Hitachi Yutaki SCombi Heat Pump - Owners
Posted by: @sim0n0@jamespa I know it’s reached the set point as the set temp and the actual temp are both showing 48 degrees. Usually this would trigger the switch back from DHW to heating mode. I haven’t sat with it for long enough to know if it tries to reach a higher temp but I don’t think it does. Normally in DHW mode the heat pump gradually raises the flow temp to 53 degrees. The immersion then takes over, but this only happens with the Legionella program. I’d have to check but I think the heat pump wasn’t producing heat when I found it ‘stuck’ at 48 in DHW mode. No other symptoms other than the house getting cold.
Yes, only happened recently, the heating and hot water have both been working fine for several weeks and no, nothing has been changed on the controller
OK. The interesting thing is that the heat pump is still in DHW mode, which presumably means that the controller thinks the job isnt finished yet. Thats why I ask if it overshoots.
If the flow temp only gets to 53C is it possible that achieving 48 is 'marginal'? Has something changed which meant tahat its gone from marginal to to insufficient.
This begs the question - what happens if you reduce the target temp. It also begs the questions
can you adjust the offset between flow temp and target temp?
what cylinder have you got?
Its difficult to ask all the questions without being there (sorry Im not offering.).
Is there anything else at all which changed around the same time as the problem first appeared, which might give us a clue?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa It has always worked with these settings and nothing has been changed which points to a fault somewhere. I haven’t done any troubleshooting yet as I know it will work in manual with the immersion on. I know this works as it’s how we were forced to run it the whole first winter before I had the system pipework modified.
Yes I can adjust the hysteresis and the target temp but all that will confirm is it’s not working and I know that already.
It’s a 300L ‘heat pump specific’ tank I can’t remember the brand.
I honestly don’t want to appear ungrateful but yes I will test connections but then I will want to speak to Hitachi to firstly make sure I’m on the latest firmware and then to ask if they’ve seen this particular issue.
Hitachi support doesn’t exist in the UK - it’s not a long term proposition. I will no doubt switch to a supported brand which is a shame as the Hitachi is a nice spec machine. Even if it’s 3-4kW too big for my property but that’s another story LOL
BTW my old Potterton Suprema boiler I had for almost 25 years with just annual services and the odd circuit board change. It was still going strong when I sold the property 2 years ago.
The MCS certified heat pump installer/developer who fitted the Hitachi spec’d the wrong size heat pump, fitted a Freedom Heat Pumps low loss heater, multiple room stat not fit for purpose package. Incorrectly sized the primary pipework and delivered a system that was basically faulty from day one. The developer pocketed the £7500 and I’m left to pick up the bill to fix. And that same heat pump installer is now not only MCS certified, but they’re also Heat Geek certified and to rub salt into the wound they use photos of my property as advertising on their website.
So please forgive my tone. There may be decent installers out there but you can count them on one hand and there certainly aren’t any near me prepared to support my system.
.
Posted by: @sim0n0It has always worked with these settings and nothing has been changed which points to a fault somewhere.
It does but, unless there has been a firmware update, it cant be a controller fault, suggesting its a wiring, connection or valve fault. But that is unlikely to be consistent with the controller saying its in DHW mode when it should be in space heating mode.
A faint possibility is that the temperature sensor has moved or is at fault, but its difficult to see how that is consistent with the controller showing its reached temp.
Something isnt making sense!
Posted by: @sim0n0I honestly don’t want to appear ungrateful but yes I will test connections but then I will want to speak to Hitachi to firstly make sure I’m on the latest firmware and then to ask if they’ve seen this particular issue.
Hitachi support doesn’t exist in the UK - it’s not a long term proposition. I will no doubt switch to a supported brand which is a shame as the Hitachi is a nice spec machine. Even if it’s 3-4kW too big for my property but that’s another story LOL
Im not suggesting you are ungrateful. As you describe it its a weird (and unlikely) fault though which makes me wonder if there are any other clues to be had from close observation (which it sounds like you have been doing)
It does appear from what people here are saying that few Hitachi A2W heat pumps have been fitted in the UK. The manual suggests it is a highly capable machine, possibly one of the most flexible on the market, but it seems like they haven't built out their support network like some others have.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 334 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
cop for yesterday 1.8. getting the installer to try a...
By AdamK , 29 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
Let me point out that there are many Chinese suppliers ...
By Transparent , 59 minutes ago
-
RE: Weather compensation- why you should use it
@majordennisbloodnok — The Two Ronnies Mastermind sketc...
By cathodeRay , 1 hour ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
The Regulations specify the export limits in Amps. If...
By Transparent , 1 hour ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hope your issues are sorted out soon. We have ...
By ChandyKris , 1 hour ago
-
RE: Setback savings - fact or fiction?
The costs, if any, are not that great - see my calculat...
By JamesPa , 3 hours ago
-
RE: Electricity price predictions
As electricity prices continue to rise and specialist h...
By Mars , 4 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Your installer is probably right. The L9 error means l...
By JamesPa , 4 hours ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 5 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 5 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 6 hours ago
-
RE: Running from backup generaor in powercut?
@batpred Thanks for the warning. definately a job for a...
By Pipcart , 6 hours ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 6 hours ago
-
RE: Heat pump not reaching flow temperature
is the house warm enough?
By davidnolan22 , 11 hours ago
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 12 hours ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 12 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 22 hours ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 22 hours ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 1 day ago