Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
My setup is as follows: Aerona R32 6kw and Smart Controller with oversize rads (single zone) in a small two bed house with excellent insulation.
I use a WC curve of 0.7 and shift of 0 (despite Grant saying rads should have a curve between 1.2-1.6). Although I don’t achieve a reliable balance (the WC always requires tweaking), it will do for now.
The problem I have and am looking to resolve is the constant running of the in-built circulating pump. To date, I have pump blockade on, so that when the compressor stops, the pump stops 30 seconds afterwards. More importantly, during setback the pump is not running all night. This has worked fine for much of the year, but now winter temperatures are falling below 4 degrees the circulating pump goes into frost protection mode.
Pump blockade not only allows the circulation pump to pause, but it also shuts of the 2-port flow valve. So in defrost mode, the pump is pushing against the Bypass valve (ABV) causing the flow to drop to around 5-6 lpm. If the outside temp sits at 4 degree or below all night, then the pump is under stress pushing water through the ABV during that time.
The Grant manual appears to hint that the pump and/or valve is affected when pump blockade is on. Does anyone know of a way to keep the 2-port valve open during pump blockade to allow the water to flow during frost protection mode?
I have a Grant Aerona 290 15.5 kW with the Smart Controller. I have radiators throughout the house and no underfloor heating. I am running on Shift = 1 and Heating Curve = 0.8. Obviously, the right numbers depend on how well the house is insulated.
Our system was installed in August and I soon discovered that the water circulation pump was on all the time. Since the heating was hardly on at all, this seemed to impose unnecessary wear on the pump and waste electricity. In the summer, one solution is to reduce the temperature at which Winter Mode activates. However, that is not appropriate in winter.
Grant recommends that Pump Blockade should be set to No, if you are using weather compensation. In the colder months, I think this makes sense. Ideally, the heat pump compressor should be running 24 hours per day, so the water pump must be designed to handle that level of work. When the compressor turns off, the water is still hot, so it is good to keep it circulating to impart the maximum energy to the house. It also enables the heat pump to measure the temperature of the water and thus to decide when to turn back on again.
We are not using a set back temperature at night for a couple of reasons:
- We are on the Intelligent Octopus Go tariff, which costs only 7p at night, compared to almost 30p during the day. Therefore, it makes sense to make the house as warm as possible while the cost is a quarter of what it is during the day.
- By running at the same temperature all day, we minimise the required flow temperature, which again keeps our costs down.
If you prefer your bedrooms to be colder, maybe you could use flow regulating valves or lock shield valves to reduce the water flow in those rooms?
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
I ran it last winter 24/7 with no stat. Feeling smug, I told Grant that for over 14 weeks my heat pump only cycled once. That was met with Whoaa! that could wear out the compressor, please let it cycle a few times per day. So I started to question compressors and pumps running 24/7 and the overall feedback I received was that its not a good idea. There should be a balance between efficiency and longevity.
I put the stat back because the WC still requires constant attention. This is despite using a combination of curves, circuit temp correction, and set point correction to fine tune it. The stat acts like Grant intended, a safety net if the internal temp climbs too high. For example, yesterday was a steady 5 degrees outside, and 21 inside. When the outside temp dropped to 3 degrees, my internal temp shot up to 23. If I fine tuned that out, then it would cause issues with the start of the day. Even Grant having looked at my Data concede that it will be an ongoing issue for me so the stat was put back.
If only I could find a way of having pump blockade on without it shutting down the 2-port valve.
@unsure you make an interesting point about longevity. Most of what I have read and heard says that compressors are worn out most by starting up and not by continuous running. Apparently, they are designed to handle so many thousand on/off cycles. If you run a compressor for 24 hours per day and it stops once for 10 minutes per hour, then that reduces its run time by 16%, which is pretty marginal. On the other hand, it adds 24 start stop cycles.
Do you have any concrete evidence for the view that continuous compressor run time is a problem?
I don't quite follow your comment about weather compensation. You said that you managed to run your compressor continuously for 14 weeks, which is very impressive. You also said that you can't adjust weather compensation to keep a constant indoor temperature. Does that mean that you spent 14 weeks continually tweaking it?
My experience is that weather compensation cannot hold to an exact temperature, because of various factors that WC cannot detect - e.g. solar gain on a sunny day, closing the curtains at night, a gaggle of relatives arriving and leaving the front door wide open while they bring in all their luggage...
Having said that, I have found that weather compensation alone can probably keep the temperature within 1C of the target. It is harder when the outside temperature varies a lot, but I have adjusted the Shift and Heating Curve and I think I am fairly close now. The key is to get the slope right and not just set the flow temperature at a specific outdoor temperature using Shift.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
Posted by: @grahamfDo you have any concrete evidence for the view that continuous compressor run time is a problem?
Only the comments I've received from old school HVAC engineers in the states and nordic countries. There is a logic to what they're saying, but I'd be interested if any scientific evidence exists.
Posted by: @grahamfDoes that mean that you spent 14 weeks continually tweaking it?
Yes ! My first heat pump experience during the winter. A kind of obsession creeps in with graph paper, calculations, and reaching heat pump nirvana. Then reality sets in. No work gets done around the house, waking in the night to tweak the EcoNET app whilst in bed annoys the partner, and you find a new mental health medical condition starts to emerge.....Heat Pump Mania.
Posted by: @grahamfMy experience is that weather compensation cannot hold to an exact temperature, because of various factors that WC cannot detect - e.g. solar gain on a sunny day, closing the curtains at night, a gaggle of relatives arriving and leaving the front door wide open while they bring in all their luggage...
Having said that, I have found that weather compensation alone can probably keep the temperature within 1C of the target. It is harder when the outside temperature varies a lot, but I have adjusted the Shift and Heating Curve and I think I am fairly close now. The key is to get the slope right and not just set the flow temperature at a specific outdoor temperature using Shift.
I came to the same conclusion as you, hence why I reinstated the stat to prevent temp runaway. You can fine tune the HC with 'Decreasing Fixed Water Temperature', 'Circuit Temp. Correction', and 'Set Point temp. Correction' in Service settings > 0000 > Main Heat Source and Circuit 1. It takes a lot of time and experimenting, but I did achieve some good results during Jan/ Feb this year. But once the temp swings during the day and the sun is strong it all goes to pot.
I'm confident that in the near future with AI and a few more sensors, we will be able to enter the room temperature and it will remain constant without have to touch the controls for at least a..................day 🙂
Posted by: @unsurethe sun is strong it all goes to pot.
Posted by: @unsureI'm confident that in the near future with AI and a few more sensors, we will be able to enter the room temperature and it will remain constant without have to touch the controls for at least a..................day 🙂
Not unless either you allow the AI to turn on cooling when the sun is strong, or you give it control of the windows and curtains also!
No amount of fiddling with heating controls alone will deal with sunny days at the ends of the season when the potential solar gain well exceeds the loss yet there is still a big diurnal swing. Perversely this problem gets worse for lower loss houses because there isnt the constant drag of heat escaping.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 237 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
…otherwise known as “hive got news for you”. And don’...
By Majordennisbloodnok , 6 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Logically, I'll fall into that category so the natural ...
By Sheriff Fatman , 7 hours ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
I haven’t got a Daikin but I have been having some fun ...
By Majordennisbloodnok , 7 hours ago
-
RE: Setback savings - fact or fiction?
@robs — thanks again for your detailed comments. Some r...
By cathodeRay , 9 hours ago
-
RE: Free Ecoheat Heat Pump Install
I don't mind thread drift, it's how conversation natura...
By Deltona , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 13 hours ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 15 hours ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 15 hours ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 15 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Recently had my follow up with octopus for the vibratio...
By swwils , 17 hours ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 18 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 18 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 20 hours ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 1 day ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 2 days ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 2 days ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 3 days ago