Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pump's integral circulator pump
@heacol I am sorry that this provoked such a reaction. Misinformation applies to me as well so I did warn you. I never made any definitive statements. Heatpumpmonitor is the only resource I know of that provides some insight into what is happening out there. I said that “I presume….” about Vaillant and asked where else this variability of flow would come from otherwise. Likewise, why the prevalent low flow dT’s when these are top performing systems? I calculated a notional 5C dT power to see if there was any correlation to explain this e.g. oversizing? I put this out to get comments and a possible explanation of what the trend is here and what could be learnt from it. As there has been a lot of discussion and misunderstanding about fixed flow and variable flow, perhaps an explanation as to how Vaillant systems manage to alter flow with essentially fixed pumps would be very useful or are my calculations a red herring? Are you saying that we should not take these systems as representative? We are all trying to understand what the best configurations are and what the pitfalls are. If you have detailed insight into how different brands work, or don’t, this would be very helpful to all. Case studies are all we have. Bly goed, meneer. 😊
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @heatgeekBeware disinformation on this forum. I took some time out to verify the statement made about all the top performing heat pumps on heatpumpmonitor.org being fixed flow.
The statement was "not a single one of the top performing heat pumps on heatpumpmonitor.org have a constant dT of 8C. At warmer OATs they mostly run with a dT between 2 and 4.", which you then confirm:
Posted by: @heatgeekiii) In most cases, the flow dT’s are very low (2-4C)
BTW the site can give you the actual flow rates (by switching on "Show flow rate" in the "Show detail" panel), here's a 7kW Vaillant (one of many Valliants) showing a fixed flow rate for CH and a different fixed flow rate for DHW:
@heatgeek No offense taken or inferred. The problem is, no-one actually knows but many claim to, and are disseminating unverified information as fact. This is the very reason there are so many who have such poor systems. I do not blame the installation base, I blame the manufacturers and leading training organisations for not supplying adequate training and information to the general installer to do a good job. The required MCS training is a 3-day course producing "FULLY QUALIFIED HEAT PUMP ENGINEERS 🤣 🤣 🤣 " Open zone appears to work well on systems with delta T control, but it appears to make Valiant units work very poorly, the reason, I think, is due to the lack of Delta T control, why I surmise this? A number of leading Heat Geeks have told me that they perform much better, at part load, with a blocked filter, and at full load when undersized. When I asked them to justify this, they all threw their toys out the cot. However, (I am talking from experience and the analysis of a large number of units) they do seam to perform reasonably well with buffer tanks, very high system volume or thermal mass (under floor) and on-off thermostats, or and a very high heat curve, the reason? This matches with what I was told, when they switch on, they run hard, creating a larger Delta T and then off again.
The other thing this industry completely ignores, but is actually incredibly important, is the balancing of the system. There is no way to balance a radiator heating system accurately at low temperature and 5-10 Deg Delta T, temperature gauges/meters are just not accurate enough and with the modulation of heat pumps, the load, hence the Delta T and flow rate is continually changing. It is easier to do it with a boiler, as there is a Delta T of 20 Deg C and a flow temperature of 70 or 80 Deg C. If the radiators are not balanced, there is no chance of getting good performance, I am just as guilty as every one else. If you notice, most of the best performers on OEM are under-floor at very low temperatures. Balancing radiators is about as accurate and reliable as reading the tea leaves.
I, and others have realized these problems for many years and have been working hard to come up with a solution for both. It will not be too long before they are on the market. Hopefully they will make systems more predictable and easier to commission.
@robs Thanks for this. The statement about 8C was not mine. It came from a Brendon quote. The flow rate shown is the current one. Are you saying that this CH flow rate is maintained at all temperatures with WC? If the flow rate does change, how does it change (what mechanism)? The historic data suggests that it does change with OAT. This is what I have been trying to tease out all along.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
@heacol I agree entirely with you about balancing radiators on low dT. I made the mistake of putting 2 radiators together with my UFH, which is the majority of the house instead of going the whole hog with UFH. I also needed 2 towel rails in the bathrooms to provide primary heating as the UFH was miniscule. I bit the bullet and put all the rads on a separate HP running at 50C together with DHW, with the UFH running continuous low temperature open-loop on a Split HP with PWM pump. Not the most economic, but head soothing.
Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.
Posted by: @heatgeek@robs Thanks for this. The statement about 8C was not mine. It came from a Brendon quote. The flow rate shown is the current one. Are you saying that this CH flow rate is maintained at all temperatures with WC? If the flow rate does change, how does it change (what mechanism)? The historic data suggests that it does change with OAT. This is what I have been trying to tease out all along.
@heatgeek Sorry if I miss attributed that. Yes, the same CH flow rate is maintained at all OATs. Here's the same heat pump running at lower OATs:
And a higher OATs:
The CH flow rate stays at approx. 20.7 lpm. As @heacol said "Vaillant Arotherm heat pumps do have a variable speed pump, however, unlike the Daiken, it does not track the flow temperature maintaining a fixed Delta T".
@robs The flow rate is determined by the capacity of the unit. If you close a valve in the flow, the pump speeds up to try to match the desired fixed flow rate. Why? I have no idea.
Posted by: @heacolOpen zone appears to work well on systems with delta T control, but it appears to make Valiant units work very poorly, the reason, I think, is due to the lack of Delta T control, why I surmise this? A number of leading Heat Geeks have told me that they perform much better, at part load, with a blocked filter, and at full load when undersized.
Interesting
Have you got some examples/evidence you can point to. So far my Vaillant 7kW operated 24x7 open zone no buffer tank is working out 13% cheaper than gas would have done over the same period (November 2024-February 2025), so Im happy. But if you are right Im possibly about to become unhappy (perhaps I should block a filter?)
Posted by: @heacolThe required MCS training is a 3-day course producing "FULLY QUALIFIED HEAT PUMP ENGINEERS
Really? What are the prerequisites, presumably just some plumbing experience in which case thats a bit of a joke isn't it?
Posted by: @heacolThe other thing this industry completely ignores, but is actually incredibly important, is the balancing of the system. There is no way to balance a radiator heating system accurately at low temperature and 5-10 Deg Delta T,
Im with you on that. I cant see how any installer can ever hope to balance a system in the time they can realistically allow. For now it seems to me householders have to do this, and also have to adjust the WC curve because that also takes elapsed days not tens of minutes. There seems, by repute and from my limited experience, almost to be a conspiracy of silence about this, with many (most?) installers instructing householders not to touch the very thigs they have to touch to get the system working properly. I can understand why (Im not sure I could defend the practice, but equally im not sure I could criticise it strongly), but its dodging a problem surely.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa you are right about the cospiricy of scilence regarding system balancing. There is no industry consensous, I put a post on linked in at the end of last year about it, there were approximtly 100 replies but not 1 suitable methode.
Not to worry, I have somehing coming out shortly to sort the ballanceing of radiators and I am testing a product that will sort your delta T out. If it works, I will let you know.
@heacol Of course, balancing radiators properly is not a five minute job for the installer at the end of some four or more days of frenetic work installing the whole system. I witnessed my installers tearing around my ten radiators at the end of a very mild February day when the heat pump wanted to switch off and there they were trying to get the radiators all to warm up! Luckily for them, I was happy to carry out this task myself. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 286 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 2 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 16 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 16 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 19 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago