Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
E121 error code on Samsung 12kw gen 6
Hi Craig,
First of all you will be using more electrical energy, since it is now colder outside. You should also be aware that electrical energy use by a heat pump is not linear with change in outside air temperature, but increases exponentially as the outside air temperature reduces. How much energy did you use?
I am assuming that the heat pump is no longer switching off for only 20 seconds?
One further interesting point is that the 'Inverter Pump' reading is now showing as 25%, which if you had a PWM controlled pump would mean that it would be running much slower. Don't change anything at the moment, but later it may be possible to try the pump on a slower speed setting.
What I don't understand is that the descriptions on the 'Master Indoor Zone Information' screen refer to an 'Indoor Unit', which you don't have in your system. I suppose it could just be that Samsung forgot to change the text in the software for the Monobloc heat pump.
Keep carrying out your tests, which I feel certain both you and others will find of use. One important thing to remember is that no two days are exactly the same, so making like for like comparisons may not always be possible.
@derek-m I had also noticed the reduction in pump speed. It also dropped to 45 when we turned of WC a few days ago.
What KW we were using is a little irrelevant as we didn't have the heating on much and it was much milder at over 10 degrees. We were using as little as 8.6 up to 15kw. Now yesterday was 20 but the outside temp has dropped again and we are on 3.6 outside temp.
The indoor unit bit threw me off aswell. I assumed it was something to do with the box on the front of the UVC.
Yes, we are no longer short cycling. Hooray. Just trying to get it to run as efficiently as possible now. I'll see tomorrow if the 2091, 2 and 3 at #3 is better or worse.
One of the difficulties I have is that we were on LPG before and on auto fill so had no real idea how much we used. We also rarely ran the boiler apart from a few hours a day when it got cold. So I've no comparison for electric Vs previous gas use.
@derek-m I've just read this article on this site
In your situation the simple answer is no.
Because your controller is showing a value of 0.0 at the moment, this indicates that your controller is solely in WC mode, and takes no account of the indoor air temperature. The thermostats can switch the heat pump on and off, but the controller will only vary the LWT dependent upon the outside air temperature.
I'm back now and having checked the energy use it seemed to run for longer and use more energy on #3 on all three settings although this could be down to outside temps as you said. I've put all three back to #2
I'm not sure if 2093 remote controller, room temp control should be the same as the others but that's what I've done so far.
@craig1980 it’s been two years since you posted on this topic. Curious to know what happened.
New to heat pumps? Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
🎧 Prefer to listen? Heat Pumps Explained
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 1,182 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@peterackstraw A few observations rather than a recomme...
By Toodles , 10 minutes ago
-
My newly installed Tesla Powerwall 3 and Gateway. The b...
By trebor12345 , 11 minutes ago
-
RE: Microgeneration Certification Scheme (MCS)
I personally would characterise it as a process/standar...
By JamesPa , 24 minutes ago
-
RE: Jokes and fun posts about heat pumps and renewables
... except that the legal notice (part of which was rep...
By JamesPa , 35 minutes ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 21 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 3 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago