Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
How to Zone with a Single Room with UFH
Hi all,
I am currently looking at a project to fit an ASHP for a client. I haven't come across this before, but I wouldn't imagine it being too uncommon nowadays. The ground floor is all radiators except for one room, which is an extension with underfloor heating. The first floor is then radiators. What are the options here?
I tried speaking to Vaillant, but I didn't seem to get anywhere, what's your guys recommendations.
Thanks,
We have exactly what you describe, one utility room with UFH but radiators elsewhere.
Design one single open loop, increase radiator size if need on a room by room basis. Use a down-mixer for UFH section from overall design flow temperature (often 45C or 50C) for worst external temp (often -2C).
The installer was trained through the Heatgeek system, changed the main pipe flow from ashp to DHW cylinder from 22mm to 26mm diameter and also about 15m of first section of main feed to radiators. The only “thermostat” box is the Vaillant control box in the entrance hall. Weather compensation set up with the slope parameter at 0.6.
The key to getting the design right is the heat loss analysis of the house. Personally I like the Heatpunk software.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
-
High air source heat pump running costs – Vaillant AroTherm Plus
3 weeks ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 months ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
4 months ago
-
Running my new Nibe ASHP efficiently
4 months ago
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 378 Online
- 7,028 Members
Join Us!
Latest Posts
-
RE: Anyone concerned about GivEnergy?
Good. That's the right approach. If the PSU (power su...
By Transparent , 52 minutes ago
-
RE: Estimating true heat loss from twelve months of consumption data
@ian33a — a measured heat loss always trumps a calculat...
By cathodeRay , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay Thanks for your detailed response.Just two ...
By PeterWurmsdobler , 2 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
The hot water heating looks normal. The heat transfer ...
By GrahamF , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
Good questions @temperature_gradient. My understanding ...
By springswood , 6 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 17 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 22 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 1 day ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 1 day ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 1 day ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 1 day ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 2 days ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 2 days ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 2 days ago