Do I need a bigger volumizer: 8kW Daikin Altherma R32 LT split
Posted by: @rgledhillThanks... I've wondered from day one why it's there.
To suck out energy largely, which it appears to be doing rather well
And to cope with the possibility all your rads are shut down.
I have heard on here and elsewhere of some poor setups, this takes the biscuit.
You will almost certainly be better off bypassing or removing the secondary pump, and bypassing the llh on the flow side so that it becomes a small volumiser in the return. If you do this you need to ensure at least one rad is guaranteed to be open, or fit a pressure activated bypass.
Then please do what @derek-m suggests to re-baseline how the system operates.
But also please note that this is not professional advice just ideas to be tried at your own risk, as we still don't have a system diagram so there may yet be hidden reasons to do things in a particular way.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
That's my suspicion too. We do have two towel rails that are permanently on and there's always the 18l volumiser!
I've dropped Daikin a message as I had the ear of their senior heating engineers, asking if removing the LLH and Grundfos pump work be better. They seem completely redundant to me...
Apologies for not drawing out a system diagram, but it's literally what you see in the photo, presumably with a manifold behind the wall to drive multiple circuits to the radiators and towel rails. If there's anything else you need please let me know and I'll track it down.
the others have already said it. get rid of the pointless 1 foot long middle loop, and the LLH. you've been given a really bad design unfortunately. all its doing is adding complexity and energy loss. its impossible to diagnose and improve your system the way its currently built. don't fit a pressure activated bypass. Just make sure you have always on rads.
also, investigate whether daikin has the capability to report on flow rate and temperatures on the "right hand side" of the indoor units heat exchanger. Other daikin users on this forum may know. If not, fit a heat meter (flow rate and flow/return temp gauge) into the CH side loop. Ideally one that has real time logging. this will be invaluable when you try to balance and optimise the system behaviour between input and output sides of the indoor unit.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @rgledhillApologies for not drawing out a system diagram, but it's literally what you see in the photo, presumably with a manifold behind the wall to drive multiple circuits to the radiators and towel rails. If there's anything else you need please let me know and I'll track it down.
It's 'presumably' that worries me. Given how bad what we can see is, who knows what we can't see? Personally I would presume nothing given the evidence we have! Not your fault I know so no criticism of you!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
A very fair point James! The trouble is that without taking up floorboards, I'm not able to see the exact pipework.
Ian, the unit has the flow rate for its internal pump to the LLH/CHW loop as well as leaving and return temperatures available from the user interface, which does help a lot.
I'm going to contact the installer to see if I can get them to come and remove the LLH and Grundfos pump.
Posted by: @rgledhillA very fair point James! The trouble is that without taking up floorboards, I'm not able to see the exact pipework.
Ian, the unit has the flow rate for its internal pump to the LLH/CHW loop as well as leaving and return temperatures available from the user interface, which does help a lot.
I'm going to contact the installer to see if I can get them to come and remove the LLH and Grundfos pump.
brilliant. so just double checking, you can you see flow rate and leaving + return temps, both sides of the HEX? if so you've got what you need to tune it once the LLH has been removed.
your installer may have put the LLH in because of concerns about evohome TRV's closing and dropping the flow rate too low. reassure them that you are aiming to run with almost all rads open all the time and that you therefore do not need an LLH and you definitely don't need a bypass valve either.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I believe I can see all of those readings, yes. I've been using them to watch it establish and maintain the temperature differential, cycling up and down due to the overshoot setting of 4C.
Thanks for the advice for talking to the installer. I will keep this thread updated.
Thank you all!
Well, we had the low-less header and accompanying Grundfos pump removed a few weeks back. And the results... well, the system has stabilised somewhat and isn't prone to the freak COPs of <2 any more. It's more settled but we're still just getting high 2's, occasionally tipping over 3, with temperatures varying between 0-13C overall. My suspicion is that a lot of the problem is extremely poor energy measurements inside the system, such that rounding errors can cause a massive perceived swing in COP - not a lot I can do about that.
So overall at this point, I'm just going to accept that it is what it is. I've spent hours and hours on this and the bottom line is that the particular combination we have (Evohome + Daikin ASHP) is just not an efficient combination. If I effectively disable the Evohome system by setting all room temperatures to 25C and control it with the flow valves, it still doesn't help as the ASHP cycles in and out at the super-low flow temperatures needed to keep the house at a sensible temperature.
Thanks for the support and help everyone.
-
Daikin 6kw setup with Dixell controller
1 day ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 months ago
-
Daikin Error Code 7H05
1 year ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
1 year ago
-
Daikin COP / energy used measurement from MMI
2 years ago
- 27 Forums
- 2,475 Topics
- 57 K Posts
- 227 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
Got Vaillant coming on Monday. Any tips on how to get t...
By AdamK , 5 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
Several years ago we went away for a weekend in the mid...
By JohnnyB , 8 hours ago
-
@jamespa Many thanks NAPIT have misinformed me again. 2...
By Bart , 9 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
This is the vision I bought into when I signed the cont...
By razz , 9 hours ago
-
RE: Rate the quality of your heat pump design and installation
@technogeek, you raise several fair points. You’re abs...
By Mars , 10 hours ago
-
@sune, will you be easy to identify and are you still s...
By Mars , 10 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
What’s remarkable from this very short thread is just h...
By Mars , 11 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson I am using the met.no forecast integration and ...
By Grantmethestrength , 11 hours ago
-
RE: Setback savings - fact or fiction?
The system I looked at and used the charts from was a M...
By cathodeRay , 13 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
er, if you do this how will the heat pump ever know to ...
By JamesPa , 14 hours ago
-
RE: What a Bad Heat Pump Installation Looks Like
@editor I can just about make the badges from the front...
By idemportent , 14 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
Btw, fixing your system so the underfloor heating is wo...
By Adrian , 16 hours ago
-
RE: Optimising LG Therma V R32 using AI
On the main controller you can easily press + or - u...
By Tim441 , 18 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
@errmm, have the original installers not come out to ha...
By Mars , 23 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 1 day ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 1 day ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 2 days ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 2 days ago