Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Sounds like it might be setup with a fixed flow temp without weather compensation? Might be best to set up a new thread and post the link here so we can hop on and get into the detail of your install. There will be lots of people who are happy to help you investigate.
Posted by: @murchison2003Hi all
Just read this through this topic and looks like there are alot of yous with the same issue as i have and hopefully someone can help with the high running costs i'm experiencing.
Some basic background information, i have a timber frame kit /block bungalow, heating area 267m2 with underfloor heating, highly insulated, A rating EPC. Replaced a 14 year old ground source pump with a Vaillant Aro Therm 12 kw air source pump approx 3 months ago and haven't touched any settings that the installation team set up. I have tried various timings, on all time / timer etc to try and get this running as efficiently as possible. DHW set at 48 deg on manual to top up when water drops 5 deg. All underfloor manifolds open and inside thermostat set at 21.5 with fallback at 21 deg. I normally run this for 4 hours at night on the cheap tariff to heat the house which retains the heat for about 10 hours then it kicks in for approx 4-5 hours, this is the time it takes to increase the inside temp by .5 to 1 deg.
What i have noticed is this, no matter what the outside temperature is, i've seen it at -3 ranging to + 9 deg, the flow temperature is always 32-38 deg, i haven't seen above 38 deg no matter how long the pump has been running. When heating DHW, i've seen the flow temp up as far as 69 deg which tops up the 300 ltr water tank in about 30 mins. Another thing i've noticed too is that the pump runs at 5 kw/ hr all the time, again no matter how long the pump has been running, it ran for 7 hours solid once, all at 5 kw/hr. Is this correct as i would have thought that when it gets up to temperature it wouldn't take so much energy to sustain that temperature. Am i right or have i got this all wrong? I'm hoping a few setting adjustments will remedy this running costs but not holding out much hope. I am grateful that i have solar and battery storage to compensate for the running of this pump, if not my December bill would have been £980 which is a bit worrying. I appreciate electricity prices have risen dramatically however this pump is running way more expensive than my ground source pump did. My old system used to run at 34 deg and that kept my whole house at 22 deg where now i have cold ceramic floors at this flowrate temperature which i just can't understand.
Any input would be appreciated.
Thanks in advance.
Why didn't you replace the old GSHP with a new GSHP, since they are more efficient?
I would suggest that you read through the manual, particularly the section on weather compensation (WC), and check that your ASHP is set to operate in WC mode, and report back the actual settings of the WC curve.
Derek M
i would have if I could have but due to new regulations, all the house demand now has to come completely from the source. My old pump had an immersion back up whereas now the pumps do not come with such backup. I would have required to double the length of my ground coil which wasn’t viable hence why the air source pump is fitted.
@derek how is your COP looking for DHW when the heating is switched off in April/May? We had our Glycol levels adjusted and would like a comparitor.
Ours is 3.15 for May heating 250l to 47 degrees once per day.
I also noticed the heat pump uses 1kwh every few days for 'heating' even though heating is switched off. Does yours do similar?
Posted by: @webcmg@derek how is your COP looking for DHW when the heating is switched off in April/May? We had our Glycol levels adjusted and would like a comparitor.
Ours is 3.15 for May heating 250l to 47 degrees once per day.
I also noticed the heat pump uses 1kwh every few days for 'heating' even though heating is switched off. Does yours do similar?
We don't have an A2W heat pump we have an A2A one that cannot heat the DHW. At the moment our DHW is provided exclusively by our solar PV system via a power diverter.
@webcmg Pretty busy at the mo and also getting solar + battery installed so not been paying attention to heat pump. We had family staying so had to tweak the DHW temp to accommodate more. Not had time to look at COP but here's a dump of my May DHW screens.
Posted by: @sazI'm also trying to get to the bottom of my high running costs. It is arduous to say the least. Have you had an independent inspection @webcmg?
@saz whatever happened to your issues? I know you were really stressed out, with no obvious resolution.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@derek-m I have re-read this thread because @colin and I were discussing our respective ASHP efficencies. Quite early on in the thread you suggested measuring the flow and return temps across the buffer which I didn't really understand at the time and did not have the equipment to measure. The buffer was subsequently re-piped so the flow was through the top and the return was through the bottom (both pipes on direct opposite sides for flow and return). I thought I would measure the temperatures across the buffer today and noticed that there is only Delta-T of 2 degrees between flow and return, but that there was also a 1 degree loss on the outward flow across the buffer. The system flow temp via the Vaillant app was reporting 29 degrees at the time the photo was taken.
I'm interested in whether this all look as expected? My 2024 COP was 4.82 (5.5 CH, 3.73 DHW) Total usage for the year was 4181 kwh.
Thanks
Posted by: @webcmgI'm interested in whether this all look as expected? My 2024 COP was 4.82 (5.5 CH, 3.73 DHW) Total usage for the year was 4181 kwh.
Posted by: @webcmgI thought I would measure the temperatures across the buffer today and noticed that there is only Delta-T of 2 degrees between flow and return, but that there was also a 1 degree loss on the outward flow across the buffer. The system flow temp via the Vaillant app was reporting 29 degrees at the time the photo was taken.
!C drop across the buffer is small, and might cause an efficiency degradation of ~3%. But 2C flow to return is also small so was this at a time when the heat pump wasnt working particularly hard?
SCOP of 4.82 means that your heat pump will be quite a bit cheaper than oil or gas so probably not worth worrying too much!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
After running a search in the god ol' watson, this is where it took me for running costs of heat pumps. No further comments..
I came across this recent Home owners alliance survey that puzzled me. 66% of people that own a heat pump (presumably in the UK) find it is more expensive to run than their previous system... The study was commissioned by "Green Britain Foundation":
https://hoa.org.uk/advice/guides-for-homeowners/for-owners/how-much-does-a-heat-pump-cost
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpred...
I came across this recent Home owners alliance survey that puzzled me. 66% of people that own a heat pump (presumably in the UK) find it is more expensive to run than their previous system... The study was commissioned by "Green Britain Foundation":
...
To be frank, that doesn't entirely surprise me.
At face value, there seem to be two obvious issues in play at the same time:
- The cost differential between fossil fuel and electricity. We already know that a heat pump can reasonably be expected to deliver 300% or more efficiency over a year if set up properly and may manage more. However, that obviously can't entirely offset an electricity kWh price of perhaps 5 times that of gas.
- The actual system setup for "most" installations. This forum exists primarily because of the sheer number of badly implemented heat pump systems, and I suspect there's a significant proportion of heat pump owners who don't even realise they are running their system in a less than optimal way. It would be incredibly interesting to know what proportion of the total heat pump install base is set to run at a fixed flow temperature; it's not something I ever expect to find out but if a sizeable proportion of that 66% are responding about a system like that then no wonder they're finding it more expensive to run. Apples may not be getting compared with apples. Of course, I'm not assuming that definitely is the case, but we can't disregard it either.
There's a third related point as well that's obvious but needs stating nonetheless; no matter how efficient a gas boiler may be, there is currently no solution on the market for creating one's own home grown fuel for it (Heru has been almost ready to sell to consumers for several years but isn't there yet). That means the running cost is the running cost and there's nothing one can do about that except move tariffs. Any electrical solution - heat pump, electric heater, electric combi boiler, whatever - could if you take it to its logical conclusion be horrendously inefficient and still more cost effective if being run purely on free home leccy. In practice, I'm well aware home PV is more of an offsetting than a replacement for grid power but even so it makes for far more flexibility in deciding a strategy for running one's home heating.
What does seem clear from all I've learned on the forum, though, is that if a heat pump system is designed, installed and configured properly it should either turn in similar running costs to the boiler it replaces or show a small saving. If it is then run in a more cohesive and intelligent way that integrates with home solar generation, a home battery and a smart tariff (so that by various means the actual average price per kWh consumed is lowered) then the savings can become quite significant. However, that takes a bit of tinkering and is certainly not a plug and play type solution.
Specifically for you, @batpred, I'm well aware you're not afraid of tinkering and already have the setup necessary to integrate all the moving parts together into a cohesive single solution.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 month ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
3 months ago
-
Running my new Nibe ASHP efficiently
3 months ago
-
Weather compensation- why you should use it
4 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 309 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 4 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 4 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 4 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 5 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 5 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 7 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 8 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 9 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 11 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 14 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 17 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago