New Build - Grant Aerona3 10kW - Questions and observations
@ggw I think you've nailed the issue. Very odd.
I think you may have a faulty outdoor temperature sensor probe, if the unit is under warranty this will be covered by Grant. You've enough evidence based on your own monitoring to ask them to come out and replace it. Fault when running only may be vibration caused, so it might be OK when the unit is not running, but goes doo-lally when it is. Just because it's not open circuit doesn't mean it's not faulty, a poor connection onto the PCB or in the thermistor unit itself could mean vibration causes incorrect readings.
I have the exact same 10kW Aerona and the outdoor air sensor is pretty accurate. It can be slightly affected by heat from the coil when it defrosts during which time the fan stops for a while, other than that it's been within 1degC or so of where it should be. As the outdoor temperature goes above 17degC the unit starts to cycle on and off for long periods, as the heat load for a typical 21degC set point falls below the unit minimum unit turn down of about 25%. Above 20degC outdoor air temperature heating is disabled regardless of the indoor thermostat setting or demand.
In addition to the suggestions by AllyFish, another reason could be electrical pickup from a nearby power cable, that is only live when the heat pump is running. Whenever possible, all cables should be kept separated from each other, and in particular that would apply to power and signal cables.
Do you know what flow in l/m your unit is showing? @allyfish
How do i check this? is it a parameter on controller? i've not seen it in manual. Tho, with the bewildering amount of parameters, that wouldn't be a surprise.
Posted by: @ggw
Both Good shouts - ill make sure to tell Grant that if they ever commit to coming to look/fix. Noise affecting resistance would be a new one for myself. never considered vibration either.
BT is sometimes right, It's good to talk...
It is possibly electrical interference on the cable rather than affecting the thermistor. The controller will be measuring the OAT by passing an electrical current down one core of the cable, through the thermistor, and back to the controller via a second core. An electrical interference entering the controller could affect its reading.
I presume that you have measured the air temperature, near the sensor, with the heat pump operating, to be certain it is not a true reading?
@ggw This is a requirement of the Grant pump - Section 9.13 of the Installation Manual: "A flow regulator is supplied with the heat pump. This must be fitted in the return pipe to the heat pump."
If it's not present then speak to the installer/builder.
There's no parameter on the Grant controller which shows the flow, so looking at that is the only way to find out (outside of adding your own flow meter).
Grant Aerona 3 10kW
SITREP #2
Learning experience - that's what his first winter has been... The future, maybe - the present... If willing
Temperature Sensor issue is still unresolved - Grant have talked a good game on phone - still no one is yet to turn up to fix (1 month) - they offered to post a replacement sensor - I declined, worried that if I install and something fails, bad job for the warranty. So they grudging said they would organise someone.. still waiting
Fixed temperature has worked well above freezing. 33Deg LWT is lovely and warm, even when 4Deg OT.
Our recent 0Deg weather has stressed the 10kW unit, cannot get to 33Deg, best I've seen it is 29Deg - then defrost - then 29deg - rinse and repeat. Double the electrical cost for less heat - oh the joys. Found reducing the zones down (heat only living room and bedrooms) has been effective in both getting heat into the property and slowing the defrost rate to closer to 60mins. That is my decision, and other parts of the house are *much* cooler.
Another issue - DHW
I have 3rd party controls on my S-Plan PDHW setup. For CH, works great. For DHW, the timings to get to 50Deg vary depending on the outside temp. Normal so far...
If I set the DHW time to 90min run, the unit will heat up to 50Deg - stop - but is keeping the pump running. So taking heat away from the Tank. I've had several days with no HW. I understand how this is happening, but how to correct? I need the pump to stop when it reaches set point. ? If using the 3 way valve, it will changeover to CH but as I am 3rd party setup, the unit doesn't talk to valves.
Need to get the engineering hat on - might try and Jerry rig the connections for the 3 way valve on the unit to provide an interlock
Thoughts welcome..
- 27 Forums
- 2,483 Topics
- 57.2 K Posts
- 590 Online
- 6,179 Members
Join Us!
Worth Watching
Latest Posts
-
RE: A Smarter Smart Controller from Homely?
@benson yes, I keep forgetting those tools do these ...
By Papahuhu , 5 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
PS to above Can you please confirm the model of hyd...
By JamesPa , 6 hours ago
-
RE: Say hello and introduce yourself
Underfloor hydronic, powered by both the heat pump and ...
By upnorthandpersonal , 7 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna no problem at all… I’ll see what my installer ...
By Mars , 7 hours ago
-
@majordennisbloodnok has a clear explanation above, W...
By F1p , 8 hours ago
-
RE: PV export revenue and HMRC
That makes sense. They are companies that are on market...
By Batpred , 10 hours ago
-
RE: R290 Heat Pump and Foundation Air Bricks
I have been having fun and games whilst getting surveys...
By petch , 10 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@ashp-bobba brill thanks again!
By cmartinbwmba , 16 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay OK, thanks all. Much as I thought. I am usi...
By Tasos , 18 hours ago
-
RE: Setback savings - fact or fiction?
My Midea unit reports the OAT or rather AIT (air intake...
By cathodeRay , 18 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
House was finished several years ago, complicated a bit...
By errmm , 1 day ago
-
RE: Extending Puredrive Modular Batteries
@scmilne If the manufacturer says they are ...
By Batpred , 1 day ago
-
RE: Configuration issues with 10kW Midea R32 heat pump
@cathoderay thanks so much for your helpful and expert ...
By Richard T eco home , 1 day ago
-
RE: Optimising LG Therma V R32 using AI
@bontwoody Yes, remove schedules for now anyway. H...
By Tim441 , 1 day ago
-
RE: Mitsubishi Ecodan Stats Reporting - Accuracy Worsens In Auto-Adaptation Mode
Emoncms uses the instant power consumption and delivery...
By Sheriff Fatman , 1 day ago
-
RE: Global Energy Systems Thurso ASHP
Thanks for the update Alexander, and I'm glad that you'...
By Mars , 2 days ago
-
RE: Help…my NIBE heat pump has faulted again!
@Fiona, thanks for coming back with the update, and I’m...
By Mars , 2 days ago
-
@martinrobinson, must just be the way that they've set ...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa the installer did fit primary pro flexis which...
By AdamK , 2 days ago
-
@papahuhu Ah good point. Perhaps I will need to make...
By Batpred , 2 days ago
-
RE: Plant Room Panel in Garage for ASHP, PV & Battery
@colinc Ours have their own LEDs, with plenty of col...
By Batpred , 2 days ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Yes, anyone trying to get a sense of what a heatpump wi...
By Batpred , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Eventually I had confirmation that, when setting an exp...
By Batpred , 2 days ago
-
RE: Five Years of Renewable Heating Hub
By Majordennisbloodnok , 2 days ago