Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
E121 error code on Samsung 12kw gen 6
I've had this error pop up after changing back from a flow temp only setting to a WC setting.Â
The fitting manual tells me to check PCB connector CN41 and it would appear nothing is plugged in there.Â
I've found videos of older Samsung units and it's a setting in the menu telling it to check but as there is no sensor it comes back as open circuit. It appears this might be what is happening with mine but I can't find the settings to turn it off. Can someone tell me how please?Â
I also appear to have an issue with the Teva out sensor as that is reading -50. Not sure if the two are connected. ThanksÂ
Â
Hi Craig,
When you changed to fixed LWT, I believe that you also changed the setting for the External Room Thermostat, 2091 or 2092.
I suggest that you check the settings and put them back to their original values.
When changing settings always keep a record.
Â
I did change these, but these settings are all back to what they were originally. I take photos on my phone of all settings before and after. That way they are date stamped too so I can go and check a particular day.Â
The part that I have changed that I believe is correct is Indoor Zone Option, standard temperature. I've changed this to indoor and not water outlet.Â
When changing this from Water Outlet to indoor, that is when I get the error.Â
@craig1980 It should be set on Water Outlet if you are using an external thermostat. If you are using the wired remote controller as your thermostat (the one in your airing cupboard), then you set it to indoor, but I believe when you do that there is an additional step required, quite what I don't know! Possibly FSV 2092 or 2093
Posted by: @craig1980I did change these, but these settings are all back to what they were originally. I take photos on my phone of all settings before and after. That way they are date stamped too so I can go and check a particular day.Â
The part that I have changed that I believe is correct is Indoor Zone Option, standard temperature. I've changed this to indoor and not water outlet.Â
When changing this from Water Outlet to indoor, that is when I get the error.Â
Hi Craig,
Is your system working? What are the present settings of #2091, #2092 and #2093?
Â
@mike-h I'd be happy to run it on the wired controller rather than external stats. I'm led to believe that's how they like to run. I'm not using room stats as on/off but as a back stop to WC to stop it going too warm.
@derek-m yes, system is working, still doing 20 secs - 8 min thing though. When the error shows is when you change "standard temperature" from water outlet to indoor. Although Mike has pointed out that it should be set on Water Outlet with my current set up using room stats.
As for #2091,2 and 3 they are all set on "Room temp. On/off or WL interlink on/off (water pump 3).Â
Hi Craig,
I have been giving the page from the manual that you posted, a closer inspection, and although, in typical Samsung fashion, the text is about as clear as mud, the diagrams throw a little more light on the subject.
The first diagram #2092 2 would indicate that when #2092 is set to the value 2, the heat pump will stop when the LWT achieves the value set by the WC curve (WL), but the water pump should continue to run for a further 1 minute.
When #2092 is set to the value 3, the water pump continues to run after the heat pump has stopped, the on - off of the water pump possibly controlled by the thermostat, but that is not specified.
When #2092 is set to the value 4, when the heat pump stops, the water pump should run for a further 3 minutes, then the water pump is stopped for 7 minutes, then runs for a further 3 minutes ad infinitum, until the heat pump restarts.
This seems to tie in to some extent to the way your system is stopping and starting.
The manual does not clearly state the value to which #2091 or #2093 should be set, so you may have to try different combinations.
I would suggest that you try changing #2092 to the value 2, and possibly also #2091. Then try the value 3 and then value 4, noting the operation each time.
Â
@derek-m I've now set 2091, 2 and 3 to Room temp. On/off or WL interlink on/off (water pump 2).
Am I right to assume this is value 2? I'm not sure how to tell which is value 1, 2, 3 and 4
As far as I am aware, you go into Field Setting Mode, as you did when you obtained the data previously.
Â
@derek-m yeah, I'm in field settings in 2091 but there are 5 choices that you can scroll through.Â
Not use
Use signal only on/off
Use (signal on/off) or WL interlink off (water pump 1)
Use (signal on/off) or WL interlink off (water pump 2)
Use (signal on/off) or WL interlink off (water pump 3)
I wasn't sure which of these was which value 1-4. I'm guessing not use is 0 and the others are the corresponding numbers so pump 2 would be value 3.Â
Â
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 2,075 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 2 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 7 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 13 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 4 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago