Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Radiator sizing for heat pump installation by British Gas - are these correct?
We are booked in for a heat pump install with British Gas. So far we have been very impressed with them and it will be installed in around 10-12 weeks.
I'd like to run by your thoughts as to their radiator plans.
They look pretty sensible to me and have been designed at 42.5c (not 50c like Octopus).
They want to change all bar one of our radiators, including an additional on the landing and all much bigger than we have (which we are happy with).
They have sized the radiators at 21c in all rooms, including bedrooms. Only the bedrooms will have TRV's.
Will the bedrooms be too warm? Ideally we want to run the heat pump 24/7, with a small setback overnight.
Should we stick with the bedroom radiators at this size, or ask BG to resize them at a lower temperature?
Is it better to have the bedroom radiators oversized for greater volume and let the TRV's limit the flow to avoid overheating, or reduce the radiator sizes in the hope the TRV's won't need to kick in?
Heat pump will be a Daikin 8kw Altherma LT, 25l volumiser.
House heat loss was 6.2kw.
Attached is the radiator schedule.
Thanks.
Assuming the heat loss figures are accurate, the radiator sizings look sensible. We have Flow Regulating Valves (FRVs) installed on almost all our radiators. They make it very easy to balance the flow across all the radiators. I wonder whether they would be prepared to install them?
I am not sure whether it's OK to have TRVs as well as FRVs on bedroom radiators. Hopefully, someone else can advise.
We are finding that upstairs is about 1.0-1.5C higher than downstairs. I am not sure whether that is just natural stratification with the warm air rising from downstairs. So far, we are just running all our bedroom TRVs wide open. We find the bed is a bit cool at the beginning of the night, but we wake up a bit too warm. That may be due to our rather old Tempur foam mattress. Apparently, the latest ones breathe and release heat better. Still, it is really nice to be able to go downstairs and make a cup of tea without need to wear a dressing gown!
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
Good point about the FRVs, @grahamf. Renewable Heating Hub members get 10% off by using the discount code RHHFRV10 at checkout, if you buy from Firepower.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Posted by: @grahamfWe are finding that upstairs is about 1.0-1.5C higher than downstairs
So why not just turn down the frvs on these radiators? There is nothing sacrosanct about the 'design' flow rate
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @bashWill the bedrooms be too warm? Ideally we want to run the heat pump 24/7, with a small setback overnight.
If bedrooms are too warm just reduce the flow rate through them by turning down the lsvs (or frvs if you can get them fitted) This reduces the average rad temp this reducing the heat emitted. That's what I and others have done.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Thanks, I'm assuming as I'll have a decent volume of around 120ltrs + pipework, the reduced flow shouldn't make much of a difference and better than allowing the TRVs to take over too much?
With the frvs, I assume looking at the blurb, they just make the balancing easier?
Posted by: @bash@jamespa Thanks, I'm assuming as I'll have a decent volume of around 120ltrs + pipework, the reduced flow shouldn't make much of a difference and better than allowing the TRVs to take over too much?
Posted by: @bashWith the frvs, I assume looking at the blurb, they just make the balancing easier?
Trvs switch the flow off altogether so anything which reduces flow rather than switching it off is better from a flow perspective.
Frvs are as you say sold to help with balancing. However given what they do is adjust the flow rate, they can be turned down or up from the 'design' setting thus doing the same job as lsvs but with better control. Another way to look at it is that they can be used to balance the rads for equal room temp (or desired temp differences) as opposed to equal deltaT.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
After months of research, that is my understanding, that you ideally don't want to remove a radiator from the system completely (the trv switching it off), as you want to keep as much of the entire system as possible flowing.
These frvs do look to be a better way than trial an error with a standard lock shield.
I assume you'd want the whole system balanced at point of install, that all radiators heat evenly.
Then as time goes by and you get a better idea of how each room heats up, you can reduce the flow to some rooms that may have a tendency to overheat, which will be pretty straightforward and more accurate with a frv.
Are these radiator frvs the same as what is used with underfloor heating?
Posted by: @bashAfter months of research, that is my understanding, that you ideally don't want to remove a radiator from the system completely (the trv switching it off), as you want to keep as much of the entire system as possible flowing.
These frvs do look to be a better way than trial an error with a standard lock shield.
I assume you'd want the whole system balanced at point of install, that all radiators heat evenly.
Then as time goes by and you get a better idea of how each room heats up, you can reduce the flow to some rooms that may have a tendency to overheat, which will be pretty straightforward and more accurate with a frv.
You are spot on.
Posted by: @bashAre these radiator frvs the same as what is used with underfloor heating?
I don't know TBH as I don't have them, they weren't available when my heat pump was fitted. They look that way though!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,754 Topics
- 64.8 K Posts
- 2,081 Online
- 7,159 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
Thanks for sharing that. Your objective seems very sen...
By JamesPa , 3 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Very nice. Ours was the opposite, about 10%...
By Papahuhu , 4 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
A couple more points about placing solar panels at low ...
By Transparent , 4 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@kilgorexv definitely a larger inverter will help and m...
By AndrewJ , 1 day ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
The installation is almost done! I've written up two ...
By tomasmcguinness , 2 days ago
-
RE: Glass lined Cylinder for private water supply
This has turned into a fascinating little rabbit hole. ...
By Mars , 2 days ago
-
RE: Switch suitable to change between two inverter CT's
Last winter my battery ,32KWh, could run the house com...
By Jancold , 2 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Agree with Major. And even if I was very happy with ...
By Batpred , 2 days ago
-
RE: Is the "divide by 2900" rule still valid?
There is another estimator that you could use, a formul...
By Rob of York , 2 days ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 5 days ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 6 days ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 6 days ago