot water springs?
(3) loft insulation needs increasing unless physically impossible.
If you can post the detail on your heat loss calculations we can have a look in greater detail.
The other thing to try is a sanity check based on your oil usage, but this is far from easy given the way we buy and consume oil for central heating. The kitchen range use will also complicate things. But worth a try nonetheless.