Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Hitachi Yutaki SCombi Heat Pump - Owners
Posted by: @sim0n0@jamespa I know it’s reached the set point as the set temp and the actual temp are both showing 48 degrees. Usually this would trigger the switch back from DHW to heating mode. I haven’t sat with it for long enough to know if it tries to reach a higher temp but I don’t think it does. Normally in DHW mode the heat pump gradually raises the flow temp to 53 degrees. The immersion then takes over, but this only happens with the Legionella program. I’d have to check but I think the heat pump wasn’t producing heat when I found it ‘stuck’ at 48 in DHW mode. No other symptoms other than the house getting cold.
Yes, only happened recently, the heating and hot water have both been working fine for several weeks and no, nothing has been changed on the controller
OK. The interesting thing is that the heat pump is still in DHW mode, which presumably means that the controller thinks the job isnt finished yet. Thats why I ask if it overshoots.
If the flow temp only gets to 53C is it possible that achieving 48 is 'marginal'? Has something changed which meant tahat its gone from marginal to to insufficient.
This begs the question - what happens if you reduce the target temp. It also begs the questions
can you adjust the offset between flow temp and target temp?
what cylinder have you got?
Its difficult to ask all the questions without being there (sorry Im not offering.).
Is there anything else at all which changed around the same time as the problem first appeared, which might give us a clue?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa It has always worked with these settings and nothing has been changed which points to a fault somewhere. I haven’t done any troubleshooting yet as I know it will work in manual with the immersion on. I know this works as it’s how we were forced to run it the whole first winter before I had the system pipework modified.
Yes I can adjust the hysteresis and the target temp but all that will confirm is it’s not working and I know that already.
It’s a 300L ‘heat pump specific’ tank I can’t remember the brand.
I honestly don’t want to appear ungrateful but yes I will test connections but then I will want to speak to Hitachi to firstly make sure I’m on the latest firmware and then to ask if they’ve seen this particular issue.
Hitachi support doesn’t exist in the UK - it’s not a long term proposition. I will no doubt switch to a supported brand which is a shame as the Hitachi is a nice spec machine. Even if it’s 3-4kW too big for my property but that’s another story LOL
BTW my old Potterton Suprema boiler I had for almost 25 years with just annual services and the odd circuit board change. It was still going strong when I sold the property 2 years ago.
The MCS certified heat pump installer/developer who fitted the Hitachi spec’d the wrong size heat pump, fitted a Freedom Heat Pumps low loss heater, multiple room stat not fit for purpose package. Incorrectly sized the primary pipework and delivered a system that was basically faulty from day one. The developer pocketed the £7500 and I’m left to pick up the bill to fix. And that same heat pump installer is now not only MCS certified, but they’re also Heat Geek certified and to rub salt into the wound they use photos of my property as advertising on their website.
So please forgive my tone. There may be decent installers out there but you can count them on one hand and there certainly aren’t any near me prepared to support my system.
.
Posted by: @sim0n0It has always worked with these settings and nothing has been changed which points to a fault somewhere.
It does but, unless there has been a firmware update, it cant be a controller fault, suggesting its a wiring, connection or valve fault. But that is unlikely to be consistent with the controller saying its in DHW mode when it should be in space heating mode.
A faint possibility is that the temperature sensor has moved or is at fault, but its difficult to see how that is consistent with the controller showing its reached temp.
Something isnt making sense!
Posted by: @sim0n0I honestly don’t want to appear ungrateful but yes I will test connections but then I will want to speak to Hitachi to firstly make sure I’m on the latest firmware and then to ask if they’ve seen this particular issue.
Hitachi support doesn’t exist in the UK - it’s not a long term proposition. I will no doubt switch to a supported brand which is a shame as the Hitachi is a nice spec machine. Even if it’s 3-4kW too big for my property but that’s another story LOL
Im not suggesting you are ungrateful. As you describe it its a weird (and unlikely) fault though which makes me wonder if there are any other clues to be had from close observation (which it sounds like you have been doing)
It does appear from what people here are saying that few Hitachi A2W heat pumps have been fitted in the UK. The manual suggests it is a highly capable machine, possibly one of the most flexible on the market, but it seems like they haven't built out their support network like some others have.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Hitachi Shirokuma Air2Air HP
10 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,717 Topics
- 63.6 K Posts
- 2,153 Online
- 7,119 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Hi everyone, I’m looking for real-world advice and co...
By asoksevil , 2 hours ago
-
I knew that Reactive Power support was required by the ...
By Transparent , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Those are very good questions and indeed ones I was ask...
By JamesPa , 6 hours ago
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 7 hours ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 7 hours ago
-
I don't remember the manufacturer name, but I saw simil...
By bobflux , 9 hours ago
-
RE: Weather compensated secondary circuits with Biomass
UFH is ideal to get max efficiency with a heat pump, bu...
By bobflux , 9 hours ago
-
RE: Vaillant Arotherm Pro vs new Plus
when our system was installed in September 2 years ago ...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
I had a Heat Geek lead install by Green Heat Norfolk. T...
By Orlando , 1 day ago
-
RE: Mitsubishi Ecodan FTC6 settings
While @F1p's dongles are great, the FTC can do this its...
By RobS , 2 days ago
-
RE: Samsung heat pump - data cable issue
If it's a data cable, current will be minuscule, voltag...
By bobflux , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
I got hit with an RHI audit in 2022. It was far from c...
By Abernyte , 2 days ago
-
Hi,is there any Haier super aqua gt users on here,that ...
By Glenn Crawford , 2 days ago
-
RE: Electricity price predictions
@papahuhu Groucho Marx had something to say about no...
By Toodles , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa haha very true, although the engineer yesterda...
By swwils , 3 days ago