Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Mitsubishi Ecodan not good enough ?
2 weeks ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
2 months ago
-
Mitsubishi Ecodan circulation pump running.
2 months ago
-
Ecodan Auto Adapt Options
2 months ago
-
Ecodan heat pump leak
2 months ago
- 26 Forums
- 2,645 Topics
- 61.8 K Posts
- 381 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
No, I agree entirely. There shouldn't be a need for an ...
By Majordennisbloodnok , 58 minutes ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 2 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 2 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 2 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 15 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 23 hours ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 4 days ago