Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@markc The installers put buffer tanks in to stop low flow errors occurring with their badly designed heating systems. It covers their inadequacies, at your cost.
Mars's system is a bivalent system, therefore he gets paid for the renewable heat he produces ONLY. If his running costs are high due to the poorly designed system, he does not get compensated for this. If it was a stand-alone system, the payment would be deemed, based on the EPC figure.
Hi Mark,
I think that you are correct that the DHW valve is not functioning correctly, this is shown by the changes in operation after you lowered the water flow temperature for heating. What appears to be happening now is that the water in your hot water tank is being heated to 50C, at which point the system switches over to heating at 35C. Because the DHW control valve is not closing, water from the ASHP at 35C is still being pumped through the coil in your hot water tank, which of course cools the water in the tank. Since hot water production takes priority over heating, when the water in the tanks falls below the reheat setting the system once more switches over to hot water production at 50C.
First thing to check, there should be a lever on the DHW valve actuator, which can be locked in the open position. Please check by moving the lever backwards and forwards. If the actuator is the type that I think it is, it requires power to open the valve, but the valves closes by spring return when the power is removed. It may be that the actuator has been left in the latched open position.
Please check the above and let me know what you find.
Posted by: @derek-mHi Mark,
I think that you are correct that the DHW valve is not functioning correctly, this is shown by the changes in operation after you lowered the water flow temperature for heating. What appears to be happening now is that the water in your hot water tank is being heated to 50C, at which point the system switches over to heating at 35C. Because the DHW control valve is not closing, water from the ASHP at 35C is still being pumped through the coil in your hot water tank, which of course cools the water in the tank. Since hot water production takes priority over heating, when the water in the tanks falls below the reheat setting the system once more switches over to hot water production at 50C.
First thing to check, there should be a lever on the DHW valve actuator, which can be locked in the open position. Please check by moving the lever backwards and forwards. If the actuator is the type that I think it is, it requires power to open the valve, but the valves closes by spring return when the power is removed. It may be that the actuator has been left in the latched open position.
Please check the above and let me know what you find.
The lever is loose. i.e. I can movie left to right meaning it is open.
As a test this morning when the DHW was at 35º I turned off the DHW heating, made sure the space heating was on and increased the flow temp to 40º. 2 hours later the DHW is at 40º. So what you have described is definitely happening.
Mark,
Move the lever to the valve open position and then let go, it should return to the closed position via spring action. If this is not the case, try holding the lever in the valve closed position and see what affect that has on your system operation.
You should still get your installer back to resolve the problem and if they try to charge for the visit I would be inclined not to pay since they did not fully complete the installation and commissioning of your system in the first place.
Posted by: @heacol@markc That valve you have there is a low flow high-temperature valve, you are throttling your system, effectively it cannot breathe. You need to change it to a full bore 3 port valve for it to work properly.
Thanks for your suggestion Brendon. You clearly have a comprehensive understanding of ASHP systems.
I imagine swapping out that valve in isolation would cause other issues due to how my pipework has been designed.
Posted by: @derek-mMark,
Move the lever to the valve open position and then let go, it should return to the closed position via spring action. If this is not the case, try holding the lever in the valve closed position and see what affect that has on your system operation.
You should still get your installer back to resolve the problem and if they try to charge for the visit I would be inclined not to pay since they did not fully complete the installation and commissioning of your system in the first place.
I've just tried that on another valve that controls flow to the radiators and yes manually opening it (move to the left) is quickly followed by an automatic closing (move to the right).
With the DHW valve in question there is no resistance to the lever left or right so it seems to be permanently open. I've put a call in to the installers (voicemail). As I have a maintenance contract with them this will be covered.
Putting that to one side for the moment, with the DHW turned off, can we get back to your thoughts on the system settings?
Hi Mark,
It would appear that the valve is the problem, here is a video you may find of interest.
I don't think that it will be possible to utilise weather compensation with your present system because of the location of your controller in the utility room.
To fully utilise weather compensation it would first require the addition of a remote sensor, either hardwired or wireless. If you wish to consider this option then please let me know and I will have a detailed look at the manual to guide you through the process.
@markc I can guaranty that your pipework will be wrong. Installing these valves it is the equivalent of driving your car with a potato up its exhaust pipe, and you are blaming the car for not getting above 20 miles per hour and having horrendous fuel consumption.
Mark,
One thing that you could try would be to tap the valve body with a rubber mallet or a block of wood, which may free the valve if it has some dirt stopping if from closing.
Another thing if you feel up to it, would be to switch off the electric supply and remove the cover from the actuator, as shown in the video. Check that the springs are in place and try moving the internal mechanism.
Posted by: @derek-mMark,
One thing that you could try would be to tap the valve body with a rubber mallet or a block of wood, which may free the valve if it has some dirt stopping if from closing.
Another thing if you feel up to it, would be to switch off the electric supply and remove the cover from the actuator, as shown in the video. Check that the springs are in place and try moving the internal mechanism.
Aha! It seems the motor had gotten jammed. After quick manual turning of the little cog with some pliers the valve seems to open and close as expected.
I've just set the DHW heating back on and watched the motor open (the level becoming loose). I'll give it an hour or so and see if the valve closes.
Thanks Derek.
Back to the weather compensation, yes I am interested in trying this out.
Mark,
It is always a good feeling when you solve the problem and fix it yourself.
Once you are certain that the valve problem is resolved, i would suggest that you set your heating water flow temperature to 35C and DHW to 50C again, and monitor your system to see how this affects the COP values. Because of the valve problem, and the original settings by your installer, your system has been operating with a water flow temperature of 50C under all conditions. It will therefore be highly useful to see the different COP values obtained between DHW production and heating. If, as I suspect, it shows quite an improvement in efficiency, it may be cost effective to have the additional equipment installed to provide active weather compensation.
Without wishing to upset 'she who must be obeyed', you could try manually lowering the water flow temperature for heating, to the point where it no longer meets the heat demand. Obviously, because home heating systems respond slowly to changes in temperature, it would be a matter of making a slight adjustment and then waiting several hours to see the effect.
Mark,
A quick question, how did you produce the graphs? Were they derived from your Ecodan controller?
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
1 week ago
-
Running my new Nibe ASHP efficiently
3 months ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
8 months ago
-
Ecodan consuming 100kwh per day in new build!!!
9 months ago
-
Help with understanding my Mitsubishi Ecodan air source heat pump
12 months ago
Currently viewing this topic 22 guests.
- 26 Forums
- 2,591 Topics
- 60.3 K Posts
- 7,056 Online
- 6,924 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Rate the quality of your heat pump design and installation
I had a Worcester Bosch compress 2000 fitted March 2026...
By Josejo , 5 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 8 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 20 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 22 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 22 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 1 day ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago