Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pump's integral circulator pump
Acting on current advise from this channel and others, I'm planning to ask my installer to remove the 4 port buffer and associated circulator from my 200 square meter UFH system over two floors.To be fair to them I had originally (naively) intended to use zoning controls. I'm running weather compensation - fully open loop and I have balanced the zones to achieve desired room temperatures 😀 .
My concern is "will the Daikin integral water pump be powerful enough to provide sufficient circulation" ?
6kW Daikin-ERGA06EAV3A - Indoor Hydrobox Model: EHBH08EF6V
Secondary circulator - Grundfos 25-50 180 (set to minimum speed )
Any advise please.
The quick answer to your question is that the Daikin's own circulation pump probably won't be powerful enough. So in instances like this, if the installer has calculated that it's insufficient, they can repipe your 4-port buffer into a volumiser and then utilise your Grundfos post volumiser to help flow.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Iam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
I understand how important feedback to a question can be, so here is mine.
With no disrespect intended to Mars, I decided to chance it and go ahead with the removal of the 20ltr. 4 port buffer and secondary water circulator to further simplify my system, retaining the redundant components with the proviso that they could be re-instated if needed, .
By using only the Daikin's integral circulator the flow rates appear to be sufficient with no increase in cycling frequency.
I'm very pleased with the results so far, with a COP (using Daikin's on-board energy meter figures!!) of just above 400%- with a happy wife to boot!
@ubert767, I'm really pleased to hear that your pump is strong enough. That’ll definitely be interesting reading for those with Daikins. I’ve been in private contact with a homeowner who’s had issues with Daikin’s defrost cycling and distribution pumps, so it’s great to hear yours is working well.
For the benefit of others, did you remove or bypass the buffer tank yourself, or did you have someone do it for you?
This is a great example for anyone still doubting whether buffer tanks actually improve system efficiency!
And, just to clarify, my doubts about the Daikin pump weren’t unfounded – most installers I’ve spoken to say that because buffer tanks are so commonly used, many manufacturers cut corners on the power of the internal pumps, leaving them with insufficient head.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Posted by: @alfapat@ubert767 Thanks , no wonder I get too much of a temp drop , mine is 200L , too much mixing .
Ours is 100 litre and it's been piped for maximum distortion/mixing with an X shape between the pipes. Ridiculous. We're planning to get ours repiped in late spring.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
In order to answer my doubts about my buffer vessel I built a cheapish temperature logging system from a Raspberry Pi and five DS18B20 temperature sensors(one sensor on each buffer port and one measuring O.A.T.) This allowed me to see the differentials across the flow and return ports, to check the distortion in the buffer vessel and record the system cycling intervals.
Posted by: @alfapatIam also looking at this route from 4 pot to maybe a volumiser thaks to Jamespa. Can I ask how does the volumiser help ,or not, if you are putting the return to the top of the old buffer then back to the HP at the bottom of the buffer. Is it not simpler to straight connect through returns.
It provides extra system volume which is useful for defrost but may well not be necessary. Have you any idea what volume of water you have in your secondary circuit.
One of the ports at top and the other at bottom to ensure it's actually both heated by the water passing through and engaged in the flow. Otherwise you could end up with most of the water in the volumiser just being 'bypassed'
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,665 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 1 hour ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 7 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 12 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago