Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
How to Zone with a Single Room with UFH
Hi all,
I am currently looking at a project to fit an ASHP for a client. I haven't come across this before, but I wouldn't imagine it being too uncommon nowadays. The ground floor is all radiators except for one room, which is an extension with underfloor heating. The first floor is then radiators. What are the options here?
I tried speaking to Vaillant, but I didn't seem to get anywhere, what's your guys recommendations.
Thanks,
We have exactly what you describe, one utility room with UFH but radiators elsewhere.
Design one single open loop, increase radiator size if need on a room by room basis. Use a down-mixer for UFH section from overall design flow temperature (often 45C or 50C) for worst external temp (often -2C).
The installer was trained through the Heatgeek system, changed the main pipe flow from ashp to DHW cylinder from 22mm to 26mm diameter and also about 15m of first section of main feed to radiators. The only “thermostat” box is the Vaillant control box in the entrance hall. Weather compensation set up with the slope parameter at 0.6.
The key to getting the design right is the heat loss analysis of the house. Personally I like the Heatpunk software.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
-
Issue with Samsung Cascade System
1 day ago
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
2 weeks ago
-
Surface mount or bury primaries for heat pump installation?
4 weeks ago
-
Design Of Cascade System Replacing Undersized ASHP
4 weeks ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
3 months ago
- 27 Forums
- 2,733 Topics
- 64.2 K Posts
- 1,561 Online
- 7,140 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Questions about A2A for heating as well as cooling
@ashp-bobba ah that's good to know, I'll get in contact...
By donciccio , 1 minute ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Samsung 16kw has been working well at home in Perthshir...
By DowallyDrifter , 43 minutes ago
-
RE: Aircon - in listed buildings
@etchedpixels thanks for giving such a full and helpful...
By GrahamF , 22 hours ago
-
RE: Acond heat pump failed after four years - diagnostic quote £940 plus VAT
Another idea if the above don't work - there are compan...
By downfield , 1 day ago
-
RE: Love veg, hate watering cans
They have their downsides but boreholes are great in th...
By ian33a , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist The service engineer powered down the ex...
By Papahuhu , 1 day ago
-
RE: Issue with Samsung Cascade System
@jamespa It's a funny system, but was out only option l...
By Renewables345 , 1 day ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Thanks, I like the chart, very helpful and this will de...
By baroquebank , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Production resumed to normal once the issue ...
By MK4 , 2 days ago
-
RE: Digest of UK Energy Statistics
That sounds painful. It would be much better to charg...
By Transparent , 3 days ago
-
Hole diameter is small but hole length is also very sma...
By bobflux , 3 days ago
-
RE: Are Wind Turbines Really “Losers”?
We were sailing near a wind farm in the North Sea last ...
By Jeff , 3 days ago
-
@trebor12345 The idea is to ensure that Powerwall knows...
By Toodles , 3 days ago