Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Grant Aerona3 13kw - Buffer Tank - Heating Journey

37 Posts
4 Users
10 Reactions
5,377 Views
bobflux
(@bobflux)
Reputable Member Member
Joined: 9 months ago
Posts: 226
Your energy: 12 kWh
 

If you tweak the lockshields you'll unbalance the rads so nope. Just TRVs open.

It's a simple sanity check. If I read correctly you used to have 30l/min (1.8 m3/h) before the buffer tank was installed. If the Wilo can push that flow rate at a reasonable pressure drop (check the display) through your installation with all TRVs open then:

1) the heat pump circulator which is about twice as beefy should work just fine with the tank as a volumizer.

2) there is no more crap stuck in your pipes, which is always nice to know!

 



   
ReplyQuote
HeyMikey
(@heymikey)
Eminent Member Member
Joined: 10 months ago
Posts: 28
Your energy: 0 kWh
Topic starter  

Hi @bobflux and @jamespa 
tagging you as you both have been giving me advice which is invaluable and helpful. I have done the pipe trace and everything looks to be piped up how it should be. I think it was a case of misplaced probes, I also noticed the secondary Wilo pump was on the lowest setting whilst the heat pump is on the highest and I think what was happening is that the wilo pump was taking the bare minimum and the rest was mixing and returning back to the heat pump. I did put the Wilo on max give it a couple minute test and it worked better and saw the return on the bottom left come down. 

This is my trace and I hope it makes sense. 

loft

image

Airing cupboard

image

 

I know the drawings are crude but I'm trying my best to get the data across for a 2nd opinion. I think to turn it into a volumiser I'd have to connect the returns where I labelled it with a purple line. That way the return flow goes back into the airing cupboard via the flow setter and back to the heat pump. Then on the buffer plumb the heat pump flow in at the bottom left then cap the top left and bottom right. Remove the Wilo pump from system. 

Is this about right? 


This post was modified 8 months ago 6 times by HeyMikey

   
ReplyQuote
HeyMikey
(@heymikey)
Eminent Member Member
Joined: 10 months ago
Posts: 28
Your energy: 0 kWh
Topic starter  

What stiff baffles me....

How the loft flow setter which is the flow in is 28 and the return is 33. No matter what speed I use on the 2nd pump it stays relatively the same



   
ReplyQuote
Toodles
(@toodles)
Daikin
Famed Member Contributor
Joined: 4 years ago
Posts: 3100
Your energy: 35 kWh
 

@heymikey Perhaps the errors in the pump readings might suggest the actual flow rate is somewhere between (in the region of 30.5 lpm), they must match for the water circuit to run unless you have a constant top up of supply or an ever leaking pipe somewhere! Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
Like
1
ReplyQuote

HeyMikey
(@heymikey)
Eminent Member Member
Joined: 10 months ago
Posts: 28
Your energy: 0 kWh
Topic starter  

@toodles yes I think ur right.

Any thoughts on my volumiser diagram? 



   
ReplyQuote
Toodles
(@toodles)
Daikin
Famed Member Contributor
Joined: 4 years ago
Posts: 3100
Your energy: 35 kWh
 

@heymikey Sorry, with my poor vision, I have great difficulty with diagrams and photo details so will refrain from comment on that.

For what it is worth though, my system has a Low Loss Header and a Wilo Pico pump for the secondary circuit. I calibrated four probes against each other and noted the differences before attaching them to the four ports on the LLH. The Wilo Pico pump has a variable speed facility and I have managed to tweak the speed so that the pairs of ports on that LLH match within 0.1 degree C. for the vast majority of the time. Of course, the LLH is much smaller than a buffer tank might be but the same principle applies; if you can match the flow rates, then the distortion within the LLH / buffer tank is minimised and thus more efficient. Is your secondary pump furnished with a variable speed setting? Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
Love this
1
ReplyQuote
HeyMikey
(@heymikey)
Eminent Member Member
Joined: 10 months ago
Posts: 28
Your energy: 0 kWh
Topic starter  

@toodles

This is the dial on the pump below .

So the left side is Variable differential pressure (Δp-v): .

The top has a fixed I, II, III.

I believe the right side is for under floor heating. 

hcon254 1


   
ReplyQuote
Toodles
(@toodles)
Daikin
Famed Member Contributor
Joined: 4 years ago
Posts: 3100
Your energy: 35 kWh
 

@heymikey That looks as though you have a variable speed control to me; if you have the means to measure the temperature on all four ports of the buffer simultaneously, then you might care to try and match the ports (as pairs) as closely as you can using the variable speed. The aim is to match the temperature of the flow in and the flow out as closely as possible and in the same way, match the return in and out as closely as possible. You should expect to see the difference between the flow and return circuit as reflected by the Delta T of your system (typically ~5 degrees C) but the important bit is to match the temperatures in the flow (in and out) as closely as possible and similarly, the return in and out. The closer the temperatures, the less distortion is occurring and the greater the efficiency.

I had contemplated asking my installer about removal of the LLH but felt that with such a close match as I was able to achieve, I would leave well alone. Regards, Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
Like
1
ReplyQuote

HeyMikey
(@heymikey)
Eminent Member Member
Joined: 10 months ago
Posts: 28
Your energy: 0 kWh
Topic starter  

@toodles thanks Toodles.

I do have 4 probes for when I was balancing radiators 2 at a time. Maybe I should leave it and do what u did as I feel my installer probs will not agree to it. I'm fairly sure I'm a thorn in their side. 



   
ReplyQuote
Toodles
(@toodles)
Daikin
Famed Member Contributor
Joined: 4 years ago
Posts: 3100
Your energy: 35 kWh
 

@heymikey Have fun!😆Toodles.


Toodles, heats his home with cold draughts and cooks food with magnets.


   
Funny
1
ReplyQuote
HeyMikey
(@heymikey)
Eminent Member Member
Joined: 10 months ago
Posts: 28
Your energy: 0 kWh
Topic starter  

@toodles Having fun and managed to balance the buffer as best I could with the colder weather approaching. I got the flows in and the flows out within a 1 to 1.5c of each other which I think is pretty good. I don't want to have to call them back and have it removed as I think some separation is probably a good thing for my house and setup. Now to balance the heat in all the rooms. I'm going to focus on heating the rooms and not balance the radiators as such as I'd rather have an even warm house than trying to get the perfect delta t.



   
ReplyQuote
Toodles
(@toodles)
Daikin
Famed Member Contributor
Joined: 4 years ago
Posts: 3100
Your energy: 35 kWh
 

@heymikey Well done in achieving as nearer a match across the LHH port pairs. Our system has a variable speed pump within the Daikin monobloc but it tends to run at or about 30, 15 or 7.5 litres per second. The great majority of the time, the pump settles down at ~7.5 lps and this is the velocity I have set the Wilo Pico secondary pump to match - achieving a ~ 0.5 degree or better match between the flow in from the heat pump port to the flow out to the emitters port most of the time.

Regarding the balancing of radiators, as long as the rooms are achieving the comfort levels you require without any other rooms being too cold or too warm, then you probably have a reasonable balance already! I started with all radiators fully open on the TRV’s and LSV’s, noted which rooms were the warmest and started shutting down the LSV’s until they all were working in harmony achieving the room temperature required. In our case, this is simple: 22.5 C in all rooms other than the bathroom which was elevated ~ 3 degrees (we like to be comfortable!) We have most internal doors open 24/7 so are effectively ‘open plan’. Our system employs a Homely controller and one way or another we enjoy 22.5 degrees C 24/7 throughout the house.

Perhaps I should add that all TRV’s are fully open and fitted with Decorator’s Caps instead of the thermostats influencing the settings. The adjustable tops are in a box in my garage these days. Regards, Toodles.


This post was modified 2 weeks ago by Toodles

Toodles, heats his home with cold draughts and cooks food with magnets.


   