Heat pump's integral circulator pump
Acting on current advise from this channel and others, I'm planning to ask my installer to remove the 4 port buffer and associated circulator from my 200 square meter UFH system over two floors.To be fair to them I had originally (naively) intended to use zoning controls. I'm running weather compensation - fully open loop and I have balanced the zones to achieve desired room temperatures 😀 .
My concern is "will the Daikin integral water pump be powerful enough to provide sufficient circulation" ?
6kW Daikin-ERGA06EAV3A - Indoor Hydrobox Model: EHBH08EF6V
Secondary circulator - Grundfos 25-50 180 (set to minimum speed )
Any advise please.
The quick answer to your question is that the Daikin's own circulation pump probably won't be powerful enough. So in instances like this, if the installer has calculated that it's insufficient, they can repipe your 4-port buffer into a volumiser and then utilise your Grundfos post volumiser to help flow.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Iam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
I understand how important feedback to a question can be, so here is mine.
With no disrespect intended to Mars, I decided to chance it and go ahead with the removal of the 20ltr. 4 port buffer and secondary water circulator to further simplify my system, retaining the redundant components with the proviso that they could be re-instated if needed, .
By using only the Daikin's integral circulator the flow rates appear to be sufficient with no increase in cycling frequency.
I'm very pleased with the results so far, with a COP (using Daikin's on-board energy meter figures!!) of just above 400%- with a happy wife to boot!
@ubert767, I'm really pleased to hear that your pump is strong enough. That’ll definitely be interesting reading for those with Daikins. I’ve been in private contact with a homeowner who’s had issues with Daikin’s defrost cycling and distribution pumps, so it’s great to hear yours is working well.
For the benefit of others, did you remove or bypass the buffer tank yourself, or did you have someone do it for you?
This is a great example for anyone still doubting whether buffer tanks actually improve system efficiency!
And, just to clarify, my doubts about the Daikin pump weren’t unfounded – most installers I’ve spoken to say that because buffer tanks are so commonly used, many manufacturers cut corners on the power of the internal pumps, leaving them with insufficient head.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @alfapat@ubert767 Thanks , no wonder I get too much of a temp drop , mine is 200L , too much mixing .
Ours is 100 litre and it's been piped for maximum distortion/mixing with an X shape between the pipes. Ridiculous. We're planning to get ours repiped in late spring.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
In order to answer my doubts about my buffer vessel I built a cheapish temperature logging system from a Raspberry Pi and five DS18B20 temperature sensors(one sensor on each buffer port and one measuring O.A.T.) This allowed me to see the differentials across the flow and return ports, to check the distortion in the buffer vessel and record the system cycling intervals.
Posted by: @alfapatIam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
It provides extra system volume which is useful for defrost but may well not be necessary. Have you any idea what volume of water you have in your secondary circuit.
One of the ports at top and the other at bottom to ensure it's actually both heated by the water passing through and engaged in the flow. Otherwise you could end up with most of the water in the volumiser just being 'bypassed'
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,483 Topics
- 57.2 K Posts
- 587 Online
- 6,179 Members
Join Us!
Worth Watching
Latest Posts
-
RE: A Smarter Smart Controller from Homely?
@benson yes, I keep forgetting those tools do these ...
By Papahuhu , 6 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
PS to above Can you please confirm the model of hyd...
By JamesPa , 6 hours ago
-
RE: Say hello and introduce yourself
Underfloor hydronic, powered by both the heat pump and ...
By upnorthandpersonal , 8 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna no problem at all… I’ll see what my installer ...
By Mars , 8 hours ago
-
@majordennisbloodnok has a clear explanation above, W...
By F1p , 8 hours ago
-
RE: PV export revenue and HMRC
That makes sense. They are companies that are on market...
By Batpred , 10 hours ago
-
RE: R290 Heat Pump and Foundation Air Bricks
I have been having fun and games whilst getting surveys...
By petch , 11 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@ashp-bobba brill thanks again!
By cmartinbwmba , 17 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@cathoderay OK, thanks all. Much as I thought. I am usi...
By Tasos , 18 hours ago
-
RE: Setback savings - fact or fiction?
My Midea unit reports the OAT or rather AIT (air intake...
By cathodeRay , 18 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
House was finished several years ago, complicated a bit...
By errmm , 1 day ago
-
RE: Extending Puredrive Modular Batteries
@scmilne If the manufacturer says they are ...
By Batpred , 1 day ago
-
RE: Configuration issues with 10kW Midea R32 heat pump
@cathoderay thanks so much for your helpful and expert ...
By Richard T eco home , 1 day ago
-
RE: Optimising LG Therma V R32 using AI
@bontwoody Yes, remove schedules for now anyway. H...
By Tim441 , 1 day ago
-
RE: Mitsubishi Ecodan Stats Reporting - Accuracy Worsens In Auto-Adaptation Mode
Emoncms uses the instant power consumption and delivery...
By Sheriff Fatman , 1 day ago
-
RE: Global Energy Systems Thurso ASHP
Thanks for the update Alexander, and I'm glad that you'...
By Mars , 2 days ago
-
RE: Help…my NIBE heat pump has faulted again!
@Fiona, thanks for coming back with the update, and I’m...
By Mars , 2 days ago
-
@martinrobinson, must just be the way that they've set ...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa the installer did fit primary pro flexis which...
By AdamK , 2 days ago
-
@papahuhu Ah good point. Perhaps I will need to make...
By Batpred , 2 days ago
-
RE: Plant Room Panel in Garage for ASHP, PV & Battery
@colinc Ours have their own LEDs, with plenty of col...
By Batpred , 2 days ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Yes, anyone trying to get a sense of what a heatpump wi...
By Batpred , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Eventually I had confirmation that, when setting an exp...
By Batpred , 2 days ago
-
RE: Five Years of Renewable Heating Hub
By Majordennisbloodnok , 3 days ago