Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Grant Aerona3 13kw - Buffer Tank - Heating Journey
If you tweak the lockshields you'll unbalance the rads so nope. Just TRVs open.
It's a simple sanity check. If I read correctly you used to have 30l/min (1.8 m3/h) before the buffer tank was installed. If the Wilo can push that flow rate at a reasonable pressure drop (check the display) through your installation with all TRVs open then:
1) the heat pump circulator which is about twice as beefy should work just fine with the tank as a volumizer.
2) there is no more crap stuck in your pipes, which is always nice to know!
Hi @bobflux and @jamespa
tagging you as you both have been giving me advice which is invaluable and helpful. I have done the pipe trace and everything looks to be piped up how it should be. I think it was a case of misplaced probes, I also noticed the secondary Wilo pump was on the lowest setting whilst the heat pump is on the highest and I think what was happening is that the wilo pump was taking the bare minimum and the rest was mixing and returning back to the heat pump. I did put the Wilo on max give it a couple minute test and it worked better and saw the return on the bottom left come down.
This is my trace and I hope it makes sense.
loft
Airing cupboard
I know the drawings are crude but I'm trying my best to get the data across for a 2nd opinion. I think to turn it into a volumiser I'd have to connect the returns where I labelled it with a purple line. That way the return flow goes back into the airing cupboard via the flow setter and back to the heat pump. Then on the buffer plumb the heat pump flow in at the bottom left then cap the top left and bottom right. Remove the Wilo pump from system.
Is this about right?
What stiff baffles me....
How the loft flow setter which is the flow in is 28 and the return is 33. No matter what speed I use on the 2nd pump it stays relatively the same
@heymikey Perhaps the errors in the pump readings might suggest the actual flow rate is somewhere between (in the region of 30.5 lpm), they must match for the water circuit to run unless you have a constant top up of supply or an ever leaking pipe somewhere! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@heymikey Sorry, with my poor vision, I have great difficulty with diagrams and photo details so will refrain from comment on that.
For what it is worth though, my system has a Low Loss Header and a Wilo Pico pump for the secondary circuit. I calibrated four probes against each other and noted the differences before attaching them to the four ports on the LLH. The Wilo Pico pump has a variable speed facility and I have managed to tweak the speed so that the pairs of ports on that LLH match within 0.1 degree C. for the vast majority of the time. Of course, the LLH is much smaller than a buffer tank might be but the same principle applies; if you can match the flow rates, then the distortion within the LLH / buffer tank is minimised and thus more efficient. Is your secondary pump furnished with a variable speed setting? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
This is the dial on the pump below .
So the left side is Variable differential pressure (Δp-v): .
The top has a fixed I, II, III.
I believe the right side is for under floor heating.
@heymikey That looks as though you have a variable speed control to me; if you have the means to measure the temperature on all four ports of the buffer simultaneously, then you might care to try and match the ports (as pairs) as closely as you can using the variable speed. The aim is to match the temperature of the flow in and the flow out as closely as possible and in the same way, match the return in and out as closely as possible. You should expect to see the difference between the flow and return circuit as reflected by the Delta T of your system (typically ~5 degrees C) but the important bit is to match the temperatures in the flow (in and out) as closely as possible and similarly, the return in and out. The closer the temperatures, the less distortion is occurring and the greater the efficiency.
I had contemplated asking my installer about removal of the LLH but felt that with such a close match as I was able to achieve, I would leave well alone. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles thanks Toodles.
I do have 4 probes for when I was balancing radiators 2 at a time. Maybe I should leave it and do what u did as I feel my installer probs will not agree to it. I'm fairly sure I'm a thorn in their side.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 977 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 6 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 7 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 10 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 11 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 12 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 13 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 15 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 15 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 21 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 22 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago