Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
PUHZ SW120Y & EHSC-VM2D - Buffer tank to Volumiser
Eventually I was able to find someone here in the Algarve to, amongst other things, convert my buffer tank to a volumiser and in the process remove the secondary pump. They failed on the Wireless Controller and the support from Mitsubishi Portugal throughout, was utterly deplorable.
I picked up from somewhere that a dip switch should have been changed when a buffer tank is not used and in lieu of assistance from Mitsu Portugal I put this question to Mitsu UK:
"I thought I recalled that a dip switch change was required, but the contractor had no knowledge of this.
I have studied the manual and see that SW 2-6 is for On/Off “Mixing Tank”."
The reply was:
"If you are a homeowner we cant advise on electrical or dip switch issues and this would require a callout to investigate"
So, with the heating season imminent, I am stuck.
Is anyone able/ willing to confirm the facts re this switch selection?
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 12kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 27 Forums
- 2,754 Topics
- 64.8 K Posts
- 745 Online
- 7,159 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
Thanks for sharing that. Your objective seems very sen...
By JamesPa , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Very nice. Ours was the opposite, about 10%...
By Papahuhu , 3 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
A couple more points about placing solar panels at low ...
By Transparent , 4 hours ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@kilgorexv definitely a larger inverter will help and m...
By AndrewJ , 1 day ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
The installation is almost done! I've written up two ...
By tomasmcguinness , 2 days ago
-
RE: Glass lined Cylinder for private water supply
This has turned into a fascinating little rabbit hole. ...
By Mars , 2 days ago
-
RE: Switch suitable to change between two inverter CT's
Last winter my battery ,32KWh, could run the house com...
By Jancold , 2 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Agree with Major. And even if I was very happy with ...
By Batpred , 2 days ago
-
RE: Is the "divide by 2900" rule still valid?
There is another estimator that you could use, a formul...
By Rob of York , 2 days ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
@penval, really useful update. After all the discussion...
By Mars , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 5 days ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 6 days ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 6 days ago