Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Midea "ECO Mode" - an oxymoron
Does anyone have any docs on what the purpose of ECO Mode is on Midea heat pumps? One would assume it mean "economical" or perhaps "ecological", however as far as I can see, it is neither.
Consider the following:
With ECO Mode on, Weather Compensation is disabled, the flow temperature is set to 1°C above what the non-compensating flow temperature is, the energy consumed goes through the roof, and the heat output is not really any higher than it was with ECO Mode off!
ECO Mode is only of use when using the pre-programmed Weather Compensation curves as described from page 104 onwards in the detailed Midea data.
When ECO Mode is selected, it changes the controller from curve 4 to curve 6, which lowers the specified LWT.
If you are using curve 9, which can be adjusted by the user to match the home's heat loss, then switching to ECO Mode could actually increase the specified LWT.
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,341 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How much of your renewable and home setup would still work if the internet went down?
Agree but remember to retain your isp router as they wi...
By JamesPa , 6 seconds ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@susannasaunders Reluctantly I think i agree with @r...
By JamesPa , 6 minutes ago
-
RE: Why don't people choose heat pumps?
It's swings and roundabouts - during off-peak periods t...
By Temperature_Gradient , 1 hour ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 8 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 9 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 9 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 12 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 16 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 4 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago