Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
3 days ago
-
Ecodan consuming 100kwh per day in new build!!!
4 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
7 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
7 months ago
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
8 months ago
- 26 Forums
- 2,275 Topics
- 50.9 K Posts
- 399 Online
- 5,936 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Sorry James a typo there. Eskimos CAN perform ...
By Crimson , 41 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
This is one of the reasons why AI will be the death of ...
By cathodeRay , 1 hour ago
-
@jamespa Thanks again for your reassurance. Rob
By Ubert767 , 4 hours ago
-
RE: Oil Boiler & Heat Pump Hybrid System
Thanks for the suggestion, but farmhouse is grade 2 lis...
By paultheheating , 6 hours ago
-
RE: My DIY Heat Pump installation
This is very kind. However software is not really my ...
By Polar bear , 10 hours ago
-
RE: Request for feedback on where we're at with our quest to get an ASHP or ideas.
thanks, heatpunk looks great, being able to do the calc...
By giryan , 23 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
Why arent you expecting them to make much difference. ...
By JamesPa , 23 hours ago
-
@toodles sounds good. I started with cosy but then plug...
By Eliuccio , 23 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It has been just over a year since we changed over to a...
By npru , 1 day ago
-
RE: Finding a Thermostatic Shower Valve That Works with Heat Pump Systems
@morgan I should just have written ‘Mea Culpa’ shouldn’...
By Toodles , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
'We learn from history that we do not learn from histor...
By Lawrence Leask FInstR , 1 day ago
-
Mitsubishi Ecodan FTC7 Legionella date set
I can set the number of days between Legionella cycles ...
By DRB01 , 1 day ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Yes, I like the extra facilities that NetZe...
By Toodles , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk downstairs rads are less prone to airlocks, you ...
By AgentGeorge , 1 day ago
-
RE: My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
@editor thanks for highlighting my name. Yes I did get ...
By Chansug , 2 days ago
-
RE: balancing radiators with a mixture of different size pipework and a few undersize rads.
@editor Thanks for your input Mars. No I think the comm...
By baxtDave , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
We’re looking to expand our list of recommended list of...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Along with the right workers, they can’t b...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I have just looked at my heat pump 'long interval' (27 ...
By cathodeRay , 2 days ago