Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
Hi all,
Heating has been kicking in more frequently this week and I am now getting a reccuring low flow rate error on my system, 370F27. I can clear it for a few minutes by switching it off and on again but it appears to be persistant and coming back each time.
I called up the Ideal Customer Support and they said it may be due to air in the system or a blockage and to contact my installer. We had an ECO4 install, and my installer has been diabolically slow to respond to any issues since they completed the install, so whilst I will get a response there is no guarantee when (current record is 6 weeks between us sending a message and recieving a response from them! And then they'll need to actually get someone out to us which is a whole other nightmare.)
I have cleaned the magnetic filter and checked all the automatic bleed valves, I also bled the radiators and topped up the pressure to just above 1.5bar. All to keep my Primary flow rate sitting at 13l/min which is 1.5l/min below the minimum flow rate for the system. 😩
Does anyone have any idea of what I might be able to do to increase the primary flow rate so I can have some heating as if it continues to not work, by the time I get a response, my 170 year old stone cottage will have settled back to it's happy place at around 8-10 degrees or just below whatever the outside temperature happens to be! 😱
TIA!
@wh0am3ye - do you have so called primary and secondary circuits (ie some form of separation of what goes through the heat pump and what goes through the rads)? If so, I guess the magnetic filter is on the rad circuit, but there is usually also one on the primary circuit. If there is, have you checked that? Mine is in something that looks like a ball valve, but the ball is actually a filter that unscrews from the bottom closing the valve (and reopening after checking/cleaning!).
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay As far as I can tell, there is just the one filter, on the heat pump side of the cylinder (bottom left in the photo), I attempted to clean it out earlier on, but wasn't able to remove the mesh inside. Perhaps I need to have another go at that as watching the only video I can find online with my issue, the flow rate was being limited by a blocked filter.
@wh0am3ye - can't make out all the details from that photo - is it separated (primary and secondary circuit) or just one big open circuit?
Either way, you need to get the mesh filter out of the magnetic filter, blocked mesh filter and low flow rates have a natural affinity!
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Honestly, I'm not sure. The flow and return come from the heat pump, in to the cylinder on the left side and then the flow and return out to the radiators comes out the cylinder on the right side, where the pump is. I don't know if there is a secondary circuit or not.
Sounds like the plan for this evening is walk the dog, have dinner and dismantle the filter again! I'll update when I've cleaned it and see what happens!
@wh0am3ye - it's just possible that is a huge buffer, the mother of all buffers, not sure. What about DHW, is that entirely separate, with a diverter valve? We can explore more tomorrow.
Meanwhile getting that filter out makes sense. Mine does sometimes need a firm pull to get the mesh but out, it gets a bit stuck at the bottom. If you can find a parts diagram (or cross sectional drawing) for yours, you can reassure yourself that you cam make sure you pull in a way that won't do any damage.
Midea 14kW (for now...) ASHP heating both building and DHW
@wh0am3ye Check out by the ASHP on the pipes next to the unit and see if there is a Y strainer this is usually the culprit to look for 1st
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@wh0am3ye, as @ashp-bobba has pointed out, most flow errors on heat pump systems are caused by a blocked Y-strainer. What's remarkable about them is that they don't require a lot of dirt/corrosive bits to cause the issue. This a good starting point.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor we now fit 800 micron Y strainers rather than the very standard 100Mic, Samsung and a couple of other makes are very sensitive to low flow and we found when servicing as we don't fit Samsung units that the 100Mic can sometimes halve the flow in a clean system, the 800 reduces it by about 10%.
We also sometimes go as far as fitting 35mm Y strainers on a 28mm pipe with reducers just to give a system less restriction but the same protection, just another example of a littler further for it to be a little better, also we actually go back to our installs and service them year after year so helps us not have annoying low flow issues.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Thank you for all your responses!
I gave the magnetic filter another clean and got the mesh out this time. Flow rate back up to 24.5l/min! Success!
I will take a look to see if we have any Y-strainers tomorrow and give them a clean as well if so.
@wh0am3ye super, glad your back up and running.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@wh0am3ye - good news about the flow rate being better after cleaning the mesh filter.
Posted by: @wh0am3yeI will take a look to see if we have any Y-strainers tomorrow and give them a clean as well if so.
Bear in mind the filter if fitted may look like a large ball valve with a cap screwed into the base (as mine does) rather than a Y strainer.
I also think it is still worthwhile identifying the basic design/layout of your system, if only for future reference. I am now more inclined to think that what I thought might be the mother of all buffer tanks may in fact a DHW cylinder, but it is by no means clear. For example, the pump visible in the photo appears to gave been labelled CH1 - which suggests central heating, not DHW.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,661 Topics
- 62.2 K Posts
- 313 Online
- 7,058 Members
Join Us!
Directory
Latest Posts
-
RE: GivEnergy inverter tripping due to over-voltage?
Thanks for that info. Yes, I'm well aware that GivEne...
By Transparent , 25 minutes ago
-
Thanks for sharing, ours is looking fairly different. ...
By Batpred , 2 hours ago
-
RE: Cooling with air to water heat pumps
Very sensible Unfortunately I fear that's too simple...
By JamesPa , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Good morning. I just came across your website. Was ho...
By iRadiate , 10 hours ago
-
RE: Failed Heat Pump Install: IWA Claim Rejected
Many of the estimates we received mention IWA and RECC....
By Batpred , 21 hours ago
-
RE: Rural burning – I've had enough
Same here in Finland. It's strictly forbidden ...
By upnorthandpersonal , 21 hours ago
-
RE: Renewables & Heat Pumps in the News
Something worth flagging... we've just published a news...
By Mars , 22 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
The Homeowners' Q&A podcast is back... I've changed...
By Mars , 22 hours ago
-
RE: Anyone concerned about GivEnergy?
I have already signed up with Axle so yes, that takes c...
By KevH , 23 hours ago
-
@batpred Would it pass the airbnb feedback test no. I...
By EtchedPixels , 2 days ago
-
A quick update... we've just launched the beta version ...
By Mars , 2 days ago
-
RE: Who Actually Owns a Heat Pump in Britain? We Asked. Here Is What We Found.
The age part doesn't surprise me - only 25% of UK home ...
By EtchedPixels , 2 days ago
-
RE: Home automation and the cloud; is there a better way?
Nothing you've said there, @etchedpixels, is something ...
By Majordennisbloodnok , 2 days ago
-
I've heard from others living in the vicinity of Derril...
By Transparent , 2 days ago