Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsubishi ASHP - Circulating pump noise?
Wall brackets and drip trays for wall mounting of ASHPs are readily available.
So that shouldn't be a problem.
The issue is accessibility.
If there's a flat roof beneath, then access is easy.
Save energy... recycle electrons!
Noise and vibration transference concerned me greatly - though I could see that even if vibration problems * could be negated (and I doubt how effective this might be) the noise being just outside the bedroom window would not be favoured! Access for servicing would have to have been via a ladder / tower so that didn’t appeal much either! Perhaps by the mid-2030’s, there will be ‘silent’ and much smaller / neater ASHP’s that could be installed almost anywhere!!! ;-)))
* I did investigate various anti-vibration mounts etc. in the early days of my research; the general feeling seem to be that at best, they would reduce vibration transference but could not be expected to eliminate it. I am also aware of the existence of wall mounting kits so, really noise and vibration were the real no-no’s for me. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
And going back to the very informative article ‘
‘10 Things To Consider When Choosing Pipe Insulation Thickness ’
I would class the ‘heat loss’ in the airing cupboard as “Always Useful” and am happy to leave the current pipe-work ‘as is’. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Bringing this right back on topic (noise),
can I point out that anti-vibration mounts are cheap and readily available from UK-based online stores.
They are available in a very wide range of sizes.
You simply look for the mass (Kg) you wish each mount-point to carry, and the size bolt you require.
Do heat-pump installers know about these devices, I wonder?
Save energy... recycle electrons!
The ones I discussed the subject with did - but did not rate them highly for all that! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@transparent I have been thinking about the valves that are not insulated and began to wonder if perhaps this is intentional so started to Google ….. The valves are antifreeze valves that will automatically open and drain the pipes on the heat pump side of the LLH if the temperature drops to 3 degrees C.
tells me that the valves should not be insulated - but they should be protected from the weather so I’ll take this up with the installer. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Hi,
Having the same problem was your issue fixed? If so how was it fixed please.
Hi,
We had our ASHP installed about 2 weeks ago. Hot water and heating all work well and the outside unit is much quieter than I expected it to be. Unfortunately it's the noise inside the house that's the problem. There a constant whooshing noise whenever the heating kicks in. I set the schedule to stop the water heating overnight and have set the honeywell thermostat to 15 degrees at night to stop the system running at night so I can at least sleep. This worked until the outside temp dropped below 5 degrees and suddenly the pump started circulating constantly from 11pm until 6:30 am.
We've had the installed back who says it should be quieter and must be residual air in the system which can take time to clear, just keep topping up the system to maintain pressure around 1.6 bar. I'm hoping this is all it is but it's been nearly 2 weeks and I'm topping up daily yet there are times I fancy it's getting louder and sometimes its so intrusive. I wonder about getting the whole system removed and going back to gas boiler.
Our installer had been very good and he's disabled the frost protection to stop it running at night soI can now sleep but I do worry what will happen in winter, not so much for house temp over night but for potential damage to the ASHP itself. As far as I'm aware, there is no antifreeze in the system as the manufacturer advises against it apparently.
The system is set to flow temp 46 degrees, we can't use the auto setting as the room thermometer is Honeywell so we've been advised to leave on flow temp setting.
Does anyone have any thoughts? Is there anyone who's had the same experience and it has settled down or they've found a fix?
Our system is:
Mitsubishi 6 Kw Ecodan Standalone (PUZ-WM60VAA) 150 L cylinder, low loss header/buffer tank.
Thanks
I have an Ecodan with the Mitsubishi maintenance package and it is a condition of the annual maintenance agreement that glycol is used in the system. It is unusual to hear of a system with the freeze stat switched off when there is no glycol. The installer my have fitted anti freeze valves but I would have thought that the freeze stat would be left enabled. You might wish to raise this with your installer.
https://les.mitsubishielectric.co.uk/the-hub/what-happens-to-a-heat-pump-in-the-cold
Posted by: @john00fosterHi,
Having the same problem was your issue fixed? If so how was it fixed please.
Hi,
We had our ASHP installed about 2 weeks ago. Hot water and heating all work well and the outside unit is much quieter than I expected it to be. Unfortunately it's the noise inside the house that's the problem. There a constant whooshing noise whenever the heating kicks in. I set the schedule to stop the water heating overnight and have set the honeywell thermostat to 15 degrees at night to stop the system running at night so I can at least sleep. This worked until the outside temp dropped below 5 degrees and suddenly the pump started circulating constantly from 11pm until 6:30 am.
We've had the installed back who says it should be quieter and must be residual air in the system which can take time to clear, just keep topping up the system to maintain pressure around 1.6 bar. I'm hoping this is all it is but it's been nearly 2 weeks and I'm topping up daily yet there are times I fancy it's getting louder and sometimes its so intrusive. I wonder about getting the whole system removed and going back to gas boiler.
Our installer had been very good and he's disabled the frost protection to stop it running at night soI can now sleep but I do worry what will happen in winter, not so much for house temp over night but for potential damage to the ASHP itself. As far as I'm aware, there is no antifreeze in the system as the manufacturer advises against it apparently.
The system is set to flow temp 46 degrees, we can't use the auto setting as the room thermometer is Honeywell so we've been advised to leave on flow temp setting.
Does anyone have any thoughts? Is there anyone who's had the same experience and it has settled down or they've found a fix?
Our system is:
Mitsubishi 6 Kw Ecodan Standalone (PUZ-WM60VAA) 150 L cylinder, low loss header/buffer tank.
Thanks
Sorry to hear about what are almost certainly teething troubles, the Mitsubishi is well renowned so its unlikely that there is anything major wrong. if your installer is being helpful as well it really shouldnt be too difficult to sort it out.
Lets unpack what you have said that so we understand what you are trying to fix
Noise: From the fact the installer says its air in the system, Im presuming its a gurgling sound. Please confirm. It took 4 weeks for the air to come out of my system and there was one radiator where it collected that had to be regularly bled manually. Your system (like mine) will have been fitted with an automatic bleed valve at or near the highest point, but sometimes air collects elsewhere and it needs to be bled manually. If you provide a bit more info it should be possible to diagnose.
Frost protection: There are two levels (at least) of frost protection.
- The system turns itself on. This is the primary protection (which has apparently been disabled)
- Either anti freeze valves are fitted outside near the heat pump or the system has antifreeze (glycol) in it. This is the secondary protection which kicks in if the power or primary protection mechanism fails. Your installer should tell you which of the two has been fitted if you ask, which you should.
As long as one of these is in place it shouldn't freeze, but level 2, if implemented using anti-freeze valves, can be a bit inconvenient if it triggers so we ideally need to get to the point where you can turn it back on at night.
TBH Its a shame about the buffer tank/low loss header, its almost certainly costing you an extra 15% to run as a result. Nevertheless there is certainly some optimisation to be done. Your most efficient mode of operation is to have it running 24*7 at the lowest flow temperature possible. What Honeywell thermostat do you have and do you have thermostatic radiator valves? If you tell us a bit about this we can help with some suggestions to optimise. However first lets get the noise fixed so you can run 24*7 (possibly with a night time setback) which is generally the way to run a heat pump for minimum running cost.
You may want to read this introduction which explains a lot of the key concepts.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Never did get to bottom of it. Its just because of where it's sited. Even a gas boiler engineer has said a boiler would be even more noisy if it was installed in the airing cupboard. Had I know I might have got additional sound proofing in first. Although, it may not have helped.
On the plus side, I don't really notice it anymore and friends don't find it particularly noisy either.
Sorry I've no better news for you.
- 27 Forums
- 2,815 Topics
- 66.7 K Posts
- 2,187 Online
- 7,230 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: DIY powerflushing tutorial
Inhibitor contains ions which increases conductivity no...
By bobflux , 6 minutes ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
We've had an influx of new members joining the forums o...
By Mars , 47 minutes ago
-
@editor thank you that's a very useful reply. We've man...
By Brazilguy67 , 1 hour ago
-
RE: How Can I Prove Coal Was My Main Heating Source Without Receipts?
Got excepted for the grant now so thanks for the replie...
By Chilli304 , 2 hours ago
-
Daikin Altherma 3 R F+W, room thermostat control, weath...
By JanHarley , 3 hours ago
-
RE: Buffer tank on a 2 x 14kw Ecodan system
Pretty much as I had guessed in my crude scaling from m...
By JamesPa , 6 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Well you have a vibration generator running at some fre...
By bobflux , 19 hours ago
-
RE: Why don't people choose heat pumps?
@susannasaunders The link I have found may provide a li...
By Toodles , 22 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@downfield Thats a decent rate, I’m shocked they hadn...
By Papahuhu , 2 days ago
-
RE: Should Households Who Can Afford It Pay More for Energy to Help Those Who Can't?
@batpred I mentioned earlier that targeting the payment...
By Toodles , 2 days ago
-
RE: Adventures in heat loss calculations
@toodles thanks! So as suspected, around a doubling of ...
By SusannaSaunders , 2 days ago
-
Six books in three years and I think I’ve now covered j...
By Mars , 2 days ago
-
RE: Grant Aerona3 13kw - Buffer Tank - Heating Journey
@heymikey Well done in achieving as nearer a match acro...
By Toodles , 2 days ago
-
Grant Aerona - Weather Compensation and Schedules
Im trying to set up a friends Grant Aerona. The WC curv...
By bontwoody , 3 days ago